Thread: Mitsi elec vrv
    Dec 2008
    36
    Mitsi elec vrv
    One of my jobs this week is to investigate a vrv system that has lost all heating/cooling affect. All pipework runs from small vrv system to multi box and then all pipe is branched off into the evaporators.
    Iv been told the comp is running, and the guy who had checked it before measured 12.3 12.3 and 13.7 or something along those lines on comp.
    Can anyone give me some hints to look for when i go there?
    Mar 2007
    Warwickshire UK
    723
    21
    Re: Mitsi elec vrv
    For SOG first check the suction & discharge pressure & temp.
    If it runs low suction pressure then the discharge SH gets very high & when the discharge temp get to max allowable then the compressor slows down to protect itself.
    This makes poor performance.
    Dec 2008
    36
    Re: Mitsi elec vrv
    Suction is at 50 psi which is far too low as i think it is 410a
    Feb 2008
    manchester
    80
    Re: Mitsi elec vrv
    yeah it does seem sog i had a toshiba on 410 and in heating on suction (3 pipe) at about 150 psi, if you find a leak a vac it then ring mist and they will give you cal's so u can weigh it back in
  1. moving 4 mitsi Elec G50 controllers
    By Enviro-Cooler in forum Air Conditioning
    Last Post: 20-01-2009, 08:07 PM
  2. Manual needed for Mitsi Elec PUHZRP250YHA2
    By marc5180 in forum Air Conditioning
    Last Post: 08-01-2009, 07:49 PM
  3. Mitsi Electric RP6AA Pump Fault
    By gwilliamson in forum Air Conditioning
    Last Post: 15-08-2008, 05:59 PM
  4. Mitsi Elec model numbers
    By airefresco in forum Air Conditioning
    Last Post: 07-09-2006, 09:05 AM