Re: Capillary tubes
Increasing of cooling capacity is not related only with capillary tube modification. Greater cooling capacity means a greater flow rate of refrigerant through the compressor, and as a consequence the flow rate of the liquid through the capillary tube have to be greater.
Only a) solution can do this.
The c) solution wil give you, roughly, the same pressure drop across the capillary tube and this means the same flow rate of liquid.
If you increase the flow rate of liquid using a) method then you have to be carefull because you will have a wet compression with all the consequences.