    Chiller coldroom compressor problems.

    I've got a problem with a small integral chiller c/r compressor. The compressor is an Aspera NE 7213E (R22). The c/r is approx 7ft square (Trimco me thinks). The problem is the compressor is overheating and cutting out on o/load. Condensor clean and condensor motor running ok.

    When running the compressor body is very hot.

    Its got me confused because once compressor cools and then runs it brings c/r temp down, cycles on stat cutting in and out quite happily, yet a few days later cuts out on o/load again?

    Comp valve or overcharged maybe?

    I think I'm going to remove gas, check comp and if that is ok, flush system, replace drier, vac out and re-gas to see if that works.

    There is no ID label so I'm not sure quantity of R22 to put in. I don't want to overcharge/ undecharge system. The system uses capillary tube. Any suggestions on back pressure I should be looking at and how critical is the charge in a capillary system? At moment unit running around 40psi.
    Thanks
    Lucas.
    Last edited by Lucas; 29-03-2004 at 05:59 PM. Reason: change

Similar Threads

  1. Dunham Bush Chiller Alarm
    By Regulator in forum Air Conditioning
    Replies: 11
    Last Post: 08-12-2010, 01:42 AM
  2. DIY aquarium chiller
    By BarraCuda in forum Technical Discussions
    Replies: 18
    Last Post: 06-10-2010, 11:02 PM
  3. York Screw Chiller How low will it go?????
    By bruceboldy in forum Industrial Compressors
    Replies: 11
    Last Post: 10-08-2007, 10:29 PM
  4. Chiller fault
    By iceman007 in forum Trouble Shooting
    Replies: 9
    Last Post: 27-06-2006, 06:15 AM
  5. Chiller
    By iceman007 in forum Trouble Shooting
    Replies: 9
    Last Post: 08-04-2006, 02:48 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •