Results 1 to 10 of 10
Thread: Key role of dehumidifiers
30-01-2009, 06:26 AM #1
Is dehumidifier necessary in addion to a split aircon for a ammunition bunker ?
30-01-2009, 07:00 AM #2
Re: Key role of dehumidifiers
It could be, what does the user/owner of the bunker say?
What are the storage requirement conditions.Brian - Newton Abbot, Devon, UK
31-01-2009, 03:40 PM #3
if you are required to have tight humidity control, I would say yes you need a dehu
a bunker sounds like concrete,-- no windows to let solar heat in, no lights and computers running to create an internal load so not much to make an AC unit run on temperature control.Take the V out of HVAC and you are left with a HAC job
01-02-2009, 08:06 PM #4
Depending on the requirements and the type of aircon. A concrete underground or semi underground bunker will be humid and have relatively low heatload. In this situation then unless close control units are fitted then a dehumidifier will be the more efficient option.
Brit
02-02-2009, 11:52 AM #5
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Ammunition bunker require controlled humidity because some of ammunition is sensitive to condensate and when cold ammunition comes from outside in to relatively hot bunker, surface condensation could occur at ammunition and that could be dangerous. Therefore dehumidifier is needed to keep dew point as low as possible. In fact bunker cooling is not necessary since in there is probably always around 14°C but humidity should be controlled.
03-02-2009, 01:33 AM #6
Thanks nike how come you say that bunker temperature always remain 14 degree celcius
How to calculate the required capacity of a dehumidifier for a bunker size 7m x 5m x 4m to maintain a humidity level in the range of 40 % to 50%
03-02-2009, 09:44 AM #7
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Bunker for ammunition on which I worked here are always underground. Therefore temperature of 14°C.
http://www.bry-air.com/tech-center/e...s/default.html
http://www.bry-air.com/tech-center/e...g/default.html
04-02-2009, 04:54 AM #8
Thanks nike you are helping me a lot
04-02-2009, 05:44 AM #9
As far as I know we dont need to do that for such requirments and the AC is more than enough and well do the required
04-02-2009, 08:46 AM #10
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Role call
By Reeferjon in forum TransportReplies: 167Last Post: 07-10-2008, 04:18 PM -
Dehumidifiers and Rotary Compressors
By Pete L in forum CommercialReplies: 3Last Post: 16-10-2007, 11:06 PM -
Domestic dehumidifiers - are customers being deceived?
By Psychro in forum Air ConditioningReplies: 7Last Post: 08-06-2007, 04:19 PM