Results 1 to 8 of 8
  1. #1
    Join Date
    May 2006
    Location
    Norwich
    Age
    53
    Posts
    134
    Rep Power
    18

    Worcester Bosch Air to Air Heat Pumps



    Has anyone any experience with them.

    We installed one a few weeks back for a customer.

    We were suprised to get 80 degrees Off the inside coil ( Air Temp )

    These unit are aimed at heating houses, with the intention being Heating as the no1 selling point.

    Cooling is a added extra in the Summer.

    Back door into the Domestic Market ?
    Who knows



  2. #2
    Join Date
    Sep 2006
    Location
    italy
    Age
    53
    Posts
    93
    Rep Power
    18

    Re: Worcester Bosch Air to Air Heat Pumps

    Hi,

    What type of refrigerant are using? Sorry but 80 degree air temperature (supply air temp) is too much.

    Can you give more characteristics?

    Regards

  3. #3
    Join Date
    Jul 2007
    Location
    York
    Posts
    9
    Rep Power
    0

    Re: Worcester Bosch Air to Air Heat Pumps

    80 degree c air off?? This would melt the plastic.

  4. #4
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: Worcester Bosch Air to Air Heat Pumps

    If thats 80 deg C off coil air temp then we could expect discharge pressure of arround 50 bar or arround 700 psi on R410a.

    Tip

    Do not connect your manifold gauges to the system in heating mode.

  5. #5
    Join Date
    May 2006
    Location
    Norwich
    Age
    53
    Posts
    134
    Rep Power
    18

    Re: Worcester Bosch Air to Air Heat Pumps

    well thats what i cant work out, im just going by what the engineer tod me. They are 410A

    COuld they have been designed as Firstly a Air to air Heat pump and then a Cooling unit 2nd ?

    THese units are marketing the domestic market, and are aimed at heating a Bungalow ! ( and they do ! )

    Like i say, we dont supply them we just send a engineer to conect the refrigeration side, pressure test and vac, and commission.

    I just wondered if anyone else on here has installed any ?

  6. #6
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: Worcester Bosch Air to Air Heat Pumps

    .



    Looking at W-B's web site they offer a bog-standard tin-and-wind split, probably made in the Far East and badged for W-B because they are not primarily A/C manufacturers.

    80 degrees C is unrealistic for a small split like that. High discharge temperatures would probably shut it down and throw a fault.

    So it could either Fahrenheit he's measuring or his thermometer's a dud.

    (...........I'm ruling out non--condensibles in the system..... or should I.....? .......... Nah, it would have clapped out by now..... )




    .

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Worcester Bosch Air to Air Heat Pumps

    Check your thermometer again! If you measure again that temperature, make sure that everyone in house is evacuated and call bomb squad. That is at least 60 Bar of pressure inside AC.

  8. #8
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Worcester Bosch Air to Air Heat Pumps

    As said above, is it in Fahrenheit or is there an electric heater in there as well ?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

Similar Threads

  1. Capacity control
    By sparrow in forum Training
    Replies: 44
    Last Post: 18-01-2010, 07:49 PM
  2. Replies: 5
    Last Post: 14-09-2009, 07:33 AM
  3. Heat transfer coefficient - Coolpack
    By Graham in forum Fundamentals
    Replies: 10
    Last Post: 28-05-2008, 01:08 AM
  4. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  5. High Altitude Heat Pumps
    By Grog in forum Air Conditioning
    Replies: 2
    Last Post: 23-03-2007, 09:30 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •