Just a thought.....
A condensor that is used for both water heating and air drying. Is it possible to get both service with the same condensor at the same time?
02-02-2009, 09:56 PM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
02-02-2009, 10:12 PM #3
Re: condenser
I mean both heating water and heating air simultaneously with the same condensor at the same time......
02-02-2009, 10:21 PM #4
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
02-02-2009, 10:23 PM #5
Re: condenser
do you mean one of these
http://www.spacealtherma.com:8080/in...ng=en&site=250Paul
"KEEP IT COOL"
02-02-2009, 10:45 PM #6
Re: condenser
yep superswill you are correct you can have underfloor heating, water and have a fan coil also connected to heat the air, spot on.
this system will do space heating, space cooling, hotwater on the heat pump and solar hot water.
a very good air to water source heat pump.
best in the market if applied correctly.. all refrigeration engineers should be trained on this as it will give them heaps of domestic work in the winter.
03-02-2009, 08:47 AM #7
Re: condenser
I want to use it for heating the tap water from 15 degree C to 65 degree C. I need 0.1kg/s of mass flow rate of the water and half an hour can be given for condenser to heat up water. After heating water, i want to use the same condensor to heat up dry air of quite low RH (20%) to improve the moisture absorbing capacity of the air...later that hot and dry air can be used for drying clothes in laundary.....Because of space limitation,I need a compact air source heat pump system with compact set of condensor, evaporator, compressure and expansion valve.....A good idea would be appriciated.....
martin
Sweden
03-02-2009, 08:19 PM #8
Re: condenser
by the sounds of what you want to do it sounds like you will need a buffer tank to heat up with the heat pump, the maximum temp you will get with the Altherma is 55 degrees depending on conditions. this would probably do the trick for you.
Superheat and Subcooling
By Chunk in forum FundamentalsReplies: 42Last Post: 15-01-2011, 01:24 AM -
High discharge temp
By paul_h in forum Air ConditioningReplies: 48Last Post: 06-05-2009, 11:10 AM -
Air Cooled Condenser Leakage Problem with R-404A
By RADHAKRISHNARAO in forum Technical DiscussionsReplies: 19Last Post: 30-07-2008, 12:21 PM -
method to design air cooled condenser
By abbasi in forum New TechnologiesReplies: 4Last Post: 12-02-2008, 08:34 AM -
Optimum condenser fan speed
By star882 in forum FundamentalsReplies: 4Last Post: 27-02-2006, 01:50 AM