    Frozen TXV



    We installed packaged chiller on the roof. Ambient was -30C and suction dropped. It was found that after heating the power element of the TXV, the pressure rose.

    Is anyone aware of this kind of siuation?

    How can we keep TXV element and capillary warm enough that the charge inside won't liquify?



  2. #2
    Join Date
    Feb 2005
    Location
    ENGLAND
    Age
    54
    Posts
    22
    Rep Power
    0

    Re: Frozen TXV

    What are you trying to chill at an ambient of -30?

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Frozen TXV

    Build an insulated box around the TXV - but - as the man asked --

    Why do you have a chiller running with those ambients - or - are you just commissioning ?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Mar 2005
    Location
    Belgium
    Age
    58
    Posts
    110
    Rep Power
    20

    Re: Frozen TXV

    Hi,
    since this is a chiller, I presume the TXV is one with MOP.
    MOP valves have a limited charge. If the charge has migrated from the bulb to the valve top, a raise in temperature at the bulb (superheat raise) will not open the valve, because the is no liquid left in the bulb who could produce a pressure increase above the diaphragm. Result : the valve will stay closed.
    Heating up the thermostatic element is the right thing to do, to let the charge re-migrate towards the bulb.

    An insulated box around the TXV will prevent this charge migration to the valve top. But be careful: during very warm periods it could result in a the same effect. If the valve is better insulated then the bulb, it will be colder in the valve then at the bulb (at standstill) ... resulting in a charge migration ...
    It all depends on the situation. A selfregulating flexibel heating (combined with some insulation?) could be a solution.

  5. #5
    Join Date
    Apr 2006
    Location
    Canada
    Age
    53
    Posts
    154
    Rep Power
    19

    Re: Frozen TXV

    Thanks BESC5240,

    Yes, it has MOP valve.
    We'll change the power element.
    Do we still need insualtion with the regular charge bulb?

    This is a application of packaged medical chiller sitting on the roof and chilling liquid for MRI cooling.

    Thanks to all.

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Frozen TXV

    Quote Originally Posted by jwasir View Post
    Thanks BESC5240,

    Yes, it has MOP valve.
    We'll change the power element.
    Do we still need insualtion with the regular charge bulb?

    This is a application of packaged medical chiller sitting on the roof and chilling liquid for MRI cooling.

    Thanks to all.

    Than it is better to install some free cooling coil. It could save your customer up to 75% of energy bill and prolong machine life. Also, you could earn additional money on upgrade.

    Check this pdf!

    P.S. I don't advertise this company products, I only illustrating what I mean.
    Last edited by nike123; 16-01-2009 at 02:34 PM.

  7. #7
    Join Date
    Mar 2005
    Location
    Belgium
    Age
    58
    Posts
    110
    Rep Power
    20

    Re: Frozen TXV

    Quote Originally Posted by jwasir View Post
    Yes, it has MOP valve.
    We'll change the power element.
    Be careful. The chiller manufacturer did install the MOPvalves for a reason (compressor protection at high suction pressure). If you replace them by standard thermostatic elements, the compressor(s) is (are) no longer protected ...


    Quote Originally Posted by jwasir View Post
    Do we still need insualtion with the regular charge bulb?
    Sorry, but I have no experience on ambient temperatures of -30°C ..

  8. #8
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Frozen TXV

    Quote Originally Posted by jwasir View Post
    We installed packaged chiller on the roof. Ambient was -30C and suction dropped.
    So what? Why is this a problem?

  9. #9
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Frozen TXV

    Quote Originally Posted by jwasir View Post
    This is a application of packaged medical chiller sitting on the roof and chilling liquid for MRI cooling.
    What temperature are you chilling the liquid to?

  10. #10
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Frozen TXV

    Quote Originally Posted by jwasir View Post
    Thanks BESC5240,

    Yes, it has MOP valve.
    We'll change the power element.
    MOP has nothing to do with it. Do not change the power element.

  11. #11
    Join Date
    Apr 2006
    Location
    Canada
    Age
    53
    Posts
    154
    Rep Power
    19

    Re: Frozen TXV

    Gary,

    This is a Medical Chiller used to cool MRI magnet.

    The Glycol temp. used is cooled @ 48F.

    So you think changing the power element will not change the scenario? Any other suggestions?

    Thanks,

  12. #12
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Frozen TXV

    Running the chiller in low ambients just doesn't make sense. A free cooler loop is the answer.

    If you absolutely must run the chiller, make sure the TXV bulb is mounted with the cap tube up and heavily insulate both the TXV and the bulb.

  13. #13
    Join Date
    Jun 2005
    Location
    California
    Posts
    394
    Rep Power
    19

    Re: Frozen TXV

    Wrap it with prestite tape as Gary said

  14. #14
    Marc O'Brien's Avatar
    Marc O'Brien Guest

    Re: Frozen TXV

    In -30 degree conditions with an insulated evaporator assembly being warmed by 48 degree fluid there will be TEV charge migration and especially with a MOP system.

    Sporlan produced a TEV assembly where the TEV-side power assembly was oil driven being connected by an oil filled capillary to a gas driven power element mounted right on top of the sensing bulb. This would be ideal in this circumstance.

    Wrapping the TEV power assembly with a self regulating heater tape would be a quick and effective solution.

    Better yet, install a hysave liquid pump in the liquid line, install a bypass system round the compressor and turn the system into a 100/1 COP pump assisted thermosyphon package - during low ambients.

  15. #15
    Join Date
    Jan 2009
    Location
    Queensland
    Age
    64
    Posts
    113
    Rep Power
    16

    Re: Frozen TXV

    if you do decide to replace the MOP valve, you might want to look at fitting a crankcase pressure regulating valve. I'm not a big fan of MOPs and would go for a CPR valve by preference.
    That free cooling loop sounds like a great idea if properly implemented. It's not something I see round here with our cold winter nights rarely getting below 5C.

  16. #16
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Frozen TXV

    Hi Marc

    Quote Originally Posted by Marc O'Brien View Post
    In -30 degree conditions with an insulated evaporator assembly being warmed by 48 degree fluid there will be TEV charge migration and especially with a MOP system.

    Sporlan produced a TEV assembly where the TEV-side power assembly was oil driven being connected by an oil filled capillary to a gas driven power element mounted right on top of the sensing bulb. This would be ideal in this circumstance.

    Wrapping the TEV power assembly with a self regulating heater tape would be a quick and effective solution.

    Better yet, install a hysave liquid pump in the liquid line, install a bypass system round the compressor and turn the system into a 100/1 COP pump assisted thermosyphon package - during low ambients.
    If the power head is colder than the bulb, then the charge will migrate to the power head, whether the charge is MOP or not.

    But yes... a small heater on the power head would ensure that it is never colder than the bulb.

    When using the liquid pump, would the compressor bypass be needed? Wouldn't the pressure difference be sufficient to lift the suction and discharge reeds?

  17. #17
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Frozen TXV

    Quote Originally Posted by Gary
    When using the liquid pump, would the compressor bypass be needed? Wouldn't the pressure difference be sufficient to lift the suction and discharge reeds?
    You need the bypass to reduce the pressure difference. By having a low pressure loss you allow the refrigerant to move from the evaporator to the condenser with minimal impacts.

    If the pressure in the evaporator rises too much to overcome the valves, etc you limit the system capacity at the ambient conditions.
    If all else fails, ask for help.


  18. #18
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Frozen TXV

    Quote Originally Posted by US Iceman View Post
    You need the bypass to reduce the pressure difference. By having a low pressure loss you allow the refrigerant to move from the evaporator to the condenser with minimal impacts.

    If the pressure in the evaporator rises too much to overcome the valves, etc you limit the system capacity at the ambient conditions.
    The bypass then, would consist of a pipe from suction to discharge with a check valve in it?

    Would the liquid pump be necessary for it to work?

  19. #19
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Frozen TXV

    Quote Originally Posted by Gary
    Would the liquid pump be necessary for it to work?
    Yes, if the evaporator is above the condenser. You need some way to get the liquid up to the evaporator, so that it can boil.

    Otherwise, you need to be very careful in planning the piping for adequate liquid delivery to the evaporator if it is located below the condenser.

    Thermosyphon system design is not similar to normal refrigeration piping design. You need to minimize pressure loss!

    You can use a check valve or an electrically powered high performance butterfly valve.
    If all else fails, ask for help.


  20. #20
    Marc O'Brien's Avatar
    Marc O'Brien Guest

    Re: Frozen TXV

    Quote Originally Posted by Gary View Post
    Hi Marc



    If the power head is colder than the bulb, then the charge will migrate to the power head, whether the charge is MOP or not.

    But yes... a small heater on the power head would ensure that it is never colder than the bulb.

    When using the liquid pump, would the compressor bypass be needed? Wouldn't the pressure difference be sufficient to lift the suction and discharge reeds?
    Often with a non mop valve at least some charge remains within the bulb.

    You do need a bypass round the compressor because you're especially using the pump to create a liquid over-feed effect. The concept is more like pump assisted heat pipes than thermosiphon. Heat Pipes involve phase change and Thermosiphon does not. The pump creates an overfeed in order that heat exchanger U values can be raised by about 30%. With this increase in U value the heat exchangers can perform the designed load with just 76% of the design TD.

    Chilled water temperatures are regulated by cycling the condenser fans.

    Ordinarily condensers in low ambient with all their fans off can still achieve 30% capacity just on natural convection up through the coil. In this case the temperature difference between condensing liquid and air is so slight that cycling the fans almost entirely unloads the system without any massive pressure fluctuations.

    I have attached a design I have been working on - the illustration is the most basic of the idea.

    There are only two non return valves and no solenoid or motorised valves. The accumulator sits above the condenser. The compressor can start at anytime it wishes without any preparation cycles.

    You saw it here first :-)
    Attached Images Attached Images

  21. #21
    Marc O'Brien's Avatar
    Marc O'Brien Guest

    Re: Frozen TXV

    Keep in mind too that my design concept would require a receiver for use in warmer ambients to store the excess refrigerant only used during free cooling over-feed operation and cool ambient floating head operation.

  22. #22
    Join Date
    Feb 2008
    Location
    Norway
    Age
    57
    Posts
    446
    Rep Power
    17

    Re: Frozen TXV

    Interesting system Marc. How do you avoid the compressor filling with some liqiud when the low ambient mode is active? By placing the compressor as the highest component and cranckcase heater?

  23. #23
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Frozen TXV

    What's a Kevin Pieterson?

  24. #24
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Frozen TXV

    You saw it here first :-)
    Maybe.... I have a design like this going in right now, so you are late and second.
    If all else fails, ask for help.


Similar Threads

  1. Pics of Frozen indoor A/C units
    By Greengrocer in forum Air Conditioning
    Replies: 0
    Last Post: 07-12-2008, 08:01 PM
  2. Nite shades causing frozen product
    By kengineering in forum Commercial
    Replies: 27
    Last Post: 11-04-2006, 12:59 AM
  3. Freezing tunnels vs frozen products store
    By jaxie072 in forum Technical Discussions
    Replies: 6
    Last Post: 08-03-2006, 02:51 AM
  4. Frozen Evaporator Motors
    By Brian_UK in forum Commercial
    Replies: 15
    Last Post: 03-05-2002, 11:19 PM
  5. Frozen Coils
    By subzero*psia in forum Commercial
    Replies: 0
    Last Post: 25-10-2001, 02:08 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •