    Re: Sensible Heat Factor / capacity of Inverter split Systems at part load?

    Quote Originally Posted by nike123 View Post
    Isn't that configuration (double capacity and dehumidifier) make costs of instalation and equipment similar to those of close control equipment, and you still doesn't have right equipment for the job.
    Not to mention free cooling capability of any decent close control AC.

    Check this one!
    Nike. Have you seen my other thread asking about Hiref products? Have you had any experience with them?
    If in doubt read the instructions. If still in doubt follow them.

  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Sensible Heat Factor / capacity of Inverter split Systems at part load?

    Quote Originally Posted by Greengrocer View Post
    Nike. Have you seen my other thread asking about Hiref products?
    No I did not! I will check.

    Have you had any experience with them?
    I have been in factory and seen production of all their production range 3 years ago. They also produce large chillers for Galletti and I servicing and commissioning Galletti chillers here in my region.
    I personally never worked with Hiref close control units, so I don't have any experience in that field yet. From my visit to factory, I got impression that they are solid and that also confirm their reference list.

  3. #3
    Join Date
    Mar 2008
    Location
    England
    Age
    68
    Posts
    250
    Rep Power
    17

    Re: Sensible Heat Factor / capacity of Inverter split Systems at part load?

    Quote Originally Posted by nike123 View Post
    No I did not! I will check.


    I have been in factory and seen production of all their production range 3 years ago. They also produce large chillers for Galletti and I servicing and commissioning Galletti chillers here in my region.
    I personally never worked with Hiref close control units, so I don't have any experience in that field yet. From my visit to factory, I got impression that they are solid and that also confirm their reference list.
    Many thanks Nike. Their Inverter Close control units are interesting. First full funtion close control Inverter compressor systems I've seen. They even do a small capacity range. Problem is that the prices are very high compared to convensional splits. My search goes on I guess.
    Last edited by Greengrocer; 31-01-2009 at 02:20 PM. Reason: spelling
    If in doubt read the instructions. If still in doubt follow them.

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Sensible Heat Factor / capacity of Inverter split Systems at part load?

    Quote Originally Posted by Greengrocer View Post
    Problem is that the prices are very high compared to convensional splits. My search goes on I guess.
    That is because they cannot be compared with conventional split units. Check this pdf.

  5. #5
    Join Date
    Mar 2008
    Location
    England
    Age
    68
    Posts
    250
    Rep Power
    17

    Re: Sensible Heat Factor / capacity of Inverter split Systems at part load?

    Quote Originally Posted by nike123 View Post
    That is because they cannot be compared with conventional split units. Check this pdf.
    Couldn't open that link / pdf Nike.
    If in doubt read the instructions. If still in doubt follow them.

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Sensible Heat Factor / capacity of Inverter split Systems at part load?

    Quote Originally Posted by Greengrocer View Post
    Couldn't open that link / pdf Nike.
    Ok. I uploaded it to good server!

    http://www.mediafire.com/?rmehgmmdmdw

  7. #7
    Join Date
    Mar 2008
    Location
    England
    Age
    68
    Posts
    250
    Rep Power
    17

    Re: Sensible Heat Factor / capacity of Inverter split Systems at part load?

    Quote Originally Posted by nike123 View Post
    Ok. I uploaded it to good server!

    http://www.mediafire.com/?rmehgmmdmdw
    Are they are still using R407c? Surely R410a is the way to go. Having said that some specialist UK manufacturers are still using R407c as well.
    Do you kow if they make their own condensing units or do they buy them in from elsewhere?
    If in doubt read the instructions. If still in doubt follow them.

Similar Threads

  1. online heat load calculators
    By pradyumna in forum Tools and Calculators
    Replies: 3
    Last Post: 07-09-2010, 06:42 AM
  2. Calculating heat load
    By Abe in forum Technical Discussions
    Replies: 13
    Last Post: 13-08-2010, 05:40 PM
  3. Calculating heat load
    By Abe in forum Tools and Calculators
    Replies: 58
    Last Post: 25-03-2009, 10:29 AM
  4. part p
    By eggs in forum Electrical
    Replies: 25
    Last Post: 15-11-2007, 08:55 PM
  5. Mortuary heat load
    By smithgmp in forum Commercial
    Replies: 3
    Last Post: 05-05-2003, 04:43 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •