    System Design Charge



    Hi all...

    I posted a similar question earlier, but that thread kinda diverged...

    Let me rephrase it slightly. If you just designed a chiller system what would be the method you would use to calculate the proper refrigerant charge.

    Just for the heck of it, let me throw in a few details....
    * Air cooled condenser
    * TXV
    * Receiver
    * condenser flooding for head pressure control
    * single hermetic compressor

    The other thread had somewhat converged to
    30% condenser volume +
    100% liquid line volume +
    80% receiver volume +
    70% evaporator volume

    All converted to the mass of refrigerant (at the proper temperatures). Any comments!?!? Everyone in agreement?!?!

    And the first time you charged this thing, would you just plug in that amount, and then fine tune with superheats / subcooling?!?!



  2. #2
    Join Date
    Jun 2008
    Location
    USA
    Posts
    27
    Rep Power
    0

    Re: System Design Charge

    No takers?!?!?!

    I would have thought this would have been a very basic question, as anyone/everyone who has designed a new system would have to come up with a number to put on the name-plate.


  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: System Design Charge

    Quote Originally Posted by cool-hvacer View Post
    No takers?!?!?!

    I would have thought this would have been a very basic question, as anyone/everyone who has designed a new system would have to come up with a number to put on the name-plate.

    That number doesn't come from calculation. It comes by fine tuning of system components and testing of performance in all operating conditions in predicted operating envelope.

    It cannot be calculated with satisfactory accuracy for that pourpose. You could only calculate amount of refrigerant needed to have on stock for service job rough estimation purpose or simmilar tasks.

    http://www.defra.gov.uk/environment/...pport-gen5.pdf


    And what about answering to thread which you, somehow, abandoned?
    Last edited by nike123; 12-02-2009 at 07:14 AM.

  4. #4
    Join Date
    Jun 2008
    Location
    USA
    Posts
    27
    Rep Power
    0

    Re: System Design Charge

    Not abandoned..... Before I can give better measurements, I have to visit the facility where the equipment is located - its quite remote!! Actually, at 14 000ft altitude, so that also makes things a little more interesting.

    For the charge question:

    I could counter your assertion by asking if its a brand new machine, how do they come up with the number that they put on the nameplate, but I guess that they could operate the equipment in their plant after they first manufacture, and tune it properly / measure proper refrigerant charge there before they send it out....?!?!

    Oh ya - Thanks for the link...

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: System Design Charge

    Quote Originally Posted by cool-hvacer View Post
    Not abandoned..... Before I can give better measurements, I have to visit the facility where the equipment is located - its quite remote!! Actually, at 14 000ft altitude, so that also makes things a little more interesting.
    Only for condenser size! If correctly sized, there is no problem! But that we will see after measurements are done at air side of condenser.
    For the charge question:

    I could counter your assertion by asking if its a brand new machine, how do they come up with the number that they put on the nameplate, but I guess that they could operate the equipment in their plant after they first manufacture, and tune it properly / measure proper refrigerant charge there before they send it out....?!?!
    When I visited plant which manufacture chillers by order (Geoclima) they showed me their test room and told me that for every new custom order they need to test equipment and fine adjust charge.

    Also, because of huge difference in volume of gas phase and liquid phase (check this thread) it is practically impossible to to calculate correct amount of refrigerant since small mass of evaporated/flashed refrigerant makes huge difference in occupied volume of equipment parts.
    Last edited by nike123; 13-02-2009 at 07:05 AM.

Similar Threads

  1. first estimate of system charge
    By cool-hvacer in forum Fundamentals
    Replies: 25
    Last Post: 03-02-2009, 10:34 AM
  2. Refrigeration system charge calculation query.
    By refriengr in forum Fundamentals
    Replies: 0
    Last Post: 29-05-2008, 08:03 PM
  3. System design
    By coolerboy in forum Fundamentals
    Replies: 5
    Last Post: 30-08-2007, 08:11 PM
  4. Fan model for system optimization
    By autt in forum System Optimization
    Replies: 8
    Last Post: 31-03-2007, 05:34 AM
  5. Total System Charge
    By dallan in forum Fundamentals
    Replies: 1
    Last Post: 27-12-2004, 08:18 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •