    COMPARISON OF HYDROCARBON R-290 AND

    The environmental impact of refrigerants over the entire life cycle of fluid and equipment, including power consumption, is captured in the life cycle climate performance (LCCP) value. The lower the value, the lower the environmental impact.
    In this report the LCCP of hydrocarbon R-290 (Propane) and the two HFC blends, R-410A and R-404A, were evaluated for an 11 kW medium temperature refrigeration system having -18 °C to 0 °C evaporator saturated refrigerant temperature. Major findings of the current
    study are:

    • The LCCP of R-410A is equal to that of R-290 and the LCCP of R-404A is 6.5% higher than that of R-290 for systems with condensing temperatures of 46.0°C to 47.6°C, which are representative of typical design practice.
    • On an equal first cost basis, the LCCP of R-410A is 4.2% lower and the LCCP of R-404A is 1.8% higher than that of R-290. The underlying assumption is that the first cost
    of the R-290 system may be, for example, 10% higher due to added safety features, and on an equal cost basis, the HFC systems would use the additional cost for a larger
    condenser.
    • Since the underlying baseline test is based on a relatively small condenser, and since a conservative safety cost estimate is used, it is expected that the environmental impact of both R-404A and R-410A would be reduced further as compared to R-290 in future
    system designs.
    Roger

  2. #2
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: COMPARISON OF HYDROCARBON R-290 AND

    Is LCCP same as TEWI?

  3. #3
    rbartlett's Avatar
    rbartlett Guest

    Re: COMPARISON OF HYDROCARBON R-290 AND

    Quote Originally Posted by Peter_1
    Is LCCP same as TEWI?
    wasn't he one of donald ducks nephews- huey, luey and tewi ??

    cheers

    richard

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: COMPARISON OF HYDROCARBON R-290 AND


  5. #5
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: COMPARISON OF HYDROCARBON R-290 AND

    hi peter,

    LCCP stands for: Life Cycle Climate Performance.

    you can read about it at: http://europa.eu.int/comm/environmen...df/vainnio.pdf

    chemi

  6. #6
    shogun7's Avatar
    shogun7 Guest

    Re: COMPARISON OF HYDROCARBON R-290 AND

    Peter,
    As in many things we may see different things in the same material that we read, and you are quite right in the comparison of TEWI and LCCPwith the impact to global warming but I wanted to bring attention to these facts and
    to help provide a clearer understanding of the relative performance potential of the R-290 as compared to two
    HFC’s (R-404A and R-410A) for medium temperature commercial refrigeration.
    The LCCP of R-410A is equal to that of R-290 and the LCCP of R-404A is 6.5% higher than that of R-290 for systems with condensing temperatures of 46.0°C to 47.6°C, which are representative of typical design practice.•

    On an equal first cost basis, the LCCP of R-410A is 4.2% lower and the LCCP of R-404A is 1.8% higher than that of R-290. The underlying assumption is that the first cost
    of the R-290 system may be, for example, 10% higher due to added safety features, and on an equal cost basis, the HFC systems would use the additional cost for a larger
    condenser.
    • Since the underlying baseline test is based on a relatively small condenser, and since a conservative safety cost estimate is used, it is expected that the environmental impact of both R-404A and R-410A would be reduced further as compared to R-290 in future
    system designs.
    Roger
    Last edited by shogun7; 09-04-2004 at 11:34 PM.

  7. #7
    Join Date
    May 2001
    Location
    West Lafayette, Indiana, US
    Posts
    24
    Rep Power
    0

    Re: COMPARISON OF HYDROCARBON R-290 AND

    R-410A and R-290 (propane)

    The R-410A system probably uses POE oil, and the R-290
    system probably uses 300 SUS mineral oil.

    During periodic service, hooking up gauges, etc, small amounts
    of moisture/air gets in. POE oil breaks down from this and a
    host of other reasons and fails the system. The R-290 system
    just keeps runnin'. After 8-10 years, the R-410A system may
    be on it's 5th or 6th compressor and $$$ of service calls.
    Propane system still on original compressor, only maint is to
    oil the fan motor bearings, and clean the condenser twice/year.

    Now go figure your life cycle costs.. why do you think
    industry wants R-410A? The (service) business friendly
    refrigerant... Look at all the $$$, or Euros or whatever
    money R-410 will bring in.. nobody wins with R-290,
    except for the customer.
    --ghg

  8. #8
    Join Date
    Dec 2002
    Location
    sunshine-coast, australia
    Posts
    88
    Rep Power
    22

    Re: COMPARISON OF HYDROCARBON R-290 AND

    greeting 'GHG"
    from jg/oz ---long time ago, still on the same email ????

    hope we have a good conversation on this website, seems a lot better than
    aircondition.com, some BS artists but rest seems ok.

    Started a section MACS, we recently brought a paper to the EarthForum annex MAC Summit half April, if interested sent you the file, extremely
    interesting an essay about 10 years use of HC in Australia and USA with all
    the figures as well as the riskassessment comparissons.

    jg/oz
    jg/oz,
    sunshine coast,
    australia

  9. #9
    Join Date
    May 2001
    Location
    West Lafayette, Indiana, US
    Posts
    24
    Rep Power
    0

    Re: COMPARISON OF HYDROCARBON R-290 AND

    ghg orig email will bounce (spammed out).. Send a short
    email, and the bounce error mesg contains the new email addr.
    Stops the spam..Sure send me the the paper.. thanks.

    In the US, "MACS" disease (life limiting MVAC systems with
    134a/PAG oil/moisture to fail at warranty) seems to have
    spread to HVAC as well now. Life limit with POE oils. Makes
    for Business Friendly systems. in the US, the Big Boyz have
    finally won. I have pretty much gotten out of refrigeration/AC
    now. Experimenting with making low cost colloidal silver for
    mold/mildew control and maybe solar thermal power, where
    I can use HC working fluids again and no Big Boyz to constantly
    fight you every inch of the way.
    --ghg

  10. #10
    Join Date
    Oct 2001
    Location
    Perth, Australia
    Posts
    87
    Rep Power
    23

    Re: COMPARISON OF HYDROCARBON R-290 AND

    Quote Originally Posted by ghg

    In the US, "MACS" disease (life limiting MVAC systems with
    134a/PAG oil/moisture to fail at warranty) seems to have
    spread to HVAC as well now. Life limit with POE oils. Makes
    for Business Friendly systems. in the US, the Big Boyz have
    finally won. I have pretty much gotten out of refrigeration/AC
    now. Experimenting with making low cost colloidal silver for
    mold/mildew control and maybe solar thermal power, where
    I can use HC working fluids again and no Big Boyz to constantly
    fight you every inch of the way.
    --ghg
    I try to follow the adage "Never ascribe to conspiracy that which can be explained by stupidity".

    However, now that the world has been taken over by MBAs and their life sucking economic rationalist associates, the table has been tilted to severely hinder any engineering innovation outside of the rich end of town. As you have found, if you want to innovate, you have to do it on a small scale under their radar.
    Mark Baker

  11. #11
    Join Date
    Nov 2008
    Location
    United Kingdom
    Age
    46
    Posts
    33
    Rep Power
    0

    Re: COMPARISON OF HYDROCARBON R-290 AND

    I can imagine propane use in supermarkets and maintenance staff carefully dealing with equipment + service guys trying to braze leak on kg working run.

    For bigger applications industry uses ammonia or CO, so I don't see any sense either.

    I'm wondering, did somebody tried to promote liquid metals as refrigerants

  12. #12
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: COMPARISON OF HYDROCARBON R-290 AND

    Thread a little bit old, 4 years, so responses might be a bit slow
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

Similar Threads

  1. R134a,R407c,R22 Comparison
    By chahine999 in forum Technical Discussions
    Replies: 9
    Last Post: 18-07-2010, 03:02 PM
  2. do u have any data on comparison of single screw and twin screw?
    By vuputuri in forum Technical Speculations
    Replies: 5
    Last Post: 22-02-2008, 03:52 PM
  3. Hydrocarbon refrigerants
    By mbeychok in forum Refrigerants
    Replies: 15
    Last Post: 01-09-2006, 10:03 PM
  4. Compressor comparison
    By davidk in forum Fundamentals
    Replies: 1
    Last Post: 20-07-2006, 11:32 AM
  5. Evaporator Fan Comparison
    By pcle in forum Technical Discussions
    Replies: 2
    Last Post: 18-11-2003, 10:21 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •