    Sanyo VRF system and supplemental heat



    I have a Sanyo 12 ton VRF system and 6 U model concealed duct low static indoor units. I added the electric heat strips and have them hooked up to the option plug on the indoor units. It does activate my 12v relay as predicted but the problem is the heat strips sail switches will not make with the low static units. Does anyone know if there is a way to increase my fan speed in the heating mode.




  2. #2
    whitetail67's Avatar
    whitetail67 Guest

    Re: Sanyo VRF system and supplemental heat

    Camenisch,

    Th Sanyo "U" models I have seen come with a connector for increasing duct static. Sounds like your big issue is overcoming the low low speed that Sanyo maintains in heat mode until the indoor coil warms up which they refer to as Standby mode. Wonder what would happen if you take the fan wire from low low and incorporate it into low or even medium speed winding of the motor? Only bad thing is you would get that first intial cold air blast until the indoor coil warmed. Also, the other problem would be when the condition in the space is satisfied you would then be blowing cold air into the space. I guess better not to redesign this system other then how the manufacturer states.

  3. #3
    Join Date
    Jul 2005
    Location
    Ireland
    Age
    57
    Posts
    164
    Rep Power
    19

    Re: Sanyo VRF system and supplemental heat

    Hi Guys,

    the new u type fan coil can be set to high static setting through the detailled setting data for the indoor eeprom.

    To access this please see the attached doc. Change code 5d to 0003. to achieve high static.

    To over come the low low speed problem Please set code 05 to 05 this will ensure mimimum low speed duiring heat thermostat off .


    Regards
    T

  4. #4
    Join Date
    Jul 2005
    Location
    Ireland
    Age
    57
    Posts
    164
    Rep Power
    19

    Re: Sanyo VRF system and supplemental heat

    Sorry guys can't send necessary data file is to big pvt message me and I will mail you from my company account

Similar Threads

  1. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  2. Sanyo system needs supplemental heat
    By mchild in forum Air Conditioning
    Replies: 2
    Last Post: 29-11-2007, 02:50 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •