    Daikin BS-boxes noise



    Hi all
    I have some Daikin HR VRV systems where the client is complaining the noise produced by refrigerant into BS boxes. They have some solution to reduce this noise, but I would like to ask if the other brands that are producing similar systems, come across with the same problems?

    Thanks in advance for your replies.



  2. #2
    Join Date
    Oct 2007
    Location
    Britain
    Posts
    220
    Rep Power
    17

    Re: Daikin BS-boxes noise

    Hi Nicola,

    I have only worked on Mitsubishi Electric and Toshiba VRF systems apart from the Daikins and as they work differently, i.e. with the branch controller box's they do not appear to have the same problem that Daikin have, or if there is a noise it would be in one area only.

    Regards

  3. #3
    Join Date
    Apr 2006
    Location
    Torquay
    Age
    59
    Posts
    130
    Rep Power
    19

    Re: Daikin BS-boxes noise

    We had a noise coming from a bs box. Daikin UK carried out a software upgrade (valve timing)which involved puting a lap top on every bs box. It was caused by 1 valve passing.We also had the same noise on another site, that was because we fitted an extra fan coil and bs box to an existing system, but the office ordered the wrong series fan coil. Regards Kev.

  4. #4
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: Daikin BS-boxes noise

    Any item which has electronic expansion valve or solenoid valve can make some noise as refrigerant passes through.
    If the noise is excessively more than normal it will be caused by some problem like incorrect refrigeration pipe connection or some malfuction of solenoid valve / electronic expansion valve.

    An investigation of system operation is required to find the cause.

    The premium VRV / VRF brands only make very slight refrigeration noise & if the the box is in the ceiling void there should be no noise problem.

  5. #5
    Join Date
    Feb 2009
    Location
    england
    Posts
    22
    Rep Power
    0

    Re: Daikin BS-boxes noise

    there is a service code to program from the outdoor unit to change the speed at which the vavles open and close in the function box. This is sometimes used to cure this noise,Daikin should be able to advise you on this.

  6. #6
    Join Date
    Sep 2006
    Location
    italy
    Age
    53
    Posts
    93
    Rep Power
    18

    Re: Daikin BS-boxes noise

    Thanks to all of you, I will try on site your advises

Similar Threads

  1. Noise problem on DAIKIN 4MXS68F2
    By cool#9 in forum Air Conditioning
    Replies: 3
    Last Post: 03-01-2009, 02:43 PM
  2. Noise induced hearing loss damages
    By Abe in forum Legal-Business-Marketing
    Replies: 7
    Last Post: 26-05-2008, 10:36 AM
  3. daikin noise
    By philjd26 in forum Air Conditioning
    Replies: 5
    Last Post: 09-04-2008, 06:47 PM
  4. Daikin Noise Levels, Please Help
    By gwilliamson in forum Air Conditioning
    Replies: 4
    Last Post: 28-02-2007, 07:26 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •