Re: High discharge temp
You have roughly 50C condensing. Air on/off is 28/38. This indicates the condenser is either to small or dirty or both.
A good condenser should ideally acheive roughly 38C/1350kPa discharge at 28C air on/ambient. If you had such HP conditions the discharge temp would be reduced to roughly 85-90C.
Edit:
The suction pressure could ideally be slightly higher as Nike sugests, say 430 to 460kPa. Higher suction pressure would also cause a decrease in the disharge temp.Last edited by SteinarN; 15-01-2009 at 09:26 AM.
-
20-01-2009, 07:05 AM #2
Re: High discharge temp
A dirty condenser would give a much higher air off temp given the high condensing temp.
Overcharge backs liquid up into the condenser, reducing its effective area... so in effect this would give the appearance of an undersized condenser.
Once the excess refrigerant is removed, the suction pressure will drop and the superheat will increase, clearly indicating a high side restriction (plugged drier, kinked liquid line, restricted cap tube, etc.).
Similar Threads
-
MP66 & Compressor Overheating
By Intermez in forum Technical DiscussionsReplies: 111Last Post: 13-04-2010, 08:58 PM -
Hotpoint FFA71 Freezer High Temp Light / Fridge is Freezing
By sumnerpa in forum Trouble ShootingReplies: 1Last Post: 19-08-2008, 03:16 PM -
Grasso 69, Discharge Temp to High
By Jomoniak in forum NH3Replies: 14Last Post: 05-07-2008, 07:58 AM -
Compressor loading, cooling, and range of operation.
By Air duster in forum FundamentalsReplies: 10Last Post: 02-04-2008, 08:39 AM -
GSHP discharge temp high
By Lc_shi in forum Trouble ShootingReplies: 6Last Post: 20-01-2005, 08:37 AM