    Thumbs up anybody pls urgent



    Hi friends,
    Currently iam facing a problem in Chiller the supply chilled water temperature measured near the AHU is 16 degree celcius ( which should be 7 )the return is 20, the chiller was mainted by subcontracter and AHU belongs to me. I said the problem is in the chiller, but the subcon refused to agree and said the chiller is working properly, The problem may in the AHU as the return air temperature is high the chilled water supply temperature is also high is it true? if so how the delta T is 4 degree celcius ( i hope normally it should be 5.5 degree celsius )

    my question is if the return air temperature is high is it possible to raise the CHWT to 16 degree celcius

    if the subcon statement is correct as there are no proper airflow then there is no proper heat transfer also how come the CHWT rise then

    anybody can fix this problem pls with proper justification

    regards,
    Balaji



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: anybody pls urgent

    What is AHU air temperature and RH% (or DB and WB) in and out?
    What is AHU air flow?

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: anybody pls urgent

    Quote Originally Posted by balaji View Post
    my question is if the return air temperature is high is it possible to raise the CHWT to 16 degree celcius
    Yes it is! Chiller could only maintain temperature difference! If flow is unchanged, temperature deference will be according to produced chiller power.
    So, if you have same power output at 7°C water in and at 12°C water in, then acordingly, water out will be, say 11°C (4K delta) and 16°C.

    if the subcon statement is correct as there are no proper airflow then there is no proper heat transfer also how come the CHWT rise then
    If you don't have proper air flow then heat is not transferred from air to water in quantities to make bigger delta T of water in and out. Therefore your lower delta T than you expect (you expected 5.5K) but it could be also indication that you have too much water flow.

    anybody can fix this problem pls with proper justification
    Check airflow and air temperatures and RH for evaluation on AHU performance.

  4. #4
    Join Date
    Jan 2009
    Location
    Queensland
    Age
    64
    Posts
    113
    Rep Power
    16

    Re: anybody pls urgent

    Quote Originally Posted by balaji View Post
    Hi friends,
    Currently iam facing a problem in Chiller the supply chilled water temperature measured near the AHU is 16 degree celcius ( which should be 7 )the return is 20, the chiller was mainted by subcontracter and AHU belongs to me. I said the problem is in the chiller, but the subcon refused to agree and said the chiller is working properly, The problem may in the AHU as the return air temperature is high the chilled water supply temperature is also high is it true? if so how the delta T is 4 degree celcius ( i hope normally it should be 5.5 degree celsius )

    my question is if the return air temperature is high is it possible to raise the CHWT to 16 degree celcius

    if the subcon statement is correct as there are no proper airflow then there is no proper heat transfer also how come the CHWT rise then

    anybody can fix this problem pls with proper justification

    regards,
    Balaji
    Balaji, if your chilled water supply temp is 16C, you're not going to get much cooling out of it. I would put the problem back on the chiller.
    If it can't give you your 7C supply, the problem is not at your end.

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: anybody pls urgent

    Quote Originally Posted by Slatts View Post
    Balaji, if your chilled water supply temp is 16C, you're not going to get much cooling out of it. I would put the problem back on the chiller.
    If it can't give you your 7C supply, the problem is not at your end.
    If problem is exclusively at chiller side than Chiller water temperature difference will be lower than 4°C.

  6. #6
    shamsheer's Avatar
    shamsheer Guest

    Re: anybody pls urgent

    how maney problems? the chiller compressor runs after 10 minits cut off again run again cut off why this problem coming reciprocating,100ton
    compressor

  7. #7
    Join Date
    Sep 2006
    Location
    italy
    Age
    53
    Posts
    93
    Rep Power
    18

    Re: anybody pls urgent

    If water delta is 4K means the water flow is more than nominal flow and this is still ok.
    If the chiller can`t go down more than 16 degree means the cooling heat exchanger from AHU absorb too much heat.
    The chiller could be undersized or the return air temperature of AHU is to high.

    regards

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: anybody pls urgent

    Water flow could be measured and actual cooling capacity calculated from that. Also, air flow at condenser could be measured and corresponding condenser actual capacity could be measured from that to establish is the chiller a problem.

  9. #9
    Join Date
    Nov 2007
    Location
    singapore
    Age
    45
    Posts
    24
    Rep Power
    0

    Re: anybody pls urgent

    Also, air flow at condenser could be measured and corresponding condenser actual capacity could be measured from that to establish is the chiller a problem.
    How to measure and calculate can you brief me pls

  10. #10
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: anybody pls urgent

    Quote Originally Posted by balaji View Post
    Also, air flow at condenser could be measured and corresponding condenser actual capacity could be measured from that to establish is the chiller a problem.
    How to measure and calculate can you brief me pls

    By using anemometer and measuring air speed across condenser fins in few points and average speed is calculated. Then calculating area of condenser fins by measuring with and length of condenser . From that measured data you then calculate air flow by multiplying speed with area.
    Or, you could use data about air flow from technical data of chiller if you are sure that fan is OK and at full speed and that condenser is clean.

    Now you need to measure delta T of air at condenser and insert that in this handy software from our member Marc L O'Brien.
    Lot of calculations could be done directly on his site:
    http://fridgetech.com/calculators/

  11. #11
    Join Date
    Jan 2009
    Location
    India
    Age
    42
    Posts
    13
    Rep Power
    0

    Re: anybody pls urgent

    I think your AHU inlet liquid tempreture is high. So i think your chiller is not pull down the temprature below 16 degree C .Or poor insulation on your hydronic cycle.

  12. #12
    HVAC Master's Avatar
    HVAC Master Guest

    Re: anybody pls urgent

    Balagi, I would recommend analysis of design values, It should not be a single AHU there. Try to look what are Heat loads, chiller capacity, CHW flow rate through the pumps, cooling tower or ambient air temperature etc. With out it your question is not answerable

Similar Threads

  1. copeland compressor!!! urgent
    By andrew20441 in forum Commercial
    Replies: 3
    Last Post: 15-10-2008, 10:02 PM
  2. urgent
    By A_Ahed in forum Trouble Shooting
    Replies: 6
    Last Post: 31-07-2007, 09:45 AM
  3. urgent
    By Dimitris in forum Trouble Shooting
    Replies: 7
    Last Post: 18-10-2006, 05:55 AM
  4. Urgent G Fault Codes Needed
    By botrous in forum Trouble Shooting
    Replies: 10
    Last Post: 08-08-2005, 08:13 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •