    appears short of refrigerant



    i have been out to replace a compressor in a unusual display cabinet and im saying unusual as i hardly see much commercial any way the unit is approx 4 meters long in display area the evap runs the length of cabinet it is a horizontal evap 2 tube high and 6 tubes wide the uint has storage underneath with an evap also rinning the length of cabinet and its a vertical evap 1 tube wide and 2 tubes high both evaps are static cooled(no evap fans) both evaps have a tx valve it has 7 doors to under bench storage area there is no manuaf info on cabinet i can see,
    The compressor i replaced around 3 months ago it seemed to be going ok and i was called back next day as was not cold enough, a little more refrigerant and off i went, i called the day after and coil was flooded temps were good and off i went all was good until today i was called and found sight glass bubbles and top evap runnin short ie first run only half flooded at this stage i only had suction line attached and pressure was 310kpa (43psi) due to the bubbles in sight glass i added a little fefrigerant and found no change in suct press or evap flooding in total i added approx 200 grms and found no change in evap or pressure, the system appears to run extremly hot and i then placed my gauge on liquid line i found i had HS press of 3300kpa (475psi) and still LS 310kpa(43psi) i turned system off and allowed pressures to equalise and found appeared ok i the restarted unit after 10min or so off and found same pressures the condensor is slightly blocked you can see some dust in there but you can see through it i am returning to throughly clean condensor but i am wondering if anyone may have some tips for me as correctly diagnose differences between short of gas symptons and blockage symptons this is proberly a very silly question but i gotta ask thanks for taking the time to read my story i hope to hear from you cheers



  2. #2
    Join Date
    Nov 2008
    Location
    NELSON BAY AUST
    Age
    43
    Posts
    48
    Rep Power
    0

    Re: appears short of refrigerant

    oh i forgot to mention the compressor is a kirby(heatcraft)type and manuf no. aw54lz-1c system operates on r22 how easy to forget the most valuable information

  3. #3
    Join Date
    Jan 2009
    Location
    New Zealand
    Age
    38
    Posts
    7
    Rep Power
    0

    Re: appears short of refrigerant

    Hi Tech_Tim

    does the unit have a reciever?
    was the drier changed and unit fully evacuated when the compressor was changed?
    silly question but is the condensor fan goin?
    what sorta superheat are you getting on the evaps?

    for r22 310kpa is around -6C for static coils you should expect around -10 to -12 from my experience

    475psi is crazy! no hp switch i gather? be careful!

    cheers

  4. #4
    Join Date
    Nov 2008
    Location
    NELSON BAY AUST
    Age
    43
    Posts
    48
    Rep Power
    0

    Re: appears short of refrigerant

    YEH NO HP i a bit worried bout that i was gettin suct as low as 275 wich on gauge says -10 i havnt gone as far as checkin superheat not too familuar wit that both evaps join into same suction line wich is prob normal system has got a reciever and dryer was chenged with compressor and unit was fully evaced cond fan all ok im not to sure with super heat should i get suction press at comp and suct line temp at evap ?? any tips would be great thanks for takin time to reply also temps in bottom compartment are roud 5-6 deg cel but in top (where evap not flooded) temps round 16-20 deg cel i dont wanna put more gas in even though sight glass bubbles dont want head press to get any higher (if thats poss)

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: appears short of refrigerant

    Quote Originally Posted by TECH TIM View Post
    YEH NO HP i a bit worried bout that i was gettin suct as low as 275 wich on gauge says -10 i havnt gone as far as checkin superheat not too familuar wit that both evaps join into same suction line wich is prob normal system has got a reciever and dryer was chenged with compressor and unit was fully evaced cond fan all ok im not to sure with super heat should i get suction press at comp and suct line temp at evap ?? any tips would be great thanks for takin time to reply also temps in bottom compartment are roud 5-6 deg cel but in top (where evap not flooded) temps round 16-20 deg cel i dont wanna put more gas in even though sight glass bubbles dont want head press to get any higher (if thats poss)
    First thing to do is, to clean that condenser coil, and be sure that fan is working properly.

    Than measure temperature of pipe exiting condenser and subtract that from value of saturation condensation temperature from high pressure gauge (or convert it from high side pressure). That will give you subcooling value, which tell us state of refrigerant charge in system with TXV valves.
    If it is higher tan 8K, remove some refrigerant until subcooling is lower than 8K and still above 3-4K (allow some time of 15-20 min between readings), and than make again readings of system pressures and temperatures:


    • Suction pressure
    • Condensation pressure
    • Display cabinet temperature
    • Air temperature in and out at condenser
    • Temperature of pipe at exit of evaporator
    • Temperature of pipe at suction on compressor (15-20 cm from compressor)
    • Temperature of pipe at exit of compressor
    • Temperature of pipe at exit of condenser
    • Temperature of pipe at entrance of dryer
    • Temperature of pipe before TXV


    Make temperature readings with accurate thermometer suitable for pipe temperature measurements.
    And, please, format text to be readable. You have 28 year and degree. I assume that you should know how to properly format your sentences.
    Last edited by nike123; 04-02-2009 at 10:51 AM.

  6. #6
    Join Date
    Nov 2008
    Location
    NELSON BAY AUST
    Age
    43
    Posts
    48
    Rep Power
    0

    Re: appears short of refrigerant

    Hi Nike, thanks for the comment on my gramma, i know its bad ill try be better so yous can understand what im saying, sorry bout the aussie slang if that bothers you but cant help that.

    thanks even more for your tips, i returned today and thoughrly cleand condensor, and oh my, it was way dirtier than i thought, i than test run the unit and bingo, head pressure was down to1500kpa(215-220psi), suction pressure was also lower sitting at 140kpa (20psi) too low i suspect, the sight glass was still bubblin and evap appeared to starve (cabinet was warm and unloaded), i squirted some more r22 and found still no change in suct pressure. the owner was keen to leave so i didnt get too play too much, i am getting him to turn on in mornin and i will call later and i will take suggested measurements, thanks again for taking time to reply nike take it easy....
    Last edited by TECH TIM; 05-02-2009 at 10:21 AM. Reason: gramma

  7. #7
    Join Date
    Nov 2008
    Location
    NELSON BAY AUST
    Age
    43
    Posts
    48
    Rep Power
    0

    Re: appears short of refrigerant

    also want to mention the suction pressure was 140kpa, suction line temp approx 10 cm from compressor was 18-20 deg cel..

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: appears short of refrigerant

    Quote Originally Posted by TECH TIM View Post
    Hi Nike, thanks for the comment on my gramma, i know its bad ill try be better so yous can understand what im saying, sorry bout the aussie slang if that bothers you but cant help that.

    thanks again for taking time to reply nike take it easy....
    I will.
    It is not slang what bothers me, it is lack of punctuation marks. Your text and sentence doesn't have start, middle and end marks, and is one big sausage hard to read (at least for me). That is text formating I speak about in my previous answer.

    Look at readability of my answer, if I do as you do:

    first thing to do is to clean that condenser coil and be sure that fan is working properly than measure temperature of pipe exiting condenser and subtract that from value of saturation condensation temperature from high pressure gauge or convert it from high side pressure that will give you subcooling value which tell us state of refrigerant charge in system with TXV valves if it is higher tan 8K remove some refrigerant until subcooling is lower than 8K and still above 3-4K allow some time of 15-20 min between readings and than make again readings of system pressures and temperatures suction pressure condensation pressure display cabinet temperature air temperature in and out at condenser temperature of pipe at exit of evaporator temperature of pipe at suction on compressor 15-20 cm from compressor temperature of pipe at exit of compressor temperature of pipe at exit of condenser temperature of pipe at entrance of dryer temperature of pipe before TXV
    make temperature readings with accurate thermometer suitable for pipe temperature measurements and please format text to be readable you have 28 year and degree I assume that you should know how to properly format your sentences
    Now, tell me, is this something you wish to read, and something you understand easy as original text?

  9. #9
    Join Date
    Nov 2008
    Location
    NELSON BAY AUST
    Age
    43
    Posts
    48
    Rep Power
    0

    Re: appears short of refrigerant

    it is hard to read i agree

    i know its bad ill try be better so yous can understand what im saying,
    as i said

  10. #10
    Join Date
    Nov 2008
    Location
    NELSON BAY AUST
    Age
    43
    Posts
    48
    Rep Power
    0

    Re: appears short of refrigerant

    hi guys, how are we? just want to keep tou all up to date with this one, what i have worked out is the system was actually charged with r404a, and was tagged r22, i must not have been thinkin that day, therefore i have topped up r22 on r404a obviously not good, i have returned and recovered refrigerant and hp with nitro, i then released and removed dryer and purged nitro, i replaced with new dryer and tripple evaced system, i have recharged with r404a and have found every thing so far is ok, looks like all i had to do was clean cond in first place and all proberly would have been sweet, anyways im sure ill be more visualant in future with tagging, ill keep you informed as to wats happens with unit, ill be able to inform accurate pressures too once cabinet down to temp, thanks again for your replies nike & piersons_man talk soon

  11. #11
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: appears short of refrigerant

    Quote Originally Posted by TECH TIM View Post
    hi guys, how are we? just want to keep tou all up to date with this one, what i have worked out is the system was actually charged with r404a, and was tagged r22, i must not have been thinkin that day, therefore i have topped up r22 on r404a obviously not good, i have returned and recovered refrigerant and hp with nitro, i then released and removed dryer and purged nitro, i replaced with new dryer and tripple evaced system, i have recharged with r404a and have found every thing so far is ok, looks like all i had to do was clean cond in first place and all proberly would have been sweet, anyways im sure ill be more visualant in future with tagging, ill keep you informed as to wats happens with unit, ill be able to inform accurate pressures too once cabinet down to temp, thanks again for your replies nike & piersons_man talk soon
    Good for you!
    Now you learned two things:

    1. Clean evaporator and condenser an check proper air flow (or water) before you attach gauges (in fact, do not ever take your tools before that except for cleaning purposes). That goes for every service job in this trade.
    2. Never add charge before you evaluate performance by organized method like this one

  12. #12
    Join Date
    Nov 2008
    Location
    NELSON BAY AUST
    Age
    43
    Posts
    48
    Rep Power
    0

    Re: appears short of refrigerant

    Never add charge before you evaluate performance by organized method like this one

    thank you muchly nike this is very helpful, i know it is what you have posted basically but i will use this thanks again

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. Leak Testing?
    By Thana in forum Trouble Shooting
    Replies: 36
    Last Post: 31-08-2010, 02:57 PM
  3. CARE refigerants by BOC
    By dogma in forum Refrigerants
    Replies: 8
    Last Post: 23-03-2010, 12:39 PM
  4. MHI FDCA400HKXRE4 Tech Info Please
    By L.JT in forum Trouble Shooting
    Replies: 5
    Last Post: 23-08-2008, 11:00 PM
  5. fun quiz
    By Brian23 in forum New to RE
    Replies: 6
    Last Post: 02-10-2007, 10:18 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •