    cellar cooler icing up



    Hi all


    recently installed a new cellar cooling unit. ran for a week then had a call saying it was high in temp. upon arrival both evaps where eavily iced up with soft ice on the coil and hard ice on the coil end. defrosted coil and tested system ran up cooling ok. if the cond fan is running can't get head pressure above 170psi (r404a) and 50psi suction pressure. runs for a few days with 6 degrees across the coil then ices up again. got it running on a pressure control for the cond fan to get the head pressure and suction up.. any help would be great thanks in advance



  2. #2
    Join Date
    Jul 2007
    Location
    england
    Age
    44
    Posts
    98
    Rep Power
    17

    Re: cellar cooler icing up

    Quote Originally Posted by tayler46 View Post
    Hi all


    recently installed a new cellar cooling unit. ran for a week then had a call saying it was high in temp. upon arrival both evaps where eavily iced up with soft ice on the coil and hard ice on the coil end. defrosted coil and tested system ran up cooling ok. if the cond fan is running can't get head pressure above 170psi (r404a) and 50psi suction pressure. runs for a few days with 6 degrees across the coil then ices up again. got it running on a pressure control for the cond fan to get the head pressure and suction up.. any help would be great thanks in advance
    is the condenser outside ? whats the ambient temp ? if its outside and the temps low thats whats giving low pressures. Is the model fitted ok to work in these ambients ? u might need a fan speed control. I take it the evaps clear and fans are working .? does it still ice up with the pressure switch fitted ?

  3. #3
    Join Date
    Jan 2008
    Location
    UK
    Age
    49
    Posts
    82
    Rep Power
    17

    Re: cellar cooler icing up

    Just set the LP switch to run a 'wet cycle' as we used to, keep the evap temp above freezing, or you could fit a cheeky timeclock to turn the cond unit off every night say from 4am to 9am while the landlords in bed!!!

  4. #4
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: cellar cooler icing up

    Quote Originally Posted by tayler46 View Post
    Hi all


    recently installed a new cellar cooling unit. ran for a week then had a call saying it was high in temp. upon arrival both evaps where eavily iced up with soft ice on the coil and hard ice on the coil end. defrosted coil and tested system ran up cooling ok. if the cond fan is running can't get head pressure above 170psi (r404a) and 50psi suction pressure. runs for a few days with 6 degrees across the coil then ices up again. got it running on a pressure control for the cond fan to get the head pressure and suction up.. any help would be great thanks in advance

    Stop worrying about the discharge pressure and start thinking about what the suction is doing.

    Cheers taz..
    ..

  5. #5
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: cellar cooler icing up

    yeah i would just do a time initiated defrost, it sounds like the bottom of it is not defrosting and it is working it's way up the coil.

  6. #6
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: cellar cooler icing up

    Quote Originally Posted by tayler46 View Post
    Hi all


    recently installed a new cellar cooling unit. ran for a week then had a call saying it was high in temp. upon arrival both evaps where eavily iced up with soft ice on the coil and hard ice on the coil end. defrosted coil and tested system ran up cooling ok. if the cond fan is running can't get head pressure above 170psi (r404a) and 50psi suction pressure. runs for a few days with 6 degrees across the coil then ices up again. got it running on a pressure control for the cond fan to get the head pressure and suction up.. any help would be great thanks in advance
    Hi Tayler

    sounds like you have either a lack off air flow or are flooding the evaporator, probaly the latter.

    Set your superheat to about 6/7 degrees and this will raise your suction pressure.

    This in turn will raise discharge pressure then if your still having problems we can look at how your condenser fan is controlled and how to check you are fully charged with refrigerant.

    If you need any more info on how to set up private message me an email address and i can forward you stacks of info on commisioning

    Goodluck Chillerman

  7. #7
    Join Date
    Jan 2009
    Location
    Queensland
    Age
    64
    Posts
    113
    Rep Power
    16

    Re: cellar cooler icing up

    tayrer, do you have a defrost time clock on the system?
    Do you have an LP control on the system?
    What temp are you after in the room?
    Did raising the HP make a difference?

    If it's a beer room, I'd set it up for a 1 hour defrost at the end of trade and 3 or 4 30 min defrosts during the day timed for low usage times. A time clock with battery backup is what I'd recommend. without it your big defrost could end up occurring in high usage times.
    In Australia we'd be after a room temp during trade of 0C. I set dirrect pull keg room thermostats to cycle between -2 and +2C. Gives a nice long off cycle.
    Hopes there's something in this you can use.
    Slatts

  8. #8
    Join Date
    Jun 2007
    Location
    Cyprus
    Age
    73
    Posts
    252
    Rep Power
    17

    Re: cellar cooler icing up

    Beer cellar temperature in UK should be 11 degrees. If the equipment is up to the job, and has a thermostat control there ought to be no problem.

  9. #9
    Join Date
    Jan 2009
    Location
    Queensland
    Age
    64
    Posts
    113
    Rep Power
    16

    Re: cellar cooler icing up

    Quote Originally Posted by fridge doctor View Post
    Beer cellar temperature in UK should be 11 degrees. If the equipment is up to the job, and has a thermostat control there ought to be no problem.
    Damn Doc!
    warm beer!
    oh well, each to their own.

  10. #10
    Join Date
    Jun 2007
    Location
    Cyprus
    Age
    73
    Posts
    252
    Rep Power
    17

    Re: cellar cooler icing up

    It isn't the cellar's job to hold the beer at serving temperature, just to pre-cool it before it passes through the so-called 'python' and gets supercooled on it's way to the pump. Or at least that's how it was 5 years ago when I left there.

  11. #11
    Join Date
    Aug 2007
    Location
    ENGLAND
    Posts
    63
    Rep Power
    17

    Re: cellar cooler icing up

    thats right, the cellar cooler should be at around 10 c and the final serving temp is acheived by the brewarys kit normally a python cooler or cellermatic system?

  12. #12
    Join Date
    Dec 2008
    Location
    england
    Age
    77
    Posts
    137
    Rep Power
    16

    Re: cellar cooler icing up

    what system are you using.is it a beermaster

  13. #13
    Join Date
    Jul 2007
    Location
    england
    Age
    44
    Posts
    98
    Rep Power
    17

    Re: cellar cooler icing up

    Quote Originally Posted by paulwild View Post
    thats right, the cellar cooler should be at around 10 c and the final serving temp is acheived by the brewarys kit normally a python cooler or cellermatic system?
    its all gone high tech now . Glycol cooler plates are used for most largers , super chilled and stuff . Glycol is kept at about - 10oC , some largers are served at or around 0oc .This is the general set up for the JD Weatherspoon estate and big pub chains like that , the local on the corner just standard remote beer cooler with python and water , as it was said before most breweries want pub cellars at 12 oC so no need to bother with defrosts on the cellar cooler , most ice problems on evaps are from dirty coils , infact id say about 95% .This is from venting fob bottles in the cellar and the yeast getting sucked up by the fans causing blockages in the coil . We normally turn system off and hose down , if this fails we use hydra coil cleaner ( as a last resort ver expensive !)

  14. #14
    Join Date
    Jan 2007
    Location
    UK
    Age
    53
    Posts
    82
    Rep Power
    18

    Re: cellar cooler icing up

    I don''t do a lot of cellar cooling these days, but the most recent I saw on R404a had a pressure switch to cycle the Cond' fan that maintains around 220-260 head. It was an old peice of cr*p but never had a history of freezing up the evap, despite the evap' coil being filthy.
    "I'm anaspeptic, frasmotic, even compunctuous to have caused you such pericombobulation."

  15. #15
    Join Date
    May 2007
    Location
    scotland
    Posts
    756
    Rep Power
    19

    Re: cellar cooler icing up

    it sounds like the unit might be oversized as the suction seems very low or maybee the orrrifice is to large i would fit a epr and use this to get a better control on your suction presure sort your suction presure out and the head presure will look after its self as long as its sized correctly.

  16. #16
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: cellar cooler icing up

    I think that OP lost interest for that matter, or he solved his problem and don't care to much to respond on all yours solutions. You probably frightened him with all that attention.

  17. #17
    Join Date
    Jan 2009
    Location
    Queensland
    Age
    64
    Posts
    113
    Rep Power
    16

    Re: cellar cooler icing up

    You're probably right Nike, but it keeps us away from the pub

  18. #18
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: cellar cooler icing up

    Quote Originally Posted by Slatts View Post
    You're probably right Nike, but it keeps us away from the pub
    I don't see anything wrong in pub talks!

  19. #19
    Join Date
    Jun 2005
    Location
    Stoke on Trent
    Age
    62
    Posts
    588
    Rep Power
    19

    Re: cellar cooler icing up

    I had a beermaster icing up one evap recently, the problem was a tiny particle of copper swarf stuck to the diaphram of the solenoid valve on the biggest evaporator so it was passing liquid all the time.

  20. #20
    Join Date
    Jun 2008
    Location
    gloucester
    Age
    44
    Posts
    72
    Rep Power
    16

    Re: cellar cooler icing up

    dont think u need a de - frost on a cellar cooler, sounds like your sysyem could be undercharged or a possible restriction in your liquid line. did you purge your lines when u brazed your pipe - work.

Similar Threads

  1. NRS BeerMaster cellar cooler
    By madfriday in forum Commercial
    Replies: 13
    Last Post: 22-06-2009, 09:24 PM
  2. Quiet cellar cooler
    By multisync in forum Trouble Shooting
    Replies: 15
    Last Post: 14-08-2008, 06:13 AM
  3. Hubbard cellar cooler
    By birchy in forum Commercial
    Replies: 7
    Last Post: 06-05-2008, 11:46 PM
  4. cellar cooler fault.
    By fireblade in forum Commercial
    Replies: 12
    Last Post: 11-07-2007, 11:33 AM
  5. Searle cellar cooler control problem
    By iceman007 in forum Electrical
    Replies: 6
    Last Post: 06-07-2004, 08:57 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •