    Re: leak testing



    Quote Originally Posted by Mozambezi View Post
    Well...

    Following Mitsu or Daikin Intallation manuals we need to keep pressure for 24h on comissioning...
    in 2-3h some engineers could find that pressure drops or raises and depends up to air/ sun temperature.
    True leak test is VAC test... Left pomp through the night and in the morning take VAC for 2-3h... if holds 4-6 Torr, then OK... If more.... use sealant, if more then 10, then put CO2 + Refrigerant or OFN + HE... or if system compicated, use distilated water...

    P.S.: DIN standard is in base of EN and is more demanding. Belive me /have Tuv nord certificate for pressure test./
    I intrigued to know how a pressure test of 1 bar can prove that a system is leak free.

    Also what sealant do you use ?


    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  2. #52
    Join Date
    Feb 2007
    Location
    France now, Suffolk before
    Age
    55
    Posts
    294
    Rep Power
    18

    Re: leak testing

    Also what sealant do you use ?
    He uses distilled water of course

  3. #53
    Join Date
    Jan 2009
    Location
    Queensland
    Age
    64
    Posts
    113
    Rep Power
    16

    Re: leak testing

    Quote Originally Posted by Mozambezi View Post
    Well...

    Following Mitsu or Daikin Intallation manuals we need to keep pressure for 24h on comissioning...
    in 2-3h some engineers could find that pressure drops or raises and depends up to air/ sun temperature.
    Read, some engeneers couldn't solder well enough to hold a pressure test for 2 -3 hours.
    Quote Originally Posted by Mozambezi View Post
    True leak test is VAC test... Left pomp through the night and in the morning take VAC for 2-3h... if holds 4-6 Torr, then OK...
    If only hold 4 to 6 Torr for 2 to 3 hours, pressurize the system with nitro and find then fix the leaks.
    If the system is dry and sealed it should hold 0.5 Torr (500 micron) for 24 hours.

    Quote Originally Posted by Mozambezi View Post
    If more.... use sealant, if more then 10, then put CO2 + Refrigerant or OFN + HE... or if system compicated, use distilated water...

    P.S.: DIN standard is in base of EN and is more demanding. Belive me /have Tuv nord certificate for pressure test./
    Distalated water? Sealant? Hu?
    Solder your pipes in properly.
    inspect the welds with a mirror and torch, then pressure test with nitro. If the system holds the pressure test, vac it to 500 micron and if you have to do a vacuum test. If you've been putting "distalated water" in the system, don't expect it to pass a vacuum test.

    Quote Originally Posted by Mozambezi View Post
    P.P.S.: For companies with long service contract /5 or more years/ would recommend to keep equipment gas register and monitore leaks...
    I would say loss 10% of charge in a year is bottom line... 2% is optimistic for new Daikin VRV systems...
    How is any gas loss in a newly installed and commissioned system acceptable?
    If your people are competent and the system has been pressure tested and vacced properly there should be no leaks in the first 12 months of operation.
    I can only assume that something has been lost in the translation.

    or have I missed something here?

  4. #54
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: leak testing

    I think both methods are good methods (vacuum test and pressure testing).

    With pressure test you have high pressure difference at sides of leak (leak rate is high) and low accuracy (resolution) manometers to test leak and also influence of temperature change on test gas pressure.

    On the other end, you have small pressure difference (1 bar) between sides of leak (leak rate is small but still present), but very precise and sensitive instrument to detect that small leak rate, and very, very, very small influence at reading of temperature change of gas remained in vacuumed pipes.

    To me it looks like both methods are equally good with one key difference. If some welds are mechanically weak, pressure test will make them to open and leak but vacuum test will never disclose them.

    That is why I will always make first pressure test and then vacuum test on systems where welds are involved.
    On split systems with pipes in one piece, only vacuum test is sufficient.

    That is my 2 cents.

    Also, keep in mind this:
    http://www.refrig.com/bigblumanual3....RTHING%20LEAKS
    Last edited by nike123; 14-02-2009 at 06:41 AM.

  5. #55
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: leak testing

    Quote Originally Posted by nike123 View Post
    To me it looks like both methods are equally good with one key difference. If some welds are mechanically weak, pressure test will make them to open and leak but vacuum test will never disclose them.

    That is why I will always make first pressure test and then vacuum test on systems where welds are involved.
    On split systems with pipes in one piece, only vacuum test is sufficient.
    According EN378-2008, all systems must pass a strength test at a predetermined pressure and a leak test. Both are serving a different purpose. It's not leak testing or pressure testing, it's and ..and
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  6. #56
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: leak testing

    Quote Originally Posted by Peter_1 View Post
    According EN378-2008, all systems must pass a strength test at a predetermined pressure and a leak test. Both are serving a different purpose. It's not leak testing or pressure testing, it's and ..and
    Peter, my country is not in EU (and probably will not be) and we are not obliged here to follow that norms. Our norms are still harmonizing with EU regulation.

    I wrote that from perspective of common sense and not from perspective of norms and regulations.

    That is my 2 cents.
    Also, in mini split systems with pipes from one piece, Indoor and outdoor unit is already tested and comes with certificate and pipes are tested and comes with certificate so there is nothing to strength test.
    Last edited by nike123; 14-02-2009 at 08:55 AM.

  7. #57
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: leak testing

    Quote Originally Posted by nike123 View Post
    Peter, my country is not in EU (and probably will not be) and we are not obliged here to follow that norms. Our norms are still harmonizing with EU regulation.

    I wrote that from perspective of common sense and not from perspective of norms and regulations.
    Ok, you're right

    Also, in mini split systems with pipes from one piece, Indoor and outdoor unit is already tested and comes with certificate and pipes are tested and comes with certificate so there is nothing to strength test.
    OK, but only valid outside the EU.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  8. #58
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: leak testing

    Quote Originally Posted by nike123 View Post
    Peter, my country is not in EU (and probably will not be) ..
    Croatia is negotiating to join the EU, isn't it?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  9. #59
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: leak testing

    Quote Originally Posted by Peter_1 View Post
    Croatia is negotiating to join the EU, isn't it?
    Yes, but for now, that is at hold! And date of joining are continually postponing from mostly political reasons (and EU should stand for European economic union) and our goverment incompetence. At least, that is how I see it.
    Last edited by nike123; 14-02-2009 at 09:17 AM.

  10. #60
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: leak testing



    it actually worries me about some of the work that is being carried out in different countries, i can see why a lot of countries have not changed to 410A either as i don't think the techs would be able to carry out the work.

    If you are a fully qualified refrigeration engineer and have not been bred into it, the work to be carried out on installations should be of some similar quality, sealants and Co2 being used, hmm, if a strength test and leak test is not being carried out properly, i would hate to see what is going to happen when a VRV Co2 system is installed....hmmmm... i am scared and can see why there are so many leaks and problems out there and need for regulations!!!

  11. #61
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: leak testing

    A CO2 VRV, what's that?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  12. #62
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: leak testing

    it is a Variable Refrigerant Volume, multi system running on CO2 gas.

  13. #63
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: leak testing

    What brands are already selling a CO2 VRV in the EU?
    None I suppose.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  14. #64
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: leak testing

    I dont know is any in Europe.
    Daikin: The global supplier is presenting a world premiere, as its latest VRV (Variable Refrigerant Volume) model is now using the natural refrigerant CO2. It is optimised for heating function. The outside unit features a heating capacity of 31.5 kW for heating, and 28 kW for cooling. Daikin has applied a new refrigeration cycle technology with a swing compressor and a newly developed heat exchanger. The CO2 model is compatible with all VRV control and management systems.
    http://www.r744.com/articles/2008-10...2-(part-3).php

  15. #65
    john tucker's Avatar
    john tucker Guest

    Re: leak testing

    you should only use OFN for this pressure testing

  16. #66
    Join Date
    Jan 2009
    Location
    Queensland
    Age
    64
    Posts
    113
    Rep Power
    16

    Re: leak testing

    Quote Originally Posted by john tucker View Post
    you should only use OFN for this pressure testing
    OK John. I'll bite. What's OFN?

  17. #67
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: leak testing

    Quote Originally Posted by Slatts View Post
    OK John. I'll bite. What's OFN?
    Oxygen Free Nitrogen

  18. #68
    Join Date
    Jan 2009
    Location
    Queensland
    Age
    64
    Posts
    113
    Rep Power
    16

    Re: leak testing

    Quote Originally Posted by nike123 View Post
    Oxygen Free Nitrogen
    Thanks nike.
    Over here in my neck of the woods, we still use industrial dry nitro.

Page 2 of 2 FirstFirst 12

Similar Threads

  1. Leak Testing?
    By Thana in forum Trouble Shooting
    Replies: 36
    Last Post: 31-08-2010, 02:57 PM
  2. Leak Testing Daikin K Series VRV
    By jedi in forum Trouble Shooting
    Replies: 8
    Last Post: 21-08-2008, 07:16 PM
  3. Leak Testing
    By Samarjit Sen in forum Technical Speculations
    Replies: 26
    Last Post: 25-03-2008, 08:30 PM
  4. Trace Leak Testing?
    By Jus1 in forum Trouble Shooting
    Replies: 3
    Last Post: 24-03-2008, 05:06 PM
  5. leak testing with OFN
    By davej in forum Refrigerants
    Replies: 17
    Last Post: 02-11-2006, 09:12 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •