    Cold rooms



    Hello,
    What are the low pressures to reach when charging cold room systems with vapour ( positive and negative temperatures) with:
    *R12
    *R502



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Cold rooms

    Quote Originally Posted by fathihvac View Post
    Hello,
    What are the low pressures to reach when charging cold room systems with vapour ( positive and negative temperatures) with:
    *R12
    *R502
    Pressures will depend on temperatures of room among other things. That is not way to charge system.
    System with TXV is charged by target subcooling value.

  3. #3
    Join Date
    Jan 2009
    Location
    Australia
    Age
    60
    Posts
    108
    Rep Power
    16

    Re: Cold rooms

    With the system running, charge the system to a full sightglass with what ever refrigerant the system is designed for. Make sure there is a receiver and a subcooler fitted when using this method. If either are missing, you can't do this without the risk of overcharging the system.

    If the room is hot and the sight glass is full, the system is going as hard as it can go. As the room cools, less liquid is required and the excess will back up in the receiver.

    A full head of liquid arriving at the tx valve is required to maintain stable tx valve operation. Any flash gas at the valve will generally cause it to become unstable and hunt which is why the sightglass must be full.

    Hope this helps.

Similar Threads

  1. Sizing Cold rooms
    By CJG21 in forum Fundamentals
    Replies: 6
    Last Post: 28-10-2010, 10:22 AM
  2. low humidity cold rooms
    By nambiandy in forum Technical Discussions
    Replies: 17
    Last Post: 01-05-2010, 08:00 AM
  3. Porkka cold rooms
    By Andy AC in forum Commercial
    Replies: 6
    Last Post: 29-08-2007, 08:14 AM
  4. Frost Formation in Cold Rooms
    By Samarjit Sen in forum Technical Speculations
    Replies: 21
    Last Post: 04-08-2007, 05:19 PM
  5. High RH Cold rooms
    By tadipatrir in forum Fundamentals
    Replies: 37
    Last Post: 22-06-2007, 06:39 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •