Results 1 to 9 of 9
Thread: humidity test
    Dec 2008
    Bucharest
    44
    humidity test
    Hy guys, can enyone help me please?I try to find humidity refrigerant test .I dont find in shop.Is enyone to know .Thanks .
    Mar 2007
    Warwickshire UK
    723
    21
    Re: humidity test
    Carrier Total Test Kit might be what you are looking for
    goggle = total test kit
    or
    www.totaline.com
    Connect to system to get approximate moisture & acid contamination indication.
    Dec 2008
    Bucharest
    44
    Re: humidity test
    Thanks for adress.But I need humidity test for r 134 and this test is not for R 134.Thanks allot.
    Nov 2008
    United Kingdom
    33
    Re: humidity test
    Thermatech is right. Test kit works on Carriers 134a. U should test not refrigerant, but compressor oil, because water is heavier than refrigerant.
    11,025
    Re: humidity test
    Quote Originally Posted by Mozambezi View Post
    Interesting theory, with water at 1000 kg/cu.m and,say R12, at 1310 kg/cu.m it could be the other way round.
    Nov 2008
    United Kingdom
    33
    Re: humidity test
    Did u say R12 in UK ?
    Dec 2008
    Bucharest
    44
    Re: humidity test
    I changed oil and it s separete to all instalation part .I have 500 kg r 134 and Im not shore if it s ok
    Jul 2006
    Romania
    44
    99
    Re: humidity test
    Hi Claudiu
    The first thing to do when the water content is
    high in the oil is to replace the drierfilter and run
    the chiller for a minimum 100 running hours and
    then take an oil sample again. If the water content
    has decreased but is still above 200 ppm,
    the drier needs to be changed again and another
    oil sample taken.
    I don't know where to find a lab for oil analysis in your area but i guess that is the best way ....
    Keep in touch
    Mihai
    Aug 2009
    Malaysia
    29
    Re: humidity test
    Anybody know which brand is good in humiditistats?
  1. Daikin VRV II Test Mode Failure
    By KISS KISS BANG in forum Air Conditioning
    Last Post: 30-05-2010, 08:54 PM
  2. High humidity comfort cooling
    By Thermatech in forum Air Conditioning
    Last Post: 27-11-2008, 01:01 AM
  3. Test
    By bigblock468 in forum New to RE
    Last Post: 04-06-2008, 11:16 PM
  4. Building a wine cabinet
  5. `skills / trade test???????
    By pagey in forum Chit Chat & Service Stories
    Last Post: 24-03-2004, 03:31 PM