Chiller COP
How do I determine the COP of a 12 year old centrifugal chiller ?
-
05-02-2009, 09:26 PM #2
Re: Chiller COP
Plot the running parameters on to a Mollier Chart and do the maths.
Sorry, but, there is not really any other way.
-
05-02-2009, 11:45 PM #3
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Chiller COP
Measure flow at evaporator and delta T of water/glycol and calculate cooling capacity from that.
Measure chiller power consumption and divide calculated cooling capacity with that, and you got your actual chiller COP.