    extreme winter operation



    we have been having a prolonged cold snap in our area of late( minus 44 f yesterday morning) I was wondering if anyone had any tips on system operation during the winter season. My two stage system has been operating with a average discharge pressure of 80 psig for the last few days with no adverse effects on cooler temperatures or loading dock heating.



  2. #2
    Join Date
    Dec 2008
    Location
    USA
    Posts
    17
    Rep Power
    0

    Re: extreme winter operation

    You may want to talk with your refrig consultant, engineer, or contractor first, but has a client in northern Idaho with 2-stage screw installation that found it possible to operate his plant system single stage during January and February, and save wear ane tear on the booster plus save some power dollars...

  3. #3
    Join Date
    Mar 2008
    Location
    Dallas, Oregon
    Age
    72
    Posts
    51
    Rep Power
    17

    Re: extreme winter operation

    I'd guess that your energy savings are substantial running such a low head pressure.

    Are you using NH3 to cool your compressor oil (thermosyphon / oil cooilers)? If so, are you noticing low oil temps in your compressors?

  4. #4
    Join Date
    Jan 2006
    Location
    Valrico, Florida
    Posts
    517
    Rep Power
    19

    Re: extreme winter operation

    Are you hot gas defrost? That low of a head could cause problems with defrosts.

  5. #5
    Join Date
    Sep 2008
    Location
    United States
    Age
    59
    Posts
    57
    Rep Power
    16

    Re: extreme winter operation

    we use liquid injection oil cooling on our frick RWB-40's and closed loop glycol on our Vilter 450's. We use hot gas for defrost,dock heat and under floor heat in the freezers. low discharge pressure has been a issue when ambients get to -25 f and lower. the system is pumped liquid except the liquid supply for the liquid injection oil cooling.

  6. #6
    Join Date
    Jul 2008
    Location
    wet coast B. C.
    Age
    76
    Posts
    123
    Rep Power
    16

    Re: extreme winter operation

    chilldis I have run one of my engine rooms for short time periods at 90 psi head pressure. I was told dont do it why I asked ? I got reasons from everwere 1. NH3 would condense in the oil separators 2. defrost problems etc etc I had a professional engineer tell me last year not to go below 100 psi Why who knows. It sounds like you are not having problems . So keep on saving energy. C.D.

  7. #7
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: extreme winter operation

    Quote Originally Posted by chilldis View Post
    we have been having a prolonged cold snap in our area of late( minus 44 f yesterday morning) I was wondering if anyone had any tips on system operation during the winter season. My two stage system has been operating with a average discharge pressure of 80 psig for the last few days with no adverse effects on cooler temperatures or loading dock heating.
    As far as I understand your condenser pumps and fans are off. Condensers are cooled by natural air convection. 80psig is the average head pressure. What is the range of head pressure fluctuation?

  8. #8
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: extreme winter operation

    Quote Originally Posted by chilldis View Post
    we use liquid injection oil cooling on our frick RWB-40's and closed loop glycol on our Vilter 450's. We use hot gas for defrost,dock heat and under floor heat in the freezers. low discharge pressure has been a issue when ambients get to -25 f and lower. the system is pumped liquid except the liquid supply for the liquid injection oil cooling.
    Do you run your screws at 80psig head pressure? Very often screw with liquid injection oil cooling have a problem at head pressure lower than 100psig. It isn't easy to defrost coils at 80psig. Do your coils have back pressure regulators or liquid drainers for defrosting?

  9. #9
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: extreme winter operation

    Quote Originally Posted by CHIEF DELPAC
    ... I have run one of my engine rooms for short time periods at 90 psi head pressure. I was told dont do it why I asked ? I got reasons from everwere 1. NH3 would condense in the oil separators 2. defrost problems etc etc I had a professional engineer tell me last year not to go below 100 psi
    There is no reason why a refrigeration system will not work at these pressures, but there could be some limitations which prevent you from doing this in your specific system.

    It has to do with how the system was designed. Some systems do not react very well when the discharge pressure falls below 125 psig, while others may operate OK at 90 psig.

    Oil cooling methods like liquid injection could also be one of those topics that prevent low discharge pressure.

    The end result is; you need just enough pressure differential to make the valves (liquid injection, defrost regulators, etc.) work. The problem is valve capacity. In most cases, the outlet pressure of the valve is determined by what the valve is trying to accomplish. However, the valve capacity required to meet that purpose is determined by pressure differential across the valve port.

    What the professional engineer should have told you was how to get your discharge pressure lower than 100 psig!
    If all else fails, ask for help.


  10. #10
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: extreme winter operation

    Quote Originally Posted by CHIEF DELPAC View Post
    chilldis I have run one of my engine rooms for short time periods at 90 psi head pressure. I was told dont do it why I asked ? I got reasons from everwere 1. NH3 would condense in the oil separators 2. defrost problems etc etc I had a professional engineer tell me last year not to go below 100 psi Why who knows. It sounds like you are not having problems . So keep on saving energy. C.D.
    I found many professional engineers have limited knowledge about operation at low head pressure. Usually, they design plants for the hottest ambient conditions, but operation at low head pressure is the different story. You mentioned couple reasons.
    1. NH3 will never condense in oil separator, because it is superheated.
    2. Majority of evaporator coils can be defrosted at head pressure lower than 100psig. They should be adjusted properly.
    Ask your professional engineers about the reasons of operating at head pressure higher that 100psig. We will discuss them at this forum.

  11. #11
    Join Date
    Jan 2006
    Location
    Valrico, Florida
    Posts
    517
    Rep Power
    19

    Re: extreme winter operation

    I am having problems agreeing with the statement that nh3 will never condense in an oil separator because it is superheated.

  12. #12
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: extreme winter operation

    Quote Originally Posted by nh3wizard View Post
    I am having problems agreeing with the statement that nh3 will never condense in an oil separator because it is superheated.
    I mentioned about operating compressor and oil separator. If you have different opinion, let's discuss it.

  13. #13
    Join Date
    Jan 2006
    Location
    Valrico, Florida
    Posts
    517
    Rep Power
    19

    Re: extreme winter operation

    I have seen nh3 condense in an oil separator, the machine had cycled off for a period of time and the oil heaters were not functioning.

  14. #14
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: extreme winter operation

    Quote Originally Posted by nh3wizard View Post
    I have seen nh3 condense in an oil separator, the machine had cycled off for a period of time and the oil heaters were not functioning.
    It would better if we talk about properly functioned equipment. However, in you case I think that nh3 won't condense in oil separator. Nh3 will condense in discharge line when compressor is idle for a while. This condensate will drain to oil separator through leaking check valve. At lower condensing pressure less likely nh3 will condense in discharge line. At 90psig head pressure nh3 won't condense if temperature in compressor room higher than 60degF. It means that at lower head pressure less condensation in discharge line.

  15. #15
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: extreme winter operation

    Refrigerant condensation in the oil separator would only occur when the oil temperature is less than the saturation temperature of the refrigerant (at whatever pressure being considered).

    This could happen even with an operating sump heater. If the sump heater does not produce sufficient heat to keep the separator warm in a cool engine room the oil can cool down.

    Oil separators have a lot of surface area and can reject a fair amount of heat.

    However, if the engine room is warm the usual sources of liquid are from: liquid slugging or condensation in the discharge line.
    If all else fails, ask for help.


  16. #16
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: extreme winter operation

    Quote Originally Posted by US Iceman View Post
    Refrigerant condensation in the oil separator would only occur when the oil temperature is less than the saturation temperature of the refrigerant (at whatever pressure being considered).

    This could happen even with an operating sump heater. If the sump heater does not produce sufficient heat to keep the separator warm in a cool engine room the oil can cool down.

    Oil separators have a lot of surface area and can reject a fair amount of heat.

    However, if the engine room is warm the usual sources of liquid are from: liquid slugging or condensation in the discharge line.
    Certainly, condensation can happen in cold engine room. However, this amount isn't significant, because we don't have a lot of nh3 vapor to produce significant amount of liquid. When people see liquid in sight glass, this is liquid from discharge line.

  17. #17
    Join Date
    Sep 2008
    Location
    United States
    Age
    59
    Posts
    57
    Rep Power
    16

    Re: extreme winter operation

    to answer a few of the questions, my discharge pressures range from a low of 70psig to a high of 100psig with average (by time) of 80psig. the condenser water pumps are controlled by a thermostat that locks out operation below 28f. the condenser fan controls are set to 135psig with a 5psig differential. my evaps have defrost pressure regulators set a 75psig.

  18. #18
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: extreme winter operation

    Quote Originally Posted by chilldis View Post
    to answer a few of the questions, my discharge pressures range from a low of 70psig to a high of 100psig with average (by time) of 80psig. the condenser water pumps are controlled by a thermostat that locks out operation below 28f. the condenser fan controls are set to 135psig with a 5psig differential. my evaps have defrost pressure regulators set a 75psig.
    Your condensers are cooled by natural convection or by wind. When head pressure is lower than 130psig, you don't have a control of this pressure. I prefer to have control of head pressure. When head pressure 80psig or lower, you will have problem to defrost you evaporators. For now, probably you are lucky and head pressure during defrosting was in the range 80-100psig. Why do your fan control set to 135psig? I think that fan set point of 100psig will save you more energy.

  19. #19
    Join Date
    Sep 2008
    Location
    United States
    Age
    59
    Posts
    57
    Rep Power
    16

    Re: extreme winter operation

    good points Segei, I am in the process of fine tuning my system for maximum energy conservation. the 100psig setpoint seems to be a very logical step. as far as defrosts, with the low ambients come very low humidity levels that in turn allow 80psig discharge pressures to work well for this time of the season.

  20. #20
    Join Date
    Mar 2008
    Location
    united states
    Posts
    32
    Rep Power
    0

    Re: extreme winter operation

    We have been having same winter here. When the plant here is down that is the only time we have head pressure issues. So we just valve off the condensors, to combat the low head pressure. If it is still low at with these steps we then will start a freezer to get it back up to defrost. We also will just open the liquid returns this helps if closing the whole thing would be to much. Hope this helps.

  21. #21
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: extreme winter operation

    Quote Originally Posted by chilldis View Post
    good points Segei, I am in the process of fine tuning my system for maximum energy conservation. the 100psig setpoint seems to be a very logical step. as far as defrosts, with the low ambients come very low humidity levels that in turn allow 80psig discharge pressures to work well for this time of the season.
    Your coils won't defrost at 80psig. Probably, they don't have a frost at all. To have a frost on the coil, the temperature of this coil should be lower than dew point of surrounding air. Major source of the frost is ambient air. When outside temperature is -30F, dew point will in the range of -35F ~-40F. If your coldest coil has temperature -35f or higher, frost won't form on this coil.

  22. #22
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: extreme winter operation

    Quote Originally Posted by Poodzy View Post
    We have been having same winter here. When the plant here is down that is the only time we have head pressure issues. So we just valve off the condensors, to combat the low head pressure. If it is still low at with these steps we then will start a freezer to get it back up to defrost. We also will just open the liquid returns this helps if closing the whole thing would be to much. Hope this helps.
    Major reason of low head pressure during cold weather is direct wind. Some kind of shield will prevent plant from low head pressure. You won't need to valve off condensers or to run freezers. Sometimes people shut off some fans and put curtains on them(to protect condenser from direct cold wind).

  23. #23
    Join Date
    Mar 2008
    Location
    united states
    Posts
    32
    Rep Power
    0

    Re: extreme winter operation

    I know why we get low head pressure. Curtains would be nice but i dont think my boss would spring to outfit 15 condensors with them so the simplest way is to close the valves. What we have been doing for the last 30 years or so.

  24. #24
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: extreme winter operation

    Quote Originally Posted by Poodzy View Post
    I know why we get low head pressure. Curtains would be nice but i dont think my boss would spring to outfit 15 condensors with them so the simplest way is to close the valves. What we have been doing for the last 30 years or so.
    But it isn't the safest way. Usually, condensers don't have relief valves. One day somebody forgot to open valves and it can be problem at higher ambient temperatures. I think that it is easier to spend several hundred dollars to buy material for the curtains. Permanent shields will work even better.

  25. #25
    Join Date
    Mar 2008
    Location
    united states
    Posts
    32
    Rep Power
    0

    Re: extreme winter operation

    I guess i was under the assumption that ALL condensing units had to have srv valves. All of the ones we have do even are really old ristos and for not opening a valve that is supposed to be opened comes with the training i guess.

  26. #26
    Join Date
    May 2007
    Location
    Pennsylvania
    Age
    51
    Posts
    113
    Rep Power
    17

    Re: extreme winter operation

    Quote Originally Posted by Segei View Post
    Your coils won't defrost at 80psig.
    Odd that. We have every hot gas defrost in our building set at 70(+/-5)psig and they defrost just fine.

    I assure you they form frost, and the defrost cycle removes it.

  27. #27
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: extreme winter operation

    Quote Originally Posted by Poodzy View Post
    I guess i was under the assumption that ALL condensing units had to have srv valves. All of the ones we have do even are really old ristos and for not opening a valve that is supposed to be opened comes with the training i guess.
    You have a choice.
    1. Install wind shields and forget about low head pressure.
    2. Continue to open and close condenser valves.

  28. #28
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: extreme winter operation

    Quote Originally Posted by brian_chapin View Post
    Odd that. We have every hot gas defrost in our building set at 70(+/-5)psig and they defrost just fine.

    I assure you they form frost, and the defrost cycle removes it.
    I mentioned about condensing pressure. As far as I remember you have defrosting at 110psig or higher.

  29. #29
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: extreme winter operation

    Quote Originally Posted by Poodzy
    ... for not opening a valve that is supposed to be opened comes with the training i guess.
    No guess work needed. This should be part of your SOP's if you are doing this as an Operational Requirement.
    If all else fails, ask for help.


  30. #30
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: extreme winter operation

    Evaporators will most certainly defrost at ~75 psig if the regulators and pipe mains are sized correctly.

    The higher discharge pressures are required when the above is not properly done.
    If all else fails, ask for help.


  31. #31
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: extreme winter operation

    Quote Originally Posted by US Iceman View Post
    Evaporators will most certainly defrost at ~75 psig if the regulators and pipe mains are sized correctly.

    The higher discharge pressures are required when the above is not properly done.
    It depends.
    Hot gas defrosting is the triple process.
    1. Hot gas supply.
    2. Condensation at certain temperature(pressure) level.
    3. Condensate draining.
    75psig tell us that we have correct condensation level. But it tell us nothing about hot gas supply and condensate draining.

  32. #32
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: extreme winter operation

    Quote Originally Posted by Segei View Post
    It depends.
    Hot gas defrosting is the triple process.
    1. Hot gas supply.
    2. Condensation at certain temperature(pressure) level.
    3. Condensate draining.
    75psig tell us that we have correct condensation level. But it tell us nothing about hot gas supply and condensate draining.
    No argument from me on those points. I fully concur.

    For a hot gas defrost system to work well at these lower pressures the ability to provide an adequate supply of hot gas is determined by the hot gas supply pipe capacity. If this pipe cannot supply enough hot gas at a low pressure loss then you can have some problems.

    The next big issue is being able to drain the condensate from the coils during defrost as fast as it forms. This is dependent on the coil design (the coil circuits have to be free draining) and the method of controlling the defrost. Defrost relief valves work only on pressure and do not know the difference between liquid or vapor, only pressure. This is where drainers work very well, if properly applied.

    The last point is pressure. If you try to defrost at low pressures (just high enough for defrost to occur) you cannot have high pressure losses in the hot gas supply piping.
    If all else fails, ask for help.


  33. #33
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: extreme winter operation

    Quote Originally Posted by US Iceman View Post
    No argument from me on those points. I fully concur.

    For a hot gas defrost system to work well at these lower pressures the ability to provide an adequate supply of hot gas is determined by the hot gas supply pipe capacity. If this pipe cannot supply enough hot gas at a low pressure loss then you can have some problems.

    The next big issue is being able to drain the condensate from the coils during defrost as fast as it forms. This is dependent on the coil design (the coil circuits have to be free draining) and the method of controlling the defrost. Defrost relief valves work only on pressure and do not know the difference between liquid or vapor, only pressure. This is where drainers work very well, if properly applied.

    The last point is pressure. If you try to defrost at low pressures (just high enough for defrost to occur) you cannot have high pressure losses in the hot gas supply piping.
    Unfortunatly, many coils don't have free condensate draining.

  34. #34
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: extreme winter operation

    Quote Originally Posted by Segei View Post
    Unfortunatly, many coils don't have free condensate draining.
    In the past no one paid any attention to this issue. I believe the coil manufacturers are now doing a better job of engineering the coils to achieve this, although .... I am surprised that we as an industry continue to do the same old thing without thinking about how hot gas defrost actually works.

    Here is how to get gravity drainage. If you can drop a marble down any of the coil circuits, the marble should roll out of the circuit.
    If all else fails, ask for help.


  35. #35
    Inniswhe's Avatar
    Inniswhe Guest

    Re: extreme winter operation

    There was a concern regarding overpressure if the valves were closed to limit wind driven condensation in cold weather.

    Does closing a valve on the inlet to the coil only adequately limit the condenser capacity in extreme cold adequately ?

    By only closing the inlet valve the discharge side is open to the HP receiver.

    I suppose the condenser could draw a large of amount of liquid back up but with a sufficiently sized HP receiver will that not work effectively?

  36. #36
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: extreme winter operation

    If the condenser coils fill up with liquid and have closed valves on the condenser coils, you certainly have a potential bad issue. In this case you would be right to be concerned about over-pressure from liquid lock-up in the coils.

    Leaving the coil drain valve open will still allow the refrigerant to migrate back to the condenser coils.

    I've had a new system operating at about 70 psig discharge the last few weeks with below 0°F dry bulb temperatures. It starts up and runs just fine. The customer has had numerous start-up problems with his other systems though at various locations.
    If all else fails, ask for help.


  37. #37
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: extreme winter operation

    I think that closing inlet of the condenser will significantly reduce capacity of this condenser. However, closing condenser outlet will reduce capacity of this condenser to 0%. During winter operation we have opportunity for significant energy savings that we don't have in summer time. Many refrigeration plants can operate at condensing pressure below 100 psig and people should use this opportunity.

  38. #38
    Join Date
    Sep 2008
    Location
    United States
    Age
    59
    Posts
    57
    Rep Power
    16

    Re: extreme winter operation

    sorry I have been away from the forum for so long(new grandson living with us) After some fine tuning my system has been operating very well with a average discharge pressure of 95 psig. This whole change in system operating procedures has been a learning process for me. Every system operator should remember when you are the only person operating a system DO NOT try to make all the changes the "experts" suggest at one time. Small changes can have a large impact on system performance. I have tuned my system to operate well from ambients of 115 f. to -25 f. with a average energy savings of 23% over the past year. Thanks to all for the feedback and suggestions.

  39. #39
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: extreme winter operation

    Forgive me for my ignorance as our climate is much different to yours .
    Just want to learn how its done

    Where is the load coming from under such low ambient conditions ?
    Do you insulate hot gas lines as well as have them free draining back to condenser ?
    I guess you may have float at low points + drain back to suction .

    Where do you get heating for chillers or load out docks , is it hot gas ?

    We have cool stores with similar head pressures of 600kpa (86psi) in winter with 10 deg C ambients !

    I would have thought liquid injection at these pressures would be ok if sized for your climate as you can have it on boosters .
    It may only be affected by low discharge pressures starving it I would have thought .
    If 2 stage system could you single stage system under these conditions ?

  40. #40
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: extreme winter operation

    Quote Originally Posted by Ranger1
    Where is the load coming from under such low ambient conditions ?
    A production facility should have a relatively constant load. A cold storage warehouse can be quite different if no product cooling load is evident.

    Quote Originally Posted by Ranger1
    Do you insulate hot gas lines as well as have them free draining back to condenser ?
    I do. And use what you describe in the next quote below. I like inverted bucket traps form steam systems for this. The disc traps don't have enough capacity I think.

    You can still get hot gas, but you have to get it to condense for heat recovery since there is not much temperature available. For defrost, it depends on the defrost regulator pressure settings and how large the hot gas pipe is. If the pipe is too small it restricts the mass flow and slows down the defrost. The smaller pipe also adds pressure loss, which affects the defrost cycle also.


    Quote Originally Posted by Ranger1
    I guess you may have float at low points + drain back to suction .
    If all else fails, ask for help.


  41. #41
    br1uno's Avatar
    br1uno Guest

    Re: extreme winter operation

    Hi,

    Is overcompression (fixed VI ) at low discharge pressure a problem or waste of energy ?


    grtz





    sorry for my bad english

  42. #42
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: extreme winter operation

    Quote Originally Posted by br1uno View Post
    Hi,

    Is overcompression (fixed VI ) at low discharge pressure a problem or waste of energy ?


    grtz





    sorry for my bad english
    I think that lower condensing pressure will save you more energy than keeping Vi. It is easy to test. Compare compressor energy use at two different condensing pressures. What are your discharge pressures and suction pressure?

  43. #43
    Join Date
    Jan 2010
    Location
    USA
    Posts
    41
    Rep Power
    0

    Re: extreme winter operation

    personal stuff sorry
    Last edited by jaysephus; 04-02-2010 at 06:49 PM. Reason: personal stuff sorry

  44. #44
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: extreme winter operation

    Quote Originally Posted by jaysephus View Post
    I have to run a cold storage in the very cold winter months. After doing much fine tuning with my system I can actually get liquid to move with 45 psi discharge pressure. I use an FES screw with liquid cooling and it's suggested lowest psi to keep cooling is 100psi at least, but it does work at 45psi. What my main problem is that my cold storage low temp recirculator is filled with discharge pressure. It needs high discharge pressure to push liquid into the low pressure receiver and 45 seems to be the happy number. If I can't get 45 I have to start my process freezer compressors to get high side up again(my process freezer & cold storage freezer are common)
    We actually do isolate the inlet to the condenser, i forget who brought that up, but yes it does work for me, to a point. When I have trouble with low head pressure, one by one I can isolate inlets to condensers (don't forget the equalizing lines) and I can get a rise in head pressure. The very last thing is to isolate a condenser. I have large condensers and in the winter it all goes up to them. So before winter comes it would be a good idea while all the ammonia is in the engine room to isolate a condenser, pump it down a little to try and get all the liquid out. There is no concern of overpressurizing trapped liquid for me, it's minus 10F all winter, and I have PRV's on the condensers just in case.
    How do you supply liquid to the evaporators? Do you have CPR or liquid pumps? How do you do defrost?

  45. #45
    Join Date
    Jan 2010
    Location
    USA
    Posts
    41
    Rep Power
    0

    Re: extreme winter operation

    personal stuff sorry
    Last edited by jaysephus; 04-02-2010 at 06:50 PM. Reason: personal stuff sorry

  46. #46
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: extreme winter operation

    Quote Originally Posted by jaysephus View Post
    The liquid to the evaporators is liquid pump feed, two cornell pumps. I live in the northern US and when it is that cold out the air is so dry we have no need for it. The load is so light during these times it's sometimes colder outside than inside the cold storage. As for defrosts, maybe different for you but for me I straight up don't need them. The only door that opens in the winter time is the truck dock doors, going to the outside. By October all of the product is inside of the cold storage so the doors to the warm warehouse never open. I have 7 large evaporators and I check them out everyday and they look clean with not ice. I think one of the reasons why is that the coils are never asking to be feed with ammonia because there is almost no load to heat up the room. Setpoint is 0F and when the RTD reads 2F it turns on the valve to feed ammonia, the thing is it holds it's 0F temp so well. Defrosting is not needed all winter. All I need is my 45psi or more to help move liquid around and I'm ok. However, some days I'll come in and we had a minus 25F night and the engine room is lit up with alarms. At 2am it just couldn't do it anymore and either I get a low level liquid alarm or the FES screw shuts down with high oil temp from lose of pressure for liquid cooling. I start up my low side process refrigeration, blah blah blah and away I go. Great thing for me is I get a few months of shut down time, all of the product is out of the freezer and I get to do maintenance on everything.

    This works well for me, and maybe just me and my system. My system may be nothing like yours, but at least you can maybe better understand mine and take the good with the bad. Good luck!!!
    Definitely, your plant is unique.
    FES recommendation about 100 psi liquid pressure is for 100% loaded compressor. Your compressor is most likely unloaded.
    To prevent low head pressure. I would leave operating one smallest condenser or one cond. fan. Install wind shields. You won't get low head pressure due to air natural convection. Only wind can bring it so low. Leave one operating evaporator per cold room, this prevent fluctuation of the refrigeration load. Suction pressure can be increased. Before cold night, freezer set point can be reduced by 1 F and it can be reseted back during the day.

  47. #47
    Join Date
    Jan 2010
    Location
    USA
    Posts
    41
    Rep Power
    0

    Re: extreme winter operation

    personal stuff sorry
    Last edited by jaysephus; 04-02-2010 at 06:50 PM. Reason: personal stuff sorry

  48. #48
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: extreme winter operation

    Quote Originally Posted by jaysephus View Post
    that is exactly what i do, you know your stuff. wind shields would be nice i do agree, but i doubt my manager would spend the money for that one. right, i can look at the past trends on the plc but i doubt the compressor ever loads up. we isolated all the way down to half of a condenser side out of 5 large condensers. we take the ones with the de-superheaters out right away, way to much surface area on those. may i ask, what are you keeping cold? what is your system like?
    I don't have a plant right now. Currently, I help people to run plants efficiently. So I saw many different plants. Sometimes people use tarp and 1x1 wood(and strings) to make the curtains. Roll up for summer and roll down for winter. It isn't expensive.

Similar Threads

  1. Operating Evaporative-Condensers in Extreme Winter Conditions.
    By stepperider in forum System Optimization
    Replies: 20
    Last Post: 29-07-2009, 09:35 PM
  2. Cold store Bad operation
    By Noori in forum Supermarket Refrigeration
    Replies: 14
    Last Post: 18-03-2009, 03:32 PM
  3. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  4. Trane Chiller low temperature operation
    By Brads in forum Industrial
    Replies: 2
    Last Post: 20-01-2008, 08:18 AM
  5. AC in the winter in wisconsin! will it work?
    By kurt854 in forum Air Conditioning
    Replies: 4
    Last Post: 13-06-2007, 06:18 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •