    Broken antivibration pipe



    I have one case where on compressor discharge has mounted anti vibration pipe which has leaked refrigerant out after only few days of operation.
    Only data on pipe is HTH 37-08.
    Does anyone know who is manufacturer of these anti vibrators.

    What is correct term for them to search for manufacturers and their technical details? I forgotten English term for them. I think that we here use term "vibroflex"

    Used refrigerant here is R410A and I fear that used anti vibrator is not strong enough for R410A pressures.
    Unit is new one on the market. It is Galletti air to water heat pump MPE 028HO which is their first medium size system at R410A refrigerant.

    Here is partial picture of anti vibration pipe.
    Last edited by nike123; 29-01-2009 at 08:43 PM.



  2. #2
    Join Date
    Jan 2008
    Location
    Australia
    Posts
    71
    Rep Power
    17

    Re: Broken antivibration pipe



    Hi Nike,
    I just copied this form a catalogue I have. Down here we just call them vibration eliminators. The burst pressure is 500 psi on the one's I use.

    VIBRATION ELIMINATORS
    PIERCING & LINE TAP VALVES
    SUITABLE FOR ALL HFC/HCFC/CFC REFRIGERANTS (Not ammonia)
    Maximum Test Pressure: 1-1/2 times Operating Pressure shown above.
    Minimum Burst Pressure: 5 times Operating Pressure shown above.
    • Vibration eliminators are used in the suction and discharge lines of refrigeration and air conditioning systems.
    • They are most effective when installed as close as possible to the compressor, preferably in a horizontal position (but
    not essential), with the refrigerant line anchored at the furthest end from the source of vibration.
    • Care should be taken to ensure that the vibration eliminator is not under static tension after soldering in place. They are
    not designed to compensate for lines that are out of alignment, so make sure lines are straight and in in line.
    • High temperature alloys


    Hope this helps.

    dsp

    Last edited by Brian_UK; 29-01-2009 at 08:59 PM. Reason: Font size increased.

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Broken antivibration pipe

    Quote Originally Posted by dsp View Post


    Hi Nike,
    I just copied this form a catalogue I have. Down here we just call them vibration eliminators. The burst pressure is 500 psi on the one's I use.

    VIBRATION ELIMINATORS
    PIERCING & LINE TAP VALVES
    SUITABLE FOR ALL HFC/HCFC/CFC REFRIGERANTS (Not ammonia)
    Maximum Test Pressure: 1-1/2 times Operating Pressure shown above.
    Minimum Burst Pressure: 5 times Operating Pressure shown above.
    • Vibration eliminators are used in the suction and discharge lines of refrigeration and air conditioning systems.
    • They are most effective when installed as close as possible to the compressor, preferably in a horizontal position (but
    not essential), with the refrigerant line anchored at the furthest end from the source of vibration.
    • Care should be taken to ensure that the vibration eliminator is not under static tension after soldering in place. They are
    not designed to compensate for lines that are out of alignment, so make sure lines are straight and in in line.
    • High temperature alloys


    Hope this helps.

    dsp


    Thanks dsp!
    Do you have manufacturer name of that vibration eliminators?

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Broken antivibration pipe

    Does anyone have any names of vibration eliminators manufacturers in Italy or in EU?

    I found:
    Carly

    http://www.vibrasorbers.com/

    These Chinese is only 35 bar rated (500psig):
    http://cntw.en.alibaba.com/product/2..._absorber.html

    These are only 28 bars rated (fi 22)
    http://www.amnitec.nl/UserFiles/File/Vibes.pdf
    Last edited by nike123; 29-01-2009 at 09:57 PM.

  5. #5
    Join Date
    Nov 2005
    Location
    New Zealand
    Posts
    550
    Rep Power
    19

    Re: Broken antivibration pipe

    Quote Originally Posted by nike123 View Post
    Does anyone have any names of vibration eliminators manufacturers in Italy or in EU?

    I found:
    Carly

    http://www.vibrasorbers.com/

    These Chinese is only 35 bar rated (500psig):
    http://cntw.en.alibaba.com/product/2..._absorber.html

    These are only 28 bars rated (fi 22)
    http://www.amnitec.nl/UserFiles/File/Vibes.pdf
    Hi Nike I always used Anaconda

    http://www.universalmetalhose.com/pr..._vibration.htm

    Regards Norm

    Sorry I posted the same post twice
    Last edited by Toosh; 30-01-2009 at 03:54 AM. Reason: addition
    My wife used to say you never listen to a word I say at least I think that what she said

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Broken antivibration pipe

    Quote Originally Posted by Toosh View Post
    Hi Nike I always used Anaconda

    http://www.universalmetalhose.com/pr..._vibration.htm

    Regards Norm

    Sorry I posted the same post twice

    They are no good, for fi22 maximum operating pressure is 30 bar.
    On high side I normally have 30-35 bar.

  7. #7
    Join Date
    Nov 2005
    Location
    New Zealand
    Posts
    550
    Rep Power
    19

    Re: Broken antivibration pipe

    Hi Nike, I have found anaconda failure in stressed piping, meaning the pipe has been been cut to short and pulled into fit which creates stress, and most products are usually have a failure point well above the operating pressure

    Norm
    My wife used to say you never listen to a word I say at least I think that what she said

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Broken antivibration pipe

    Quote Originally Posted by Toosh View Post
    Hi Nike, I have found anaconda failure in stressed piping, meaning the pipe has been been cut to short and pulled into fit which creates stress, and most products are usually have a failure point well above the operating pressure

    Norm
    Could be the case here, but I still want to find equipement rated for higher operation pressure.


  9. #9
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Broken antivibration pipe

    You might try some suppliers of hydraulic hoses and fittings. The pressures and fluids they work with could provide a reasonable option for you.
    If all else fails, ask for help.


  10. #10
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Broken antivibration pipe

    Quote Originally Posted by US Iceman View Post
    You might try some suppliers of hydraulic hoses and fittings. The pressures and fluids they work with could provide a reasonable option for you.
    I am more leaned toward fitting plain annealed copper pipe in place of this vibration eliminator bended to compensate for this vibrations

  11. #11
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    974
    Rep Power
    20

    Re: Broken antivibration pipe

    nike

    do you have the space to replace the anti vibration pipe with a small coil shaped piece copper piper? i have had this problem on an old airdale package and made up a loop the loop arrangement of 5/8th and fitted that in its place,ok it it would not win a beauty pageant but it has done the job
    Paul


    "KEEP IT COOL"

  12. #12
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Broken antivibration pipe

    Quote Originally Posted by nike123 View Post
    I am more leaned toward fitting plain annealed copper pipe in place of this vibration eliminator bended to compensate for this vibrations
    If the tubing is small enough for you to bend it into multiple loops, that might be OK. One thing to remember though... If the loop is vertical, it can trap oil or other in it during shutdown. If the loop is horizontal you can arrange it so the loop drains freely.

    I have used some of the hydraulic hoses and connectors before and had good luck with them.
    If all else fails, ask for help.


  13. #13
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Broken antivibration pipe

    Quote Originally Posted by US Iceman View Post
    If the tubing is small enough for you to bend it into multiple loops, that might be OK. One thing to remember though... If the loop is vertical, it can trap oil or other in it during shutdown. If the loop is horizontal you can arrange it so the loop drains freely.

    I have used some of the hydraulic hoses and connectors before and had good luck with them.
    I think that 3 U turns in different planes and arm of pipes in length of 30-40cm will be sufficient.
    This should be the shape but without elbows ( pipe would be from one piece and bended in this shape).



    It is small scroll of 25 kW of refrigeration power and not much vibrations from what I seen first few days.
    Maybe cause of vibration eliminator failing was fact that few days before failing unit was out of level some 3-5° because of unit anti vibration foots are fall out on one side of unit.
    Last edited by nike123; 31-01-2009 at 12:23 PM.

  14. #14
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Broken antivibration pipe

    I think the pressure rating of vibration eliminators drops as the size increases. What size pipe is it used with?

    Jon

  15. #15
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Broken antivibration pipe

    Quote Originally Posted by monkey spanners View Post
    I think the pressure rating of vibration eliminators drops as the size increases. What size pipe is it used with?

    Jon

    22mm at discharge of compressor to the reversing valve.

  16. #16
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Broken antivibration pipe

    Follow US iceman post,
    I only use SS vibration eliminators from the hydraulic sector, they are made up to 400 Bar.

    On the other hand, Why use VE on hermetic compressor?

  17. #17
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Broken antivibration pipe

    Quote Originally Posted by chemi-cool View Post
    Follow US iceman post,
    I only use SS vibration eliminators from the hydraulic sector, they are made up to 400 Bar.
    I think it is too expensive and complicated to fit if there is no brazing connections at them. I also don't know where to find them here. Could you point me to some page where i could find more technical details and connection options?

    On the other hand, Why use VE on hermetic compressor?
    It appears that someone in construction department of this unit thinking that they are necessary. Although, they are not fitted at suction side.

  18. #18
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Broken antivibration pipe

    Most of the energy for vibration is in the discharge lines, so that makes sense if you want to prevent the vibration (or noise) from traveling.

    3 changes in direction for the loops is typical of expansion loops for increased flexibility to prevent pipe rupture or failure due to temperature related growth or shrinking of pipes. However, I do not think this will do very much for reducing vibration.

    The issue with vibration is; trying to prevent the mechanical vibrations from creating mechanical failures or transmitting noise.
    If all else fails, ask for help.


  19. #19
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Broken antivibration pipe

    Hi Nike,
    I will try to get you some pictures of these VE soon.

    About hermetic compressors, they are equipped with internal springs to absorb any vibrations. If you get any, check for broken valves.
    Don't forget that hermetics turn RPM .
    you can try to change the RST to TRS, keep the same rotation direction and some times it reduces the vibrations.

  20. #20
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Broken antivibration pipe

    Quote Originally Posted by chemi-cool View Post
    Hi Nike,
    I will try to get you some pictures of these VE soon.

    About hermetic compressors, they are equipped with internal springs to absorb any vibrations. If you get any, check for broken valves.
    Don't forget that hermetics turn RPM .
    you can try to change the RST to TRS, keep the same rotation direction and some times it reduces the vibrations.
    Thanks Chemi!
    It is Maneurop Performer scroll SH120A4ALB and it is turning right way. And, as I said earlier, I don't think that it is his vibrations what is responsible that vibration eliminator failed.

  21. #21
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Broken antivibration pipe

    Quote Originally Posted by US Iceman View Post
    Most of the energy for vibration is in the discharge lines, so that makes sense if you want to prevent the vibration (or noise) from traveling.

    3 changes in direction for the loops is typical of expansion loops for increased flexibility to prevent pipe rupture or failure due to temperature related growth or shrinking of pipes. However, I do not think this will do very much for reducing vibration.

    The issue with vibration is; trying to prevent the mechanical vibrations from creating mechanical failures or transmitting noise.
    When I was examining at initial start up of unit, I did not found that compressor makes any excessive vibrations or that vibration eliminator moves at all. In fact I found work of this compressor pretty smooth and quiet in comparison with earlier versions of Performers for R407C.

  22. #22
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Broken antivibration pipe

    Quote Originally Posted by nike123 View Post
    Thanks Chemi!
    It is Maneurop Performer scroll SH120A4ALB and it is turning right way. And, as I said earlier, I don't think that it is his vibrations what is responsible that vibration eliminator failed.
    Nike

    i have had the same problem on new 410a units that were cracking the discharge pipe and it turned out to be cheap copper tubing - replaced with soft copper tubing with minor bend to take the movement at startup - job done - should be no need for vibrosorber

  23. #23
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Broken antivibration pipe

    The Henry 7/8" 22mm vibration eliminators in my catalogue are rated at 34.5 bar, don't know what make yours was though.

  24. #24
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Broken antivibration pipe

    hi all the correct metod of using anaconda,s is that they are used in pairs= one vertical and one horizontal close together so that all the movement is taken by the anaconda,
    of corce the pipework must be fasened = no movement .
    sedgy

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. BS Box - 3 Pipe & 2 Pipe Systems.
    By Testech in forum Fundamentals
    Replies: 2
    Last Post: 05-10-2008, 07:01 PM
  3. Burst Pipe caused by Abrasion. (aka Only on a Friday)
    By Grizzly in forum Chit Chat & Service Stories
    Replies: 11
    Last Post: 19-09-2008, 06:59 PM
  4. Mitsubishi PUHZ-RP200YHA Pipe Sizes
    By gwilliamson in forum Air Conditioning
    Replies: 11
    Last Post: 14-05-2008, 09:43 PM
  5. Pipe sizes
    By benncool in forum Chit Chat & Service Stories
    Replies: 10
    Last Post: 08-07-2003, 10:58 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •