    Copeland Scroll Compressor



    It's model ZR23K1-PFJN522

    Single phase, 240v, 50z, 10.2A
    R-22
    Made 1994

    This is going too cost the earth too run i know it but will it run okay on my house hold sparks or blow it?

    Also im trying too find the full specs for it online but no luck at all with it!

    Anyone able too help



  2. #2
    Join Date
    Jan 2009
    Location
    Australia
    Age
    60
    Posts
    108
    Rep Power
    16

    Re: Copeland Scroll Compressor

    I haven't seen other threads on this but I'm assuming its A/C that you are using it on.
    Generally Coefficient of performance (COP) for an average A/C is about 2.5 - 3 which means that refrigeration power is approximately 2.5 - 3 times the kW of the input power in kW. At 240v and 10.2A, Watts = V x I ( 240v x 10.2A). Input power is 2.45kW. Lets work on the lower end of the efficiency and say that the COP is 2.5. Refig power= Input Power x COP (2.45kW x 2.5). Refrig power about 6.1kW.

    If you can't find anything, this may get you started.

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Copeland Scroll Compressor

    Is this OK?
    pjalchemist.pdf

    pjalchemist2.pdf

    What is use for this compressor?
    Last edited by nike123; 17-01-2009 at 06:25 AM.

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Copeland Scroll Compressor

    In answer to your question, check your kettle, it runs at higher amperage than that compressor.

    You might need to run it on a separate circuit so that you can put a motor rated circuit breaker in line with it for starting purposes.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Oct 2008
    Location
    philippines
    Posts
    36
    Rep Power
    0

    Re: Copeland Scroll Compressor

    You can find this model's full specification at emersonclimate.com.
    However, here is the full specification of that compressor. The correct model number is ZR23K1-PFJ.
    Attached Files Attached Files

  6. #6
    Join Date
    Jun 2008
    Location
    India
    Age
    56
    Posts
    64
    Rep Power
    16

    Re: Copeland Scroll Compressor

    Quote Originally Posted by Scramjetman View Post
    At 240v and 10.2A, Watts = V x I ( 240v x 10.2A). Input power is 2.45kW.
    You have missed mutiplying V x I by power factor - which for single phase compressor could be 0.85 to 0.9

Similar Threads

  1. LG heat pump problem
    By back2space in forum Heat Pumps
    Replies: 132
    Last Post: 01-02-2009, 11:23 PM
  2. compressor / electrical problem
    By Northdude in forum Commercial
    Replies: 6
    Last Post: 17-01-2009, 10:24 AM
  3. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  4. SL/SB-400 Pump Down Procedures
    By absolute-zero in forum Transport
    Replies: 1
    Last Post: 29-01-2008, 09:27 PM
  5. Compressor pumping efficiency
    By shogun7 in forum Fundamentals
    Replies: 0
    Last Post: 25-02-2004, 10:50 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •