    Multiple condensors



    Excisting condensor.

    What about installing a second one (increasing capacity) but not of the same size as the original one?
    First case a bigger one and in a second case a smaller one?

    What should be done/installed/foreseen so that both are 'fed' with correct capacity? So that the discharge gasses don't follow the way of least resistance.
    Purpose is try to condens as low as possible.
    Is it anyway possible?

    Any comment is welcome



  2. #2
    Join Date
    Jun 2002
    Location
    UK
    Posts
    628
    Rep Power
    23

    Re: Multiple condensors

    Hi peter

    Yes ive seen this done two condensers side by side one smaller than the other.
    I believe as long as the pipe work is teed off equally the losses to one condenser would be negligible.

    Mark

  3. #3
    Join Date
    Jun 2002
    Location
    UK
    Posts
    628
    Rep Power
    23

    Re: Multiple condensors

    Remembering that the evaparator and condenser must have equal capacities

  4. #4
    rbartlett's Avatar
    rbartlett Guest

    Re: Multiple condensors

    Quote Originally Posted by MarkFiddy
    Remembering that the evaparator and condenser must have equal capacities

    why? what happens to 'heat of compression' ?


    cheers

    richard

  5. #5
    Join Date
    Jun 2002
    Location
    UK
    Posts
    628
    Rep Power
    23

    Re: Multiple condensors

    LOL just read my post

    It would be true if refering to a condensing unit

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Multiple condensors

    It's on a pack. Client had problems last summer with too less condensor capacity and needed to spray water on them.

    Engineering office said that if you don't install exact the same condensor, it will never work. Because actual condensor is an older type, there must be installed two new ones or a big one.

    I disagreed with him because we sometimes uses recup condensors which we had to take over when installing new ones. And in many cases , they're from different brands and size. It worked but I never measured temperatures or pressures over the condensors.

  7. #7
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: Multiple condensors

    Hi Peter,
    You want to come and work over here. Last summer all the major supermarkets were spraying water on condensers to stop them tripping out in this area. Tescos,Sainsburys,Morrisons,Somererfield are the ones i know about. It's all down to cost as per usual. One year these people might realise that ambients can hit 30 degree's in the UK. Until then we will just have to keep buying garden hoses & sprinklers from the DIY stores

    Regards

    Raymond

  8. #8
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: Multiple condensors

    Hi Guys, just had a thought (Dont knock it)

    All Major retailers put their condensers on the roof so in summer the sun beats down on them all day. Has anyone ever tried to build a canopy over the top the stop the sun going directly onto them or would it just prevent the heat escaping & therefore not work.

    Regards

    Raymond

  9. #9
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Multiple condensors

    Hi
    if you are using a vee block type condenser you can fit a minimiser type system, in essence a set of sprinker heads with a mesh curtain to reduce drift, much easier that a new condenser.
    A smaller condenser fitted with a large one, no problem provided you trap the condenser outlets to craete a liquid column, or possibly pipe both both outlets into a low velocity header witha slope away from the condensers and a liquid opt on the end to ensure gas doesn't enter the liquid line.
    Mark equal tee's don't work properly on any conderser configuation , you might be able to get this to work if you cycled fans on a mirror image sequence, but even that is touch and go
    trap the outlets and create a liquid column, much easier.
    poor condenser pipe work is a common thing on supermarket installations, nice big well sized condensers, mostly piped incorrectly.
    and the multiples wonder why they had bother last year

    Kind Regards. Andy.

  10. #10
    Join Date
    Jun 2002
    Location
    UK
    Posts
    628
    Rep Power
    23

    Re: Multiple condensors

    Andy the things you point out i felt didnt need explaining to peter as i guessed he would probably know these points .

  11. #11
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Multiple condensors

    Hi Mark
    well that's me put in my place
    Kind Regards. Andy

  12. #12
    rbartlett's Avatar
    rbartlett Guest

    Re: Multiple condensors

    Quote Originally Posted by rdocwra
    Hi Guys, just had a thought (Dont knock it)

    All Major retailers put their condensers on the roof so in summer the sun beats down on them all day. Has anyone ever tried to build a canopy over the top the stop the sun going directly onto them or would it just prevent the heat escaping & therefore not work.

    Regards

    Raymond

    we quoted some work in saudi -so we shipped the units and a load of wood to make such a shelter

    when we got there we noted that no other bugger bothered so when we flew out again there was a pile of wood left on site...

    cheers


    richard

  13. #13
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: Multiple condensors

    [QUOTE=Andy]Hi
    if you are using a vee block type condenser you can fit a minimiser type system, in essence a set of sprinker heads with a mesh curtain to reduce drift, much easier that a new condenser.

    Hi Andy,
    For us Uneducated ones whats a vee block type condenser & do you know of a website or have any info on the sprinkler system.

    Regards

    Raymond

  14. #14
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Multiple condensors

    Raymond
    vee block is just two coil blocks mounted in the shape of a vee with the fans on top, used a lot in packaged water chiller.
    As for the minimisers, I don't know of a web site, but I will ask the guy who fitted them on various sites i've been on to tell us where he got them.
    Kind Regards.Andy

  15. #15
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Multiple condensors

    Have a look at this site http://www.epsltd.co.uk/EcoMESHcatalogue.pdf on page 4 there is a picture of a V block condenser at bottom left

  16. #16
    Join Date
    Mar 2002
    Location
    San Francisco Bay Area
    Posts
    180
    Rep Power
    23

    Re: Multiple condensors

    Studied this many years ago and only remember that the problem is in pressure differential which can back refrigerant up into one condenser.

    Solution was to calculate proper line size (larger than expected) between both condensers and the receiver, which would allow pressure equalization between components.

    Suspect the Prof could provide a more sophisticated answer.

    Rog

  17. #17
    Join Date
    Jun 2003
    Location
    Georgia
    Posts
    72
    Rep Power
    21

    Re: Multiple condensors

    Quote Originally Posted by RogGoetsch
    Studied this many years ago and only remember that the problem is in pressure differential which can back refrigerant up into one condenser.

    Solution was to calculate proper line size (larger than expected) between both condensers and the receiver, which would allow pressure equalization between components.

    Rog
    Exactly, Rog!! Symmetrical piping inbound with no one inlet being favored in flow. Oversized lines equalizing pressures to ensure gravity drain into trapped piping. I remember Phaklides' lessons almost word for word!

Similar Threads

  1. Fujitsu cassette h/p condensors icing up !
    By stevo in forum Air Conditioning
    Replies: 9
    Last Post: 03-03-2006, 02:34 PM
  2. multiple evaps in a supermarket line-up
    By kengineering in forum Supermarket Refrigeration
    Replies: 4
    Last Post: 11-02-2006, 05:23 AM
  3. multiple compressor pack
    By Mark in forum Supermarket Refrigeration
    Replies: 21
    Last Post: 10-05-2005, 09:11 PM
  4. multiple evaps
    By angryk in forum Fundamentals
    Replies: 5
    Last Post: 28-12-2003, 09:49 PM
  5. Multiple Evaporators
    By rcz in forum Commercial
    Replies: 8
    Last Post: 22-07-2003, 11:20 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •