Thread: Heat pump help

  1. #1
    guest's Avatar
    guest Guest

    Heat pump help



    Installed a 3 ton 410a American Standard heat pump condenser with a new lineset. I put 100psi pressure test on lineset and detected no leak . then pulled vaccum and still no leak. when i cracked the valves open and and released refrigerant. A weld gave way on the 3/8 line just enough to make a small drip of oil appear. Step by step what should i do ?? Any advice would be greatly appreciated thank you.



  2. #2
    Join Date
    Sep 2006
    Location
    italy
    Age
    53
    Posts
    93
    Rep Power
    18

    Re: Heat pump help

    Welcome!
    100 psi (6,9 bar) is not enough to do the pressurization test, for this reason you have this problem.For R410A the standard testing value is 40bar(580psi). Also you have to let the system under pressurization enough time in order to be sure that there is not any leak.

    Now you have to recover all the refrigerant, repair the leak, vacumming the system, charging with the right charge and run it.

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Heat pump help

    The recommended pressure for strength testing on R410a is 600psig. Your test at 100psi would not show up any defects in the pipework installation.

    I'm assuming that you used oxygen free nitrogen for testing?

    Vacuum testing is only for detecting the presence of moisture, not for leak testing.

    Have you been doing this very long??
    Last edited by frank; 01-02-2009 at 04:49 PM.

  4. #4
    Join Date
    Jan 2009
    Location
    Earth
    Posts
    75
    Rep Power
    16

    Re: Heat pump help

    600 psi???

    is that safe?
    i've read on some condenser plates that the maximum pressure must be arround 450 psi, what happens if one over pressurizes the system?

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Heat pump help

    Quote Originally Posted by frostedflake View Post
    600 psi???

    is that safe?
    i've read on some condenser plates that the maximum pressure must be arround 450 psi, what happens if one over pressurizes the system?
    In hot days near or above 100°F you could easy have 500 psi of normal working pressure of R410A in condenser.

  6. #6
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: Heat pump help

    Heating mode example

    In Europe split systems which are refrigerant R410a & have a high pressure safety switch are often set at 41.5 bar cutout.

    Think about what will happen if the enduser forgot to clean the indoor unit filter & the system is running in heating mode
    then
    the system will run up to over 40 bar with poor air flow through the indoor unit coil.

    Provided you have carried out the interconnect refrigeration pipe strength test at over 40 bar then you have proved that the pipe & joint connections are strong enough for that possible running condition.

Similar Threads

  1. Capacity control
    By sparrow in forum Training
    Replies: 44
    Last Post: 18-01-2010, 07:49 PM
  2. DIY heat pump 12kW
    By kimusabi in forum Fundamentals
    Replies: 11
    Last Post: 17-10-2009, 07:50 PM
  3. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  4. Domestic VRF heat pump?
    By electronicsuk in forum Heat Pumps
    Replies: 8
    Last Post: 30-10-2007, 07:53 AM
  5. heat pump capacity adjust
    By Lc_shi in forum Fundamentals
    Replies: 5
    Last Post: 14-02-2006, 07:32 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •