Results 1 to 35 of 35
03-02-2009, 09:48 AM #1
How's water reacting under vacuum
I wondered how fast water evaporates at very high vacuum levels so that we could visualize a vacuum process in our refrigeration systems better.
A client tied a bottle of water with duct tape behind the window of a huge deep vacuum machine and pulled it vacuum.
It evaporates first and i finally freezes and the splashes freezes against the window.
I think this is a unique movie.
I posted this movie (33MB) on http://rapidshare.com/files/190366409/MOV01357.MPG
03-02-2009, 10:45 AM #2
Re: How's water reacting under vacuum
Very impressive and also didactic. I will use it for trainings.
Thanks Frank
03-02-2009, 11:07 AM #3
I am sure that I have read some where that the freezing point of water actualy rises above 0 degrees C at high vacuum levels. I will have to have another look. But as for the video its great
03-02-2009, 11:25 AM #4
Removing water in quantity from a system under a high vacuum requires heat as well as low pressure. In fact it's largely governed on the ambient temperature at the machine as well as the prevailing pressure in the system.
Too high a vacuum depresses the boiling point and ice can be the result. Removal in that condition uses sublimation and the removal rate is very slow.
It's worth looking at the tables used in absorption systems which will provide the boiling point at the ambient temperatures.
There is a technique for removing large amounts of moisture from chillers, typically after a tube burst, and it's not a quick process and certainly not just throwing a vacuum pump on and leaving it.
03-02-2009, 11:32 AM #5
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
03-02-2009, 11:46 AM #6
Is this not the reason why we encourage engineers to use triple evacuation method with OFN purge between & then double check that no moisture is left with vacume pressure rise test ?
If any liquid water left in the refrigeration tubes becomes ice during vac then it should melt & become vapor during the pressure rise test & make reduced vac reading.
Problem is very few engineers seem to bother with this procedure.
03-02-2009, 11:50 AM #7
03-02-2009, 01:00 PM #8
05-02-2009, 09:11 AM #9
dont know where u might have read this but i was under the impression that if the pressure is lowered so is the boiling/freezing temp...same as refrigerants...thus vacuum applied to the sealed system causes water to evaporate at same ambient ...is this not basic knowledge taught to 1st years
05-02-2009, 01:42 PM #10
obviously I must be thick
05-02-2009, 02:29 PM #11
The worst thing is trying to evac a freezer after a low side leak, while trying to keep everything in the freezer cold so the owner doesn't lose stock.
It doesn't work
I got blockages in the system after trying that. In the end I had to reclaim, and heat up the evap with a turbo torch while evacuating the second time.
05-02-2009, 02:47 PM #12
05-02-2009, 03:35 PM #13
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
06-02-2009, 06:00 AM #14
It is 24°C in the vacuum chamber.
PeterIt's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
06-02-2009, 11:04 AM #15
We had a large centrif split and If you want to vac out a split chiller fast,, use more than one vac pump. But we also had 4 x 3Kw blow heaters and put up plastic sheeting up to encase the whole chiller in an ambient of 40*c. This reduced the vac out time by half.
Higher ambient temps always speed up moisture removal. You wont remove water if the piping enviroment is below -0*c
06-02-2009, 04:38 PM #16
06-02-2009, 07:54 PM #17
I will ask once he's doing the test again and continues it's vacuum while the water is frozen.
Wonder if you see any change in the ice level.
This machine can go really, realy deep in vacuum.
Last stage is a diffusion pump http://en.wikipedia.org/wiki/Diffusion_pump and in the newer versions, they use turbomolecular pumps http://en.wikipedia.org/wiki/Turbomolecular_pump (price +/- 25,000 €/pump and +/- 6 to 10 pumps /chamber)It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
06-02-2009, 08:04 PM #18
Peter_1,
Very impressive video. Thanks for this effort. I am just wondering what would be the size of vacuum pump used here and what vacuum level it was maintaining inside the chamber - considering the relative ease with which the water was boiled and frozen.
06-02-2009, 08:19 PM #19
See http://www.refrigeration-engineer.co...ead.php?t=5660 and http://www.refrigeration-engineer.co...ead.php?t=5203
I can stand in the chamber.
They reach a vacuum in the range of 10^-8 PaIt's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
06-02-2009, 08:30 PM #20
Thermatech,
I do triple evacuation in my service jobs - but my understanding is that the triple evacuation is done to get the residual moisture out of compressor oil!
With the smaller capacity (regularly well maintained) vacuum pumps that we use in the field , I wonder if we can freeze water inside the system - to be frank it is a struggle reaching 500Microns!
By the way, 100 - 200LPM pumps are generally used in India for field system vacuumising. By any chance, do contractors use bigger pumps in UK or other places?
08-02-2009, 06:44 AM #21
08-02-2009, 08:07 AM #22
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
And how is that better way off doing things then Paul is done at domestic freezer. For every filter replacement, I suppose that you need to reclaim refrigerant, braze new filter under nitrogen and evacuate and recharge new refrigerant. If you do it like that few times, how much do you think it will cost the owner of that freezer to do things in that way. Or you work for banans?
08-02-2009, 08:20 AM #23
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
When lowering chamber pressure, water evaporates and takes heat from surrounding water (there is not possible to change in state of the matter without heat is taken from surrounding) because in that chamber all heat from surrounding is gone with vacuumed air. That is why water freezes and that is why in chamber is no more 24°C when water start to freeze.
So it is not 24°C water temperature when it starts to freeze and nothing amazing is happening except physics laws at act.Last edited by nike123; 08-02-2009 at 08:31 AM.
08-02-2009, 08:23 AM #24
You only need to pump it down to the receiver, you don't need to reclaim it. Pumping down takes only the time to walk to your van for a new dryer.
I don't need to breeze new filters because they're all fitted with euro-couplings.
I even fitted for the same problem 3 dryers in line - after evacuating first as much as possible - and came back the other day to replace once again the 3 dryers for 1 final dryer.
There's also something like expensive labor hours. Evacuating water takes much more time then removing it with a dryer. Practice has shown that you never can remove water with a vacuum pump in a reasonable time. I had a thread some time ago with a broken PHE and we had buckets of water in the system.
But there's nothing wrong with Paul's method.
I always heat up the coil while evacuating, especially in a freezer because the moisture will stay there.It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
08-02-2009, 08:24 AM #25
08-02-2009, 08:26 AM #26
08-02-2009, 08:41 AM #27
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
I agree with you when systems are big, not hermetical sealed and have receivers etc....
That is not what I (and Paul, if I got it correctly) was talking about.
When I work on hermetically sealed system I leave it like that. I was talking about small domestic hermetical sealed systems :
08-02-2009, 08:47 AM #28
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
I am sure that water doesn't freeze at 24°C at any vacuum level. Here is case of higher heat removal (by change of state) than heat gain (from surrounding) in water which rapidly evaporate.
Also, in that high vacuum, there is not much matter to transfer heat by conduction and only significant heat could be transferred by IR radiation. Dont forget, vacuum is best isolator.
08-02-2009, 08:52 AM #29
08-02-2009, 08:55 AM #30
08-02-2009, 09:09 AM #31
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Local adage (i taught it is more broader term) used when somebody compares two un-comparable things.
Paul never said that this job was on a domestic freezer.
Winja didn't reply to Paul's message about a domestic freezer nor cooler I suppose. (TXV in his message)
And who's repairing a leak on a domestic freezer anyway?
08-02-2009, 09:18 AM #32
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
08-02-2009, 12:12 PM #33
relax people.
I don't always work on domestics, in fact I try not too*
But I wouldn't be worried in the owner losing stock or keeping the freezer cold if it was a domestic would I? . It was a very small commercial unit.
It was a small freezer room in a fishing shop, so lots of frozen fish that needed to be kept cold, but a very small condensing unit, no reciever etc. So uneconomical to repair using drier changes and multiple visits as you couldn't pump down, you'd need to do full reclaims and recharges.
edit: *Domestic a/c, yes I work on that, domestic refrig however, I avoid. Too hard when no one stocks parts in this side of the country. Big pain when you have too may customers desperate to get their fridge running and you can't get parts for a week or more. So I avoid domestic refrig, but I don't mind domestic a/c or commercial refrig.Last edited by paul_h; 08-02-2009 at 12:20 PM.
09-02-2009, 05:25 AM #34
09-02-2009, 08:31 AM #35
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
pure water from air
By Lc_shi in forum New TechnologiesReplies: 32Last Post: 26-02-2009, 12:25 PM -
why water in a vacuum chamber freeze.
By tzur in forum TrainingReplies: 5Last Post: 10-06-2008, 03:33 PM -
open cycle R718 A/C that also provides high purity water?
By star882 in forum Technical SpeculationsReplies: 7Last Post: 27-07-2006, 04:18 AM -
problems with ice slurry production by spraying water in a vacuum chamber
By goodluck99 in forum Trouble ShootingReplies: 6Last Post: 16-04-2006, 01:27 AM -
Building a wine cabinet