    Chiller COP



    How do I determine the COP of a 12 year old centrifugal chiller ?



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Chiller COP

    Plot the running parameters on to a Mollier Chart and do the maths.

    Sorry, but, there is not really any other way.

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Chiller COP

    Measure flow at evaporator and delta T of water/glycol and calculate cooling capacity from that.
    Measure chiller power consumption and divide calculated cooling capacity with that, and you got your actual chiller COP.