Thread: humidity test

  1. #1
    Join Date
    Dec 2008
    Location
    Bucharest
    Age
    44
    Posts
    50
    Rep Power
    16

    humidity test



    Hy guys, can enyone help me please?I try to find humidity refrigerant test .I dont find in shop.Is enyone to know .Thanks .



  2. #2
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: humidity test

    Carrier Total Test Kit might be what you are looking for

    goggle = total test kit

    or

    www.totaline.com

    Connect to system to get approximate moisture & acid contamination indication.

  3. #3
    Join Date
    Dec 2008
    Location
    Bucharest
    Age
    44
    Posts
    50
    Rep Power
    16

    Re: humidity test

    Thanks for adress.But I need humidity test for r 134 and this test is not for R 134.Thanks allot.

  4. #4
    Join Date
    Nov 2008
    Location
    United Kingdom
    Age
    46
    Posts
    33
    Rep Power
    0

    Re: humidity test

    Thermatech is right. Test kit works on Carriers 134a. U should test not refrigerant, but compressor oil, because water is heavier than refrigerant.

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: humidity test

    Quote Originally Posted by Mozambezi View Post
    Thermatech is right. Test kit works on Carriers 134a. U should test not refrigerant, but compressor oil, because water is heavier than refrigerant.
    Interesting theory, with water at 1000 kg/cu.m and,say R12, at 1310 kg/cu.m it could be the other way round.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Nov 2008
    Location
    United Kingdom
    Age
    46
    Posts
    33
    Rep Power
    0

    Re: humidity test

    Quote Originally Posted by Brian_UK View Post
    Interesting theory, with water at 1000 kg/cu.m and,say R12, at 1310 kg/cu.m it could be the other way round.
    Did u say R12 in UK ?

  7. #7
    Join Date
    Dec 2008
    Location
    Bucharest
    Age
    44
    Posts
    50
    Rep Power
    16

    Re: humidity test

    I changed oil and it s separete to all instalation part .I have 500 kg r 134 and Im not shore if it s ok

  8. #8
    Join Date
    Jul 2006
    Location
    Romania
    Age
    43
    Posts
    99
    Rep Power
    18

    Re: humidity test

    Hi Claudiu
    The first thing to do when the water content is
    high in the oil is to replace the drierfilter and run
    the chiller for a minimum 100 running hours and
    then take an oil sample again. If the water content
    has decreased but is still above 200 ppm,
    the drier needs to be changed again and another
    oil sample taken.
    I don't know where to find a lab for oil analysis in your area but i guess that is the best way ....
    Keep in touch
    Mihai

  9. #9
    Join Date
    Aug 2009
    Location
    Malaysia
    Posts
    29
    Rep Power
    0

    Re: humidity test

    Anybody know which brand is good in humiditistats?

Similar Threads

  1. Daikin VRV II Test Mode Failure
    By KISS KISS BANG in forum Air Conditioning
    Replies: 8
    Last Post: 30-05-2010, 08:54 PM
  2. High humidity comfort cooling
    By Thermatech in forum Air Conditioning
    Replies: 70
    Last Post: 27-11-2008, 01:01 AM
  3. Test
    By bigblock468 in forum New to RE
    Replies: 3
    Last Post: 04-06-2008, 11:16 PM
  4. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM
  5. `skills / trade test???????
    By pagey in forum Chit Chat & Service Stories
    Replies: 26
    Last Post: 24-03-2004, 03:31 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •