18-04-2011, 03:23 PM #33
Re: 9 superheat & subcooling scenarios
If the evaporator were starved for air, the split (delta-T) would be high and the superheat would be low. The evaporator is starved for refrigerant, but the condenser is not, therefore the liquid flow is partially restricted.
Is the system TXV or fixed orifice?