    mits elect split fault



    I've got a fault I haven't seen before on a mits MSH-09NV. It's a small conventional split that has an outdoor control and de-ice PCB.
    The indoor runs as normal until the compressor is supposed to start. It briefly sends 240V to the outdoor unit, then cuts it after 2 seconds, then the indoor turns the fan off.
    I went out to the outdoor unit and checked compressor, capacitor etc, and retested the system.
    240v goes to the outdoor, but the comp relay just chatters on and off ~ 6 times, with no attempt by anything to run (fan, comp etc) Same result if I remove the relay output to the compressor, so no power going to comp, no load on the circuit, just 240v to the outdoor pcb makes the relays chatter and the indoor shut down.

    Anyone have any ideas with mits electric?



  2. #2
    Join Date
    Feb 2007
    Location
    France now, Suffolk before
    Age
    55
    Posts
    294
    Rep Power
    18

    Re: mits elect split fault

    Paul, I found this.
    Hope it can help.

    http://es.mehvac.com/UploadedFiles/R...0059123856.PDF

  3. #3
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: mits elect split fault

    Faulty solder joint on PCB at compressor relay??

  4. #4
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: mits elect split fault

    I removed the board and checked solder joins, all seems OK.
    Thats the main reason why I removed the compressor as a load on the relay, also can't figure out why that would stop the indoor working (as I said, supply to o/u is cut and indoor fan stops).
    While the outdoor relay is chattering away, normal non fluctuating mains is being supplied to the unit from the indoor.

    edit: thanks for the link expat.

    I guess my thoughts on the matter at the moment are: Is this supposed to be energize the outdoor unit longer if the comp relay is out there and there's a comms line? if so indoor board is playing up.
    Or is this supposed to only power up the outdoor when the compressor needs to run? If so the indoor is shutting down due to maybe bad comms from the o/u when it sends power to the outdoor, and the outdoor board is playing up and is the culprit.

    I had a look at the troubleshooting guide in the linked manual, nothing seems to cover my senario, and the outdoor unit isn't powered up long enough to do any voltage tests on the outdoor PCB, the indoor cuts power too quickly.
    Last edited by paul_h; 27-01-2009 at 03:23 PM.

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: mits elect split fault

    Did you checked indoor PCB relay (52C) DC voltage for same "chattering" when relay chatters?
    Use analog voltmeter!

  6. #6
    Join Date
    Sep 2006
    Location
    italy
    Age
    53
    Posts
    93
    Rep Power
    18

    Re: mits elect split fault

    Could be a problem related with the driver circuit of 52C. But in this case you have to replace entire deicer PCB.

  7. #7
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: mits elect split fault

    Do you have a good neutral ?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  8. #8
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: mits elect split fault

    Low voltage comms cable from indoor unit to outdoor unit going through outdoor isolator ?
    contacts on isolator = high resistance ?

    suggest make comms cable direct straight through.

    have not looked at M series for a loooong time
    but
    this one often resolves problems as any resistance on the low voltage comms line makes a problem.

Similar Threads

  1. mitsubishi heavy split fault
    By grovecoooling in forum Air Conditioning
    Replies: 7
    Last Post: 13-03-2011, 12:29 PM
  2. Split unit sensor explanation fault diagnosis?
    By karl957 in forum Air Conditioning
    Replies: 8
    Last Post: 04-01-2009, 05:28 AM
  3. split a/c fault code
    By ksvinod in forum Air Conditioning
    Replies: 1
    Last Post: 04-07-2007, 02:12 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •