26-04-2010, 08:09 AM #1
AHU not responding correctly to the TAC BMS panel.
I've 3 Carrier AHU's who are not responding correctly to the TAC BMS control system.
if the unit is turned off by time programming with the TAC panel it gets off but the status still shows running and the actuator does not shutoff.
i've checked and cleaned the sensors but it did not work, please advise how to rectify.
-
26-04-2010, 07:43 PM #2
Re: AHU not responding correctly to the TAC BMS panel.
Is the TAC system working correctly?
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
26-04-2010, 07:52 PM #3
Re: AHU not responding correctly to the TAC BMS panel.
What does TAC stand for? Tour Andover Controls? If it is then the status you refer to is likely called a numeric point and would be on or off based on a program and although the unit is not running the "virtual Point" thinks it is running and that virtual point is likely controlling your actuator.
-
26-04-2010, 09:02 PM #4
Re: AHU not responding correctly to the TAC BMS panel.
hi check communication cable to the tac controller from panel.
make sure u didnt exceed the recomended distance.
What xenta model controller are u using?THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!
-
27-04-2010, 03:36 AM #5
Re: AHU not responding correctly to the TAC BMS panel.
Check your air press switch on ahu, this is where the status (run) should come from.
-
27-04-2010, 08:18 AM #6
Re: AHU not responding correctly to the TAC BMS panel.
Yes, i've 13 AHU's and all response properly except 3.
-
27-04-2010, 08:21 AM #7
Re: AHU not responding correctly to the TAC BMS panel.
I've checked and cleaned the air flow sensor.
I use TAC Xenta OP.
-
27-04-2010, 09:41 AM #8
Re: AHU not responding correctly to the TAC BMS panel.
Could be a software problem-maybe the input wasnt programed properly?
THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!
-
28-04-2010, 02:16 PM #9
Re: AHU not responding correctly to the TAC BMS panel.
Whats the front end telling you about the FCU's status?
-
28-04-2010, 07:12 PM #10
Re: AHU not responding correctly to the TAC BMS panel.
hi aqeelhassan
whats up??did u find the bug??THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!
-
29-04-2010, 12:26 AM #11
Re: AHU not responding correctly to the TAC BMS panel.
This point (run status) could be in the manual forced on from a software override. But from experience there is usually another fault or two. Do you have acess to manually override points on the front end or laptop? You can trace the cable from the air press switch with a bell or fset to the controller board input or mech pannel to determine if it is a software or hardware fault. I found on a big site with TAC and York AHU's that innitial commissioning was not completed - causing the CHWV to stay open when fan is not running inturn causing chiller short cycling and a very mouldy coil.
-
06-05-2010, 01:15 PM #12
Re: AHU not responding correctly to the TAC BMS panel.
no goshen, not yet...any idea?
Similar Threads
-
LG GR642QVP Panel problem
By claguey in forum Trouble ShootingReplies: 3Last Post: 08-09-2010, 12:03 PM -
Quantum LX Control Panel
By Trevor1 in forum Trouble ShootingReplies: 2Last Post: 08-05-2010, 01:46 PM -
Bosch Fridge Freezer Control Panel Problem
By Bork in forum DomesticReplies: 1Last Post: 25-08-2009, 01:02 AM -
Wrong temperature on control panel
By swee'pea in forum Trouble ShootingReplies: 2Last Post: 14-01-2009, 09:18 AM -
Frick Quantum Panel
By LEE40 in forum Trouble ShootingReplies: 4Last Post: 27-03-2008, 05:24 PM