    problem with an hermetic pump



    HI Guys:

    I have a problem with an hermetic pump, this pump works in a ammonia recirculation system with a vertical separator vessel, the pump usually works good but when the system starts its cycle of defrost ( hot gas defrosting ) after the for minutes the differential pressure of the pump goes down and the differential pressure switch turns off the pump. Someone could explain me what is happen?



  2. #2
    Join Date
    Jul 2006
    Location
    USA
    Age
    73
    Posts
    865
    Rep Power
    26

    Re: problem with an hermetic pump

    We have little information to go on here. We do not know how many evaps you have, exactly where in the cycle this occurs, what is happening to the suction pressure etc.
    The most likely cause, without knowing all the details, is a sudden drop in suction pressure during the cycle. This can cause bubbles to form, which will make the pump cavitate.
    A good explanation of this can be found here.
    http://en.wikipedia.org/wiki/Cavitation
    Usually this can be adjusted out with unloaders, or by other means.

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: problem with an hermetic pump

    NH3LVR has the right idea I think. Any time the pump does not create differential pressure while running it either has no liquid in the pump or the pump is cavitating.

    Cavitation occurs when the pump suction pressure drops below the vapor pressure of the liquid ammonia. Essentially, this means the liquid refrigerant is boiling because the pressure of the liquid is lower than what the pressure should be at the saturation temperature.

    What you are describing seems common to other situations I have seen. When the evaporator(s) start to come out of defrost, the pressure in the vessel starts to rise. This causes the compressors to load up, which drops the suction pressure. If this happens to cause the pressure to drop just enough while the pump is running it can cause cavitation.
    If all else fails, ask for help.


  4. #4
    Join Date
    May 2007
    Location
    India
    Posts
    688
    Rep Power
    17

    Re: problem with an hermetic pump

    I had attached a paper from ARI last time, which had given the basic connections of Hot gas return to avoid this situation. But since the Info is not very clear, it is difficult to see if that is the point

  5. #5
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: problem with an hermetic pump

    May I just add to the excellent advise above.
    Try looking at the working liquid level within the separator.
    Is there room to raise it slightly?
    Has it changed recently?
    Meaning is this a new problem or historic?
    Have you changed the usage of any of the chambers it supply's?
    Basically as has been already said you need to prevent the sudden fluctuations of liquid/ pressure within the vessel.
    Cheers Grizzly

Similar Threads

  1. Markus heat pump problem
    By westray7 in forum Trouble Shooting
    Replies: 1
    Last Post: 09-12-2008, 02:40 PM
  2. How to find NH3 hermetic pump
    By sakchai21 in forum Industrial
    Replies: 7
    Last Post: 23-10-2008, 08:57 PM
  3. Replies: 14
    Last Post: 27-08-2008, 08:57 PM
  4. neslab chiller water pump problem
    By bill0577 in forum Trouble Shooting
    Replies: 5
    Last Post: 19-10-2006, 05:22 PM
  5. Pump down control problem
    By frank in forum Air Conditioning
    Replies: 17
    Last Post: 22-09-2006, 11:01 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •