Oil change problem
Hi,
Where I work we regularly change the oil in compressors during maintenance visits. Here's what we do...
Start machine: Frontseat SSV: Switch off machine when Low Side pressure is 0.1 Bar: Unscrew filler cap or oil return connection: Suck out oil into empty cylinder: Pump new oil in: Put cap/connection back on: Vac out Low Side of compressor: Wind out SSV until it is cracked off backseat position: Restart machine and adjust oil level if required.
The problem is that sometimes you get gas coming back down the oil return line meaning you have to recover all the gas to change the oil. Does this mean the Oil Sep is faulty? Or should I try to tap it gently to get it to shut off? Any thoughts welcome. Cheers, Murray.
-
06-02-2009, 02:35 AM #2
Re: Oil change problem
hi,
murry can i know what model you service about oil change problem?
-
06-02-2009, 07:20 AM #3
Re: Oil change problem
without saying what equipment you are working on it's difficult to be exact.
But assuming you have a standard oil return system.
If there is no isolation valve on the oil return line.
Then it may be feasible to pump down as you describe.
Is possible drop into a negative pressure. Dependant upon system.
Then isolate the discharge line, allow sufficient time for internal pressures to equalise.
If it has risen to much, you will have to open the discharge line and pump down again.
Then pull a Vacuum and suck your fresh oil back in.
Or if you have a good hand pump just pump down to say 1/2 a bar.
Use the remaining pressure to push the oil out.
As soon as any vapour appears in the oil dump line shut off.
Pump fresh oil in with hand pump.
Only you can decide which method is more relevant?
Incidentally as a personal preference, on larger recips.
I like to open the sump access cover
and do an inspection of the bottom of the crankcase.
For metal deposits and any other foreign particles!
Hope this helps.
Grizzly
Similar Threads
-
MFI AMP6855 defrost problem
By gliderpilot47 in forum DomesticReplies: 4Last Post: 12-01-2011, 12:11 PM -
A strange problem
By MuhengineeR in forum Air ConditioningReplies: 14Last Post: 27-10-2010, 05:21 PM -
problem with GE air con power problem
By Richie101 in forum Air ConditioningReplies: 6Last Post: 05-11-2009, 04:00 PM -
Temperature problem with liquid NH3
By energeia in forum NH3Replies: 34Last Post: 05-08-2009, 08:16 AM -
Furance problem
By ALONEI in forum Trouble ShootingReplies: 10Last Post: 14-05-2008, 11:32 AM