    Ok, I have a 30 kW office air conditioner with a hermetic compressor, air cooled, operating on R22.
    The following readings were taken of the condensing set:-
    Suction – 440 kPa
    Suction temp 20.3°C (at comp suction service valve)
    Discharge Pressure – 1950 kPa
    Discharge Temp - 75°C (at comp discharge service valve)
    Liquid line temp, before tx valve (located in the condensing set) 44.8°C
    Air on condenser - 32.8°C
    Air off condenser - 47.3°C
    Evap air on 24C
    Evap air off 14C
    Firstly, IMO suction and discharge pressures appear relatively 'normal' to me (happy to be told they are not). This is why I went further and got more readings.
    What can be gathered from these readings? I am fairly comfortable saying that the superheat appears too large. This could be TX valve setting or more likely gas charge (based on not fiddling with TX valves first).
    But what about the discharge temp at the compressor and the liquid line temp. What can be gathered from these?
    Your insight would be greatly appreciated.
    Jan 2009
    AUSTRALIA
    Re: R22 OPerating Pressures
    Have you got a liquid line drier??It could be blocked if you`ve got liquid line temp of 44.8 and discharge temp of around 53
    Aug 2007
    Russia
    139
    22
    Quote Originally Posted by james770 View Post
    So the sub cooling is about 9K and it looks good for me.
    To Futsal1st:
    If you know the compressor model a cooling capacity may be estimated with the Coolpack. Check http://www.refrigeration-engineer.co...ad.php?t=16871
    page end.
    Also, do you actually have a problem with the way the unit is performing ?
    Nov 2007
    Australia
    13
    Not really. The plant appears to be slightly short of grunt based on continuing space complaints.
    There is no liquid line drier in the system.
    Are you relating these complaints to your present high ambient conditions or is that not in your area?
    Dec 2004
    Australia
    52
    519
    It's in my area and i am well over it!!
    Quote Originally Posted by Temprite View Post
    I've been reading about it in our press and I must sympathize with you - geeeeez, that's hot
    Jan 2009
    Queensland
    65
    113
    Head seems a bit high. Is the condenser clean?
    with 20C suction return and 1950Kpa head, the discharge leaving at 75C looks strangely low. I'd have expected something closer to 100C.
    you write the air on temp at the condenser was about 32C so it's obviously not a high ambient problem.
    I'd be taking a close look at the condition of the condenser.
    on the other side of the coin, your suction pressure seems a bit low. 2C saturated suction. You say it's a TX system? Does it have a sight glass?
    Dec 2008
    China
    87
    Where did you put the compressor? Indoor or outdoor?
    Dec 2008
    China
    87
    Suct Temperature is too high and it's quite close to the evap air on temp (24), So I guess the compressor is installed outside and the suct temp is not well insulated, which makes the suct temperature incorrect.
    Jan 2009
    Australia
    108
    TD's on indoor unit don't look too bad. 10 deg C is reasonable. Dewpoint for 24 deg 50% RH room is not far below 14 deg so you probably don't want your supply air temp too much lower or you will have condensate issues with your supply air registers.
    How's your air volume?
    If you want to check if the machine is making good power, measure the air-on temp and humidity and the air-off temp and humidity of your evaporator. Get a psychometric chart and read off the values of enthalpy that correspond with these two conditions.(kJ/kg scale)
    Then measure the air volume and apply these figures to the following formula:
    Watts = l/s ( air volume) x (air-on (kj/kg) - air-off(kj/kg)) x 1.184
    Divide the result by 1000 to get kW.
    Compare this with the kW rating on the nameplate of the machine.
    Apr 2001
    79
    5,071
    35
    Quote Originally Posted by Futsal1st View Post
    I'm tempted to say the unit is running reasonably well and pumping a heavy load (cond TD 20C/36F over ambient), but given the above statement perhaps a little fine tuning is in order.
    Check the superheat at the TXV bulb. Perhaps it can be tweaked a little.
    Apr 2001
    79
    5,071
    35
    Quote Originally Posted by wilsoncheung View Post
    The suction is a little high because the blower is running a little too fast, but as long as it doesn't cause humidity problems it is not unreasonable. A little tweak of the TXV might help balance it out.
    And suction line insulation is always a good thing... if the suction line is uninsulated, this could account for a significant portion of the heavy condenser load. Unfortunately we don't have a temp reading at the TXV bulb.
  1. CARE refigerants by BOC
    By dogma in forum Refrigerants
    Last Post: 23-03-2010, 12:39 PM
  2. R134a operating pressures
    By chillymatt in forum Fundamentals
    Last Post: 08-05-2008, 09:31 PM
  3. Hitachi pressures off the scale!
    By ianybeany in forum Air Conditioning
    Last Post: 26-04-2007, 09:42 PM
  4. Replies: 35
    Last Post: 13-12-2006, 11:51 AM
  5. Operating Pressures
    By Abe in forum Air Conditioning
    Last Post: 05-06-2001, 10:20 PM