Re: 9 superheat & subcooling scenarios
Another scenario,if anyone can answer.
Checked a chiller and found low subcooling( well the manufacturer did) with an ambient of 9°C, he added some R134A, system was at 100% load.
Two weeks later another manufacturer employee went out and said it was over charged, reclaimed the gas and said it had been overcharged by 2kgs(64kg charge).
I was not sure what the ambient or pressures were as i did not attend.
Someone explained that as the ambient was lower the subcooling coud have been low and as the ambient was probably higher the 2nd time around and had been overcharged the subcooling would have been low again because of the liquid backing up in the condenser.
How can you have effectively have the same scenario ( low subcool) and have two different answers.
Similar Threads
-
Superheat and Subcooling
By Chunk in forum FundamentalsReplies: 42Last Post: 15-01-2011, 01:24 AM -
subcooling and superheat are standard measurement or not?
By karl2009 in forum Technical DiscussionsReplies: 3Last Post: 10-01-2009, 11:39 PM -
Help on superheat and subcooling
By hvac student in forum Trouble ShootingReplies: 8Last Post: 08-08-2008, 02:25 PM -
Subcooling at TEV vs Superheat at Compressor relation in Steady State
By GXMPLX in forum FundamentalsReplies: 12Last Post: 14-07-2008, 03:00 PM -
Superheat and subcooling
By marc5180 in forum TrainingReplies: 27Last Post: 08-10-2007, 09:21 PM