Good Day to All,
I was inquiring about a Sanyo mini Ecoi outdoor unit hooked up to (5) indoor air handlers. The system was started and worked well for a few weeks and then the wired remote controllers started showing a E04 error code. System was reset by cycling the main line voltage power and did come back on and run shortly, but then again would fault out on this E04 error code. Any feedback on this issue would be greatly appreciated. Thanks in advance to all who respond to this post.
15-01-2009, 09:17 AM #2
Re: Sanyo VRF Error Code E04
Hi!
Error codes explanation you can find here
http://www.oceanairdist.co.uk/contra...cal/codes.html
15-01-2009, 03:20 PM #3
- Sep 2007
- Split Croatia
- 57
- 6,175
- 6
- 36
Error in receiving serial communication signal.
When turning on the power supply, the number of connected
indoor units does not correspond to the number set. (Except R.C.
address is “0.”)
16-01-2009, 12:09 PM #4
E04 code does not necccesarily mean your issue is at the indoor units. It simply means loss of communication. If you have checked the comm line, verified the outdoor unit has the amount of indoors units set properly then reset the system and ohm out the U1 U2 line at the indoor units. You should read about 100 ohms. You can also reset the amount of indoor units at the outdoor unit, break the comm line so it is just at the first unit and re address for one indoor unit.. Test the ohm value again. Possible outdoor unit main PCB board is bad.
22-01-2009, 06:13 PM #5
Gentleman,
All your replies were greatly appreciated. I wanted to follow up and let you know what was found. It seems a mouse had made a nest in the outdoor unit by the Filter board and shorted several of the wires which feed over to the main board causing this E04 error code. Thanks again to all who replied to this post!
Sanyo fault codes
By Slim R410a in forum Air ConditioningReplies: 3Last Post: 03-11-2008, 09:02 PM -
sanyo
By cooltools in forum CommissioningReplies: 1Last Post: 27-10-2008, 08:40 PM -
Sanyo system needs supplemental heat
By mchild in forum Air ConditioningReplies: 2Last Post: 29-11-2007, 03:50 PM -
fault on a sanyo unit
By marc5180 in forum Air ConditioningReplies: 7Last Post: 18-08-2007, 11:04 PM -
Sanyo inverter split unit
By cikku in forum DomesticReplies: 3Last Post: 22-05-2006, 06:07 PM