    split driers



    hi all,
    i have a small wall hung split system that has lost its charge due to not being screwed down, where do i stick the drier? i have seen them in the liquid line after the service valves, is this the right spot and can anyone recommend a drier to do the job, for both r22 and 410.
    also, do splits have a drier built in that should be removed?
    thanks



  2. #2
    Join Date
    Feb 2008
    Location
    QLD
    Age
    53
    Posts
    74
    Rep Power
    17

    Re: split driers

    Most don't have driers, what brand is it?

    You can fit a bi flow if it is reverse cycle, in the liquid line (cooling)
    I normally recommend a 3/8'' with 1/4 " flare nuts , if it is a smaller split.

  3. #3
    Join Date
    Sep 2006
    Location
    italy
    Age
    53
    Posts
    93
    Rep Power
    18

    Re: split driers

    If you already loose the refrigerant, you can also dry the system using the vacumming procedure (of course after repairing the leaks) followed by braking of vacum with nitrogen.

    regards

  4. #4
    Join Date
    Jun 2008
    Location
    Australia
    Posts
    22
    Rep Power
    0

    Re: split driers

    its a 1hp kelvinator. in the liquid line means after the service valves, not inside the box straight after the condensor? does it matter that the filter is after the expansion device (cooling)?
    cheers

  5. #5
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: split driers

    You can fit them after the liquid valve and expansion without hassle, done it heaps of times when a compressor burns out. IE just stick a flare biflow on the liquid line externally. It doesn't affect the performance a lot, and most of the time is the only option as there's not a lot of space inside the unit. This is what the actual manufacturers wanted us to do too.

    Split's normally just have a copper spun strainer to prevent capillary/txv blockage, they don't have a proper drier.

    Also it's 1HP kelvinator split, wouldn't it almost be cheaper to buy a new one than strip down, weld in a biflow drier inside the unit before the expansion device, evac and recharge?
    Last edited by paul_h; 24-01-2009 at 08:32 AM.

Similar Threads

  1. Pressure testing for leaks on split a/c systems
    By mrchatts in forum Air Conditioning
    Replies: 46
    Last Post: 08-04-2010, 10:02 AM
  2. Australian split installers, some info needed
    By paul_h in forum Air Conditioning
    Replies: 10
    Last Post: 20-05-2008, 03:40 PM
  3. Do you beleive in data of split units?
    By jirhol in forum Fundamentals
    Replies: 4
    Last Post: 29-03-2008, 11:17 PM
  4. High overcurrent on 3.5kW heatpump split
    By Makeit go Right in forum Air Conditioning
    Replies: 12
    Last Post: 08-03-2007, 12:27 AM
  5. Replies: 8
    Last Post: 20-05-2006, 04:21 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •