    medium temp pumpdown vs no pump down



    hi all,
    i was wondering about the purpose of pumpdown for small medium (4 deg) temp coolroom, 1.25hp condensing unit. why do pumpdown? is it to prevent refrigerant migration on the off cycle and slugging at startup? i mostly see non-pumpdown on smaller units so is there any reason for doing it? like if the condensing unit is likely to get colder than the room?
    thoughts, experiences.....
    cheers



  2. #2
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: medium temp pumpdown vs no pump down

    Quote Originally Posted by Harrison View Post
    hi all,
    i was wondering about the purpose of pumpdown for small medium (4 deg) temp coolroom, 1.25hp condensing unit. why do pumpdown? is it to prevent refrigerant migration on the off cycle and slugging at startup? i mostly see non-pumpdown on smaller units so is there any reason for doing it? like if the condensing unit is likely to get colder than the room?
    thoughts, experiences.....
    cheers
    with your ambient temp above your "coolroom" (4deg) refrigerant will migrate to the evaporator, then bring liquid back to the compressor on start up, or with your ambient temp below your "coolroom" refrigerant will migrate to the compressor unless crankcase heater is in use

  3. #3
    Join Date
    Jun 2008
    Location
    Australia
    Posts
    22
    Rep Power
    0

    Re: medium temp pumpdown vs no pump down

    yeah as i thought, but non pump down is a very common arrangement on small systems that dont have sump heaters, so it would seem that practically they work. is there a rule of thumb when to use which, under what circumstances?
    cheers

  4. #4
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: medium temp pumpdown vs no pump down

    small splits years ago i used to look at had no expansion valve which when used on larger units would open fully upon evaporator temp increase allowing full flow, capillary distributor still restricts flow. By the time it takes to equalise pressure the condensor and receiver are still below compressor temp and majority of refrigerant will remain there. But I suppose in theory migration to compressor as well is still possible under right conditions

  5. #5
    Join Date
    Jan 2009
    Location
    Queensland
    Age
    64
    Posts
    113
    Rep Power
    16

    Re: medium temp pumpdown vs no pump down

    Harrison, one reason that LP pump down is used on remote condensed coolrooms is to make it easier to set up. no wiring between cold room and condensing unit. It also helps with cyclic defrost. System pumps down when down to temp, set the LP cutin to say 4 or 5C equivalent and to cut out 3 or 4 PSI below normal operating pressure. Then if you get an ice up, your suction pressure will drop and cut out the LP control and it should stay off till the evap is defrosted.
    If you're just worried about floodback on start up, you could wire your LLSV to cycle with the compressor and put it at the condensing unit.

Similar Threads

  1. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  2. Replies: 3
    Last Post: 06-11-2006, 05:04 AM
  3. R406a for high temp heat pump
    By Lc_shi in forum Refrigerants
    Replies: 1
    Last Post: 14-10-2005, 09:08 PM
  4. Oil Migration - R22 medium temp refrigeration system
    By lurioda in forum Trouble Shooting
    Replies: 10
    Last Post: 09-03-2004, 03:38 PM
  5. Multiplex For Low Temp and Medium Temp
    By allanbaker in forum Technical Discussions
    Replies: 0
    Last Post: 28-11-2002, 10:15 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •