Results 1 to 12 of 12
    Jun 2008
    India
    56
    64
    Power Factor calculation
    Anyone to help me with my question on power factor?
    I am using a 3 phase scroll compressor having 8 amp in each of R,Y,B legs consuming total 5,000 watts power input and a condenser fan motor, which is single phase and draws 4 Amps in R leg and total input power of 700 Watts.
    What is the Power factor for this condensing unit? What voltage and ampere do I consider for the P.F calculation in the formula, PF = (W)/(1.732 * V * I)? I need to select a P.F correction capacitor & hence need to know where I am now.
    Feb 2008
    Norway
    57
    446
    Re: Power Factor calculation
    How do you know the compressor is consuming 5,000W?
    V*I*1.73 gives you the kVA which is NOT the same as the power in kW.
    To get the true power you need an advanced clamp-on amperemeter measuring the amps in all three legs and the voltage across all three legs simultaneously. The instrument then calculates the true power based on the voltage, amps and the phase angle.
    This is always a lower value than the kVA value.
    Say the true power is 4.000W and the kVA is 5.000kVA.
    This gives a power factor of 4.000/5.000=0.8
    The instrument also calculates the kVAr directly or you can calculate it from the kW or kVA and the power factor. Based on the kVAr, HZ and the voltage you can calculate the capacitors.
    Aug 2008
    London
    42
    55
    Steinar,
    KR did give the correct formula for PF not KVA, if you read his comments correctly, my interpretation:
    Input Watts
    Vl x Il x 1.732
    Vl = Line volts
    Il = Line Amps
    KR Im assuming you have taken the rated KW of the compressor motor, therefore if you use the formula you did already and take 8 amps for the Il and 400 for the Vl ~3
    then PF = 5000 / 400 x 8 x 1.732
    = 0.90
    HOPE THIS HELPS? In terms of the actual line voltage to use i would measure just to make sure across two phases with a multimeter to get the three phase voltage output.On three phase system with no problems electrically/install the PF wont change greatly from the 400 taken as a approx.
    Jun 2008
    India
    56
    64
    Steinar,
    The total power of my condenisng unit = 5000 + 700 = 5,700 Watts
    Taking voltage value (or measurement) is also not a problem. What single ampere value do I use in the formula, because the ampere in the 3 legs are:
    R : 8 amp + 4 amp for fan = 12 amp
    Y & B : 8 amp each. Should I take average of 12, 8 and 8 in the 3 legs?
    Feb 2008
    Norway
    57
    446
    I'm not an expert in the area, but I think you must use the amp value for the compressor alone, calculate the three capasitors, then take the amp value for the fan, calculate the capasitor for the fan which is to be conected between one phase and neutral. You will then have four capasitors in total.
    Feb 2009
    36
    It depens on what the site Power factor is to start with. Most large plants or factorys have large power factor correction units, (basically a box with a speical controller that samples the P.F. and switches in more capacitors as the p.f. drops.
    If your P.f. is bad to start with say below 0.8. There will be little effect by adding capacitors, as your then trying to boost the site power factor up. You will only boost the site P.f. if you have a large bank of caps.
    If your site is being billed on reactive power (like all large power usage sites), the lower the p.f. the more money you will be charged per unit of energy.
    Power factor correction units i have installed i have seen pay back in 2 to 3 years on a site load of 1Mw with a cruddy p.f. of 0.6
    If your site has massive inductive loads, you would have to look at installing power factor correction unit.
    I used to install ABB P.f. units
    hope that helps ya
    Apr 2006
    55
    1,908
    30
    Quote Originally Posted by THE WOMBAT View Post
    Hi WOMBAT
    From your above posting
    Would I be right in thinking that if you install a chiller with power factor correction built in this would have no advantage in the way of reducing cost of power bills unless the site also runs power factor correction
    Jan 2008
    India
    70
    171
    12, 8,& 8 amps in Y,B &R seems to be Unbalanced. First it needs to be set right. Otherwise it is better to take average of the 3 values and work out.
    Feb 2009
    36
    Chillerman
    the units power factor is corrected for that machine attached, it wont do much to boost it around the chiller.
    small commercal installs dont always have reative power meters, so there not billed higher for having large inductive machines running.
    if your power has bad p.f. to start with, your chiller would still run slightly better with caps in it.
    Your site p.f would still be low ..
    a 5kw machine isnt going to drag the p.f. down unless ur living on an extension cord
    Nov 2008
    india, delhi
    14
    thannx great tips
    regards
    gulshan kumar
    Apr 2006
    55
    1,908
    30
    Chillerman
    WOMBAT
    Modern chillers i have worked on have power factor correction built into the panel and i was trying to make out if this is beneficial to the customer or do they have to have the whole site pf corrected to lower their power supply bill
    cheers chillerman
    Feb 2009
    36
    its always best to maintain a heathly site p.f., if the chiller dosn't have p.f. caps in it this will drag it down lower across the site. discharge lighting anything with a choke to restrict current flow. super markets have lots and lots of discharg lighting and compressors.
    Most chillers now have caps installed so that it doesn't affect the site'pf. as it stands befre the load of the chiller is added to the power network ,.
    i hope that helps a little, too may beers since collage @)
  1. compressor ratings in horse power
    By themba in forum Fundamentals
    Last Post: 30-03-2008, 12:07 AM
  2. No Power for Defrost Timer Motor
    By kln in forum Domestic
    Last Post: 21-01-2008, 08:22 AM
  3. SR2 50 models electric SBY diagonostics made simple
    By absolute-zero in forum Transport
    Last Post: 04-01-2008, 05:11 PM
  4. Daikin KRP2A61 Card Power consumption
    By EddieC in forum Air Conditioning
    Last Post: 19-08-2006, 04:08 PM
  5. NEW 3-Phase IGBT Inverter Power IC
    By theberes in forum New Technologies
    Last Post: 01-03-2004, 01:10 AM