    condenser



    Just a thought.....
    A condensor that is used for both water heating and air drying. Is it possible to get both service with the same condensor at the same time?



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: condenser

    Quote Originally Posted by mkpo View Post
    Just a thought.....
    A condensor that is used for both water heating and air drying. Is it possible to get both service with the same condensor at the same time?
    You cannot dry air with condenser.

  3. #3
    Join Date
    Feb 2009
    Location
    Nepal
    Posts
    20
    Rep Power
    0

    Re: condenser

    I mean both heating water and heating air simultaneously with the same condensor at the same time......

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: condenser

    Quote Originally Posted by mkpo View Post
    I mean both heating water and heating air simultaneously with the same condensor at the same time......
    I don't see way how could water and air could pass same condenser in same time without mixing.
    Could you describe what you want to do more detailed.

  5. #5
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    974
    Rep Power
    20

    Re: condenser

    Paul


    "KEEP IT COOL"

  6. #6
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: condenser

    yep superswill you are correct you can have underfloor heating, water and have a fan coil also connected to heat the air, spot on.
    this system will do space heating, space cooling, hotwater on the heat pump and solar hot water.
    a very good air to water source heat pump.
    best in the market if applied correctly.. all refrigeration engineers should be trained on this as it will give them heaps of domestic work in the winter.

  7. #7
    Join Date
    Feb 2009
    Location
    Nepal
    Posts
    20
    Rep Power
    0

    Re: condenser

    I want to use it for heating the tap water from 15 degree C to 65 degree C. I need 0.1kg/s of mass flow rate of the water and half an hour can be given for condenser to heat up water. After heating water, i want to use the same condensor to heat up dry air of quite low RH (20%) to improve the moisture absorbing capacity of the air...later that hot and dry air can be used for drying clothes in laundary.....Because of space limitation,I need a compact air source heat pump system with compact set of condensor, evaporator, compressure and expansion valve.....A good idea would be appriciated.....
    martin
    Sweden

  8. #8
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: condenser

    by the sounds of what you want to do it sounds like you will need a buffer tank to heat up with the heat pump, the maximum temp you will get with the Altherma is 55 degrees depending on conditions. this would probably do the trick for you.

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. High discharge temp
    By paul_h in forum Air Conditioning
    Replies: 48
    Last Post: 06-05-2009, 11:10 AM
  3. Air Cooled Condenser Leakage Problem with R-404A
    By RADHAKRISHNARAO in forum Technical Discussions
    Replies: 19
    Last Post: 30-07-2008, 12:21 PM
  4. method to design air cooled condenser
    By abbasi in forum New Technologies
    Replies: 4
    Last Post: 12-02-2008, 08:34 AM
  5. Optimum condenser fan speed
    By star882 in forum Fundamentals
    Replies: 4
    Last Post: 27-02-2006, 01:50 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •