Installed a 3 ton 410a American Standard heat pump condenser with a new lineset. I put 100psi pressure test on lineset and detected no leak . then pulled vaccum and still no leak. when i cracked the valves open and and released refrigerant. A weld gave way on the 3/8 line just enough to make a small drip of oil appear. Step by step what should i do ?? Any advice would be greatly appreciated thank you.
-
01-02-2009, 04:45 PM #2
Re: Heat pump help
Welcome!
100 psi (6,9 bar) is not enough to do the pressurization test, for this reason you have this problem.For R410A the standard testing value is 40bar(580psi). Also you have to let the system under pressurization enough time in order to be sure that there is not any leak.
Now you have to recover all the refrigerant, repair the leak, vacumming the system, charging with the right charge and run it.
-
01-02-2009, 04:47 PM #3
Re: Heat pump help
The recommended pressure for strength testing on R410a is 600psig. Your test at 100psi would not show up any defects in the pipework installation.
I'm assuming that you used oxygen free nitrogen for testing?
Vacuum testing is only for detecting the presence of moisture, not for leak testing.
Have you been doing this very long??Last edited by frank; 01-02-2009 at 04:49 PM.
-
02-02-2009, 11:32 PM #4
Re: Heat pump help
600 psi???
is that safe?
i've read on some condenser plates that the maximum pressure must be arround 450 psi, what happens if one over pressurizes the system?
-
02-02-2009, 11:57 PM #5
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
03-02-2009, 08:43 AM #6
Re: Heat pump help
Heating mode example
In Europe split systems which are refrigerant R410a & have a high pressure safety switch are often set at 41.5 bar cutout.
Think about what will happen if the enduser forgot to clean the indoor unit filter & the system is running in heating mode
then
the system will run up to over 40 bar with poor air flow through the indoor unit coil.
Provided you have carried out the interconnect refrigeration pipe strength test at over 40 bar then you have proved that the pipe & joint connections are strong enough for that possible running condition.
Similar Threads
-
Capacity control
By sparrow in forum TrainingReplies: 44Last Post: 18-01-2010, 07:49 PM -
DIY heat pump 12kW
By kimusabi in forum FundamentalsReplies: 11Last Post: 17-10-2009, 07:50 PM -
frostles heat pump
By Lc_shi in forum New TechnologiesReplies: 27Last Post: 31-03-2008, 07:53 AM -
Domestic VRF heat pump?
By electronicsuk in forum Heat PumpsReplies: 8Last Post: 30-10-2007, 07:53 AM -
heat pump capacity adjust
By Lc_shi in forum FundamentalsReplies: 5Last Post: 14-02-2006, 07:32 AM