Results 1 to 12 of 12
-
12-02-2009, 09:57 PM #1
how to remove carrier compressor from 23xl
I have to remove a 250 ton to send out for overhaul. What exactly is involved with doing this?
I want isolate and pump down the refrigerant r-22 and reclaim the compressor only. Does the compressor just lift off or do I need to seperate the motor end? I got carrier IOM manual that really does not help any.
-
12-02-2009, 10:39 PM #2
Re: how to remove carrier compressor from 23xl
Unable to trace a manual for that model number.
What type of compressor is it ?
Can you get lifting gear over the lump ?Brian - Newton Abbot, Devon, UK
Retired March 2015
-
13-02-2009, 05:05 PM #3
Re: how to remove carrier compressor from 23xl
Its a 23xl2120ec
I can rig it out no problem looking more info about disconnecting motor or leaving it attached? Do i need to pull out all refrigerant or pump down?
Do I need to multiple oil changes and filter dryer replacements since its POE oil in a R-22 system? etc etc.
-
13-02-2009, 09:03 PM #4
Re: how to remove carrier compressor from 23xl
Hi hvacdoctor 23xl a semi hermetic centrif and very big it will come out in one piece.
-
14-02-2009, 06:02 PM #5
Re: how to remove carrier compressor from 23xl
always best to reclaim the refrig. reclaim it over a filter/dryer or burn-out filter so its possible to re-use it afterwords.
when you put back the compressor you have to charge the plant by given amounts on the frabricage plate.
Ice
-
14-02-2009, 06:05 PM #6
Re: how to remove carrier compressor from 23xl
[quote=
Do I need to multiple oil changes and filter dryer replacements since its POE oil in a R-22 system? etc etc.[/quote]
always best if you do some repair on compressor's to change the filters and the oil.
Ice
ps;sorry,hit the button to fast
-
15-02-2009, 03:23 AM #7
Re: how to remove carrier compressor from 23xl
It cmes out in one piece. Pull the entire charge and weigh it to see if the systemhas lost any refrigerant. By the time you get the compressor back you may find the valves leaked and your system is flat if you leave it in the vessels. JMHO
-
15-02-2009, 11:31 AM #8
Re: how to remove carrier compressor from 23xl
A centrif on 22 -Are you sure, sure?
http://www.commercial.carrier.com/co..._PRD41,00.html
Get a referb lift and shift to do it for you..
-
15-02-2009, 02:35 PM #9
Re: how to remove carrier compressor from 23xl
Hi multisync i am pretty sure the compressor has a impellar and vanes in it and no screws ,unless they,ve changed it to screws now, i seen the link you posted .
-
15-02-2009, 03:49 PM #10
Re: how to remove carrier compressor from 23xl
The 23XL's came in R22. It is not a centrifugal, its a screw. It either has a Howden or an IR compressor on it.
QUOTE=multisync;135621]A centrif on 22 -Are you sure, sure?
http://www.commercial.carrier.com/co..._PRD41,00.html
Get a referb lift and shift to do it for you..[/QUOTE]
-
15-02-2009, 06:33 PM #11
Re: how to remove carrier compressor from 23xl
my mistake
Last edited by GHAZ; 15-02-2009 at 07:54 PM.
-
15-02-2009, 07:43 PM #12
Re: how to remove carrier compressor from 23xl
Sorry guys i am wrong its 19xl i been mixed up with
Similar Threads
-
MICROPROCESSOR DIAGNOSTICS/Differnces beteween TK/CTC
By REEFER-TEK in forum TransportReplies: 12Last Post: 27-03-2011, 04:12 AM -
Carrier 23xl chiller-Low discharge superheat alarms
By Bradysmill in forum Trouble ShootingReplies: 7Last Post: 25-04-2010, 07:43 PM -
Carrier Chillers
By Ed Burris in forum Technical DiscussionsReplies: 6Last Post: 27-03-2010, 02:00 AM -
Geoff in NY ~ Carrier Parts
By Futsal1st in forum Trouble ShootingReplies: 6Last Post: 30-12-2009, 04:07 AM -
Help identifying carrier HiWall dom. split
By paul_h in forum Air ConditioningReplies: 4Last Post: 12-12-2008, 09:12 AM