    Daikin RSXY10K7W1



    I have problem with vrv system Daikin RSXY10K7W1. There is U7 error displayed on centralised remote control.
    System do not work on heating.
    Where can I download service manual.



  2. #2
    Join Date
    Apr 2008
    Location
    australia
    Age
    58
    Posts
    47
    Rep Power
    0

    Re: Daikin RSXY10K7W1

    U7 error is a faulty transmission between outdoor units or heat storage device.
    Do you have more than 1 condensing unit?
    Have you run the system through a start up test?

  3. #3
    Join Date
    Jun 2008
    Location
    Serbia
    Posts
    13
    Rep Power
    0

    Re: Daikin RSXY10K7W1

    I have 6 units. One unit do not work on heating but works on cooling.

  4. #4
    Join Date
    Mar 2007
    Location
    manchester
    Age
    17
    Posts
    63
    Rep Power
    19

    Re: Daikin RSXY10K7W1

    have you tried wiring check from condensor?

  5. #5
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: Daikin RSXY10K7W1

    if yoou have a U7 fault it is most likely going to be one of the outdoor pcb fuses blown, power to the outdoor turned off or faulty control pcb.
    start with thecking you Q1 and Q2 cable between the outdoor units.

  6. #6
    Join Date
    Feb 2009
    Location
    Cornwall
    Posts
    9
    Rep Power
    0

    Re: Daikin RSXY10K7W1

    Hello
    would one of you's be so kind to put a link up with daikin codes
    not a d1 dealer so i can not access there site
    thanks in advance

  7. #7
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Daikin RSXY10K7W1

    Daikin Codes below - quality not the best sorry

    pdf. is 3.5mb and can not upload
    Attached Images Attached Images

  8. #8
    Join Date
    Oct 2006
    Location
    UK
    Age
    57
    Posts
    165
    Rep Power
    18

    Re: Daikin RSXY10K7W1

    Quote Originally Posted by gille View Post
    I have problem with vrv system Daikin RSXY10K7W1. There is U7 error displayed on centralised remote control.
    System do not work on heating.
    Where can I download service manual.
    Hello Gille,

    On the RSXY10K (K series VRV) it was possible to group control the outdoor unit so that that more than one system can operate in the same mode at the all times. To achieve this you would have to install an adaptor PCB known as DTA104 to one of the indoor units and wire to the F1 F2 terminals. Then you need to link the F1 F2 outdoor terminals on the condensing units you want to group control. Then you need to make some field setting on the outdoor unit in Mode 1 and Mode 2.

    You need to set up which of the outdoor units will be the master and which is the slave. You also have to program the cool/heat address on all outdoor unit in the same group.

    So the upshot is that if you program one unit as a master, it will expect to see a slave unit or vice versa otherwise you will get the U7 error code indicating communication error between master and slave outdoor units.

    Could it be that you have by mistake programmed one of the outdoor units and master or slave?

    For normal operation and factory setting the outdoor units is set to “Ind” for individual control. You can see the LED lit under “Ind” for individual, “Mst” for master outdoor unit or “Slv” for slave outdoor unit.

    Hope it helps

    Regards
    Obi Wan

  9. #9
    Join Date
    Oct 2006
    Location
    UK
    Age
    57
    Posts
    165
    Rep Power
    18

    Re: Daikin RSXY10K7W1

    Quote Originally Posted by brunstar View Post
    if yoou have a U7 fault it is most likely going to be one of the outdoor pcb fuses blown, power to the outdoor turned off or faulty control pcb.
    start with thecking you Q1 and Q2 cable between the outdoor units.

    Brunstar,

    There are no Q1 Q2 terminals on the normal VRV K series outdoor units.

    Only on the RXY10K and RNY10K VRV Plus system with the function unit will you find Q1 Q2 terminals.

    Regards

    Obi Wan

  10. #10
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Daikin RSXY10K7W1

    Quote Originally Posted by Dial666 View Post
    Hello
    would one of you's be so kind to put a link up with daikin codes
    not a d1 dealer so i can not access there site
    thanks in advance
    You do not have to be a dealer to register with the Daikin website.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  11. #11
    Join Date
    Sep 2010
    Location
    Seychelles
    Posts
    15
    Rep Power
    0

    Re: Daikin RSXY10K7W1

    Hi Obi-Wan,

    I am hoping you still post here since this is a good 4 years after this post.

    We have a similar problem to the OP but it looks like - for whatever reason - our single outdoor unit has somehow been set to 'slave', which now makes it 'look' for the master unit which does not exist and therefore sends out the U7 error.

    I have been searching through the literature Daikin gave us but nowhere does it say how we can change the setting of the outdoor unit from slave to master. any help?

  12. #12
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: Daikin RSXY10K7W1

    If you have H3P (H/C IND) & H7P (SEQ) both on this is normal LED display for individual heat/cool VRV K outdoor unit

    If you have H4P (H/C MASTER) & H7P (SEQ) both on indicates the outdoor has been set as a heat/cool master.

    If you have H5P (H/C SLAVE) & H7P (SEQ) both on indicates the outdoor has been set as a heat/cool slave.

    To modify this setting when any of the above are displayed:
    Press set until H3P individual is flashing (each time the button is pressed the display will change between IND/MASTER/SLAVE)
    Press RETURN x 1

Similar Threads

  1. Daikin not working... many problems
    By stankovicv in forum Air Conditioning
    Replies: 26
    Last Post: 11-12-2010, 09:01 AM
  2. Daikin, Why do we bother?
    By gwilliamson in forum Air Conditioning
    Replies: 21
    Last Post: 02-02-2010, 09:38 AM
  3. Daikin controller
    By mchild in forum Air Conditioning
    Replies: 8
    Last Post: 02-10-2009, 07:14 PM
  4. Daikin Comp and inverter
    By WCC73 in forum Air Conditioning
    Replies: 5
    Last Post: 08-11-2008, 08:44 PM
  5. Getting a price from Daikin....
    By monkey spanners in forum Chit Chat & Service Stories
    Replies: 4
    Last Post: 17-08-2008, 09:46 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •