    Copeland Glacier Scroll



    Need some help.Got a Copeland scroll.
    Model ZF13K4E-TFD-551
    Compressor has a third port....on about same level as the LP side. its smaller in size. Whats this for?

    Also on the top of the compressor right in the middle there is a small hole. Is this for some unloader device?

    Someone said these scrolls require liquid injection to keep the head cool. Is that third port , which should be fitted with a rotolock valve have anything to do with it??

    Any help appreciated...



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Copeland Glacier Scroll

    my dear friend.

    lovely machine, 4hp 3610 w at -23.3C.

    the port you mantioned is for the liquid injection and the top small hole, is for the temp. sensor.
    it should be connected to the liquid line.
    didnt they give you all the gear for that? it should be with the compressor as it is part of it!!!

    go to this link and check it out http://www.ecopeland.com/prodcat.cfm...ref=5&prod=410

    any help?

    you know how to reach me.

    chemi

  3. #3
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,119
    Rep Power
    26

    Re: Copeland Glacier Scroll

    Thanks Chem, downloaded the drawings....liquid injection is a feature I have not used before. been in touch with wholesaler today, the liquid injection fitting was not supplied with the rotolock valves.

    The temperature sensor did come with the compressor.....only my engineer was going to fit it to the suction line!!

    So....next question......How the ****ens do I "effect" liquid injection cooling???? Where do I draw the cool refrigerant from??? Scroll compressors are something new we are starting to use.....hence our ignorance on the subject.

  4. #4
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,119
    Rep Power
    26

    Re: Copeland Glacier Scroll

    And just one more thing.......

    It says in bold above.......Aiyub.....Moderator, etc , etc........and......." generallly nice guy"

    Dont you believe a word of it!!!

  5. #5
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Copeland Glacier Scroll

    after the the liquid reciever, install a T with a ball valve towards the compressor and connect it to the liquid injection unit.

    get from copeland europe all the instructions for this compressor.

    are you going to use R404A?

    chemi

  6. #6
    shogun7's Avatar
    shogun7 Guest

    Re: Copeland Glacier Scroll

    Aiyub
    see if you can log on to this!
    http://www.copeland-corp.com/americas/en_scroll/9.htm
    Roger

  7. #7
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,119
    Rep Power
    26

    Re: Copeland Glacier Scroll

    Shogun

    The link was good....Thank you..

Similar Threads

  1. use of digital scroll technology
    By katyalrk in forum Technical Discussions
    Replies: 6
    Last Post: 11-11-2008, 03:12 PM
  2. Dual Scroll Compressor
    By ernestlin in forum Technical Discussions
    Replies: 7
    Last Post: 27-06-2006, 04:14 AM
  3. Hermetic reciprocating versus hermetic scroll
    By Cofreth in forum Technical Discussions
    Replies: 26
    Last Post: 19-11-2005, 07:29 PM
  4. Scroll Compressor
    By dwallan in forum Commercial
    Replies: 1
    Last Post: 30-07-2001, 04:18 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •