    control v/v and coil mismatch



    To make a long story short here's the problem.
    I have 4 /27 ton coils made by AREO COIL model #MH2-2408-120-3AXG-5 mated with Danfoss ICAD 600 Danfoss motorized control valves. The problem is that the tube diameter is to large 1" on these coils this is an DX system. The valve modulates liquid feed via a sensor which reads super heat in the suction line but because of the amount of liquid comming out of the coil ( BRINING) into the suction line these valves for the better word are confused because there just is no super heat to read so they are all over the place.So we just took them off line and are now using the by-pass vaves for our feed at a 1/4 turn open each what I get in the end is a 2 degree T.D. and my transfer tank dumps on average 60 to 100 times daily which is better than what I get with the control vavles. Now without having to change the control valves or the evaps or go to a pumped liquid system does anyone have a sugestion on what to try. I can go into more detail on the whole dilema if need be but I thought I would just throw this out there and see what kind of response I get with the info given. Thanx for the ear.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: control v/v and coil mismatch

    What is the system serving, refrigerant type and evaporating temperatures please?

    We assume that the control parameters were all set correctly.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Nov 2008
    Location
    canada
    Posts
    64
    Rep Power
    16

    Re: control v/v and coil mismatch

    The system is serving a low temp cold storage room which is 1,125,164 cu ft in size. the medium is ammonia and we like to see temps at -5f. We get this temp but to get any lower we have to wind up the engine room balls to the wall. We have had all sorts of suggestions of what to do from putting in a pulse v/v which opens and closes at set times for the liquid feed to modifying the distributor at the coil.It was also guggested to make the suction riser smaller in diameter to create more valocity. We moved the sensor around with no luck so now we want to do something else but I don't want to this to go any farther south on us than it has already. I can afford to loose one coil this time of year but in the warmer months thats not an option.

Similar Threads

  1. Why a capacitor on contactor coil
    By wambat in forum Electrical
    Replies: 18
    Last Post: 15-05-2009, 03:18 AM
  2. LG heat pump problem
    By back2space in forum Heat Pumps
    Replies: 132
    Last Post: 01-02-2009, 11:23 PM
  3. Dont be shy, advice needed.
    By Sledge in forum Air Conditioning
    Replies: 9
    Last Post: 27-06-2007, 03:09 PM
  4. Burst Coil
    By frank in forum Air Conditioning
    Replies: 13
    Last Post: 20-02-2005, 06:28 PM
  5. Article in ACH&R News
    By Gary in forum Fundamentals
    Replies: 8
    Last Post: 20-05-2003, 12:27 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •