19-01-2009, 09:14 PM #1
Fridge and Freezer technical differences
Although there are many posts on the Net about using (ie converting) a freezer as a fridge I have seen a few posts both here and on the Net in general with the general advice that a freezer should be used as such and not as a fridge.
However I cannot find any technical explanation as to why this might not be a good idea, only that it might shorten the life of the compressor.
Apart from the obvious fact that a freezer cools to much lower temparatures, can anybody explain what other differences there might be that could shorten the compressor life if a freezer were converted to cool at around 4C instead of the usual -17c ?
19-01-2009, 11:20 PM #2
Re: Fridge and Freezer technical differences
Apart from cooling the freezer the refrigerant also cools the compressor.
If you are then going to run the compressor at up to 21°C (-17° + +4°) then the compressor is liable to be overheated. This will damage the oil and motor windings as well as reduce efficiency.Brian - Newton Abbot, Devon, UK
20-01-2009, 06:18 PM #3
differance are mainly pressure differance and compressor displacment.
In a freezer you have a lower sst and thus low gas density and thus you can use a larger displacment compressor with a lower motor Hp as the suction gas is rarified.
Where as a fridge has denser suction gas thus a smaller displacment with a larger hp motor and the pressure differance is less due tot he lower pressure gradient.
you can convert a fridge to a freezer with little worry how ever you take a big (Well ok a huge) capacity hit due tot he small starting displacment and then adding rarified suction gas, your re-expansion inside the compression chamber is big! As the high Hp and small displacment work well in this order albeit no where near ideal!
But converting a freezer to a fridge you suffer more as now the much denser suction gas in conjunction to the large displacment and low Hp you over heat in fast order as the motor strugles to compres the denser gas!Last edited by The MG Pony; 20-01-2009 at 06:22 PM.
Hotpoint FF200E Fridge Freezer Fault
By fredalfred in forum DomesticReplies: 107Last Post: 29-12-2012, 01:26 PM -
BOSCH Fridge/Freezer - fridge wont cool....freezer fine
By andy_lanc in forum DomesticReplies: 6Last Post: 25-10-2010, 01:25 PM -
Hotpoint FFA71 Freezer High Temp Light / Fridge is Freezing
By sumnerpa in forum Trouble ShootingReplies: 1Last Post: 19-08-2008, 03:16 PM -
Differences between fridge and freezer?
By Petel in forum Technical DiscussionsReplies: 3Last Post: 22-03-2008, 02:24 AM -
Help! fridge freezer probs
By Glenreed in forum Trouble ShootingReplies: 2Last Post: 06-01-2006, 10:51 PM