Thread: leak testing

  1. #1
    Join Date
    Jan 2009
    Location
    england
    Posts
    15
    Rep Power
    0

    leak testing



    I have been informed that you should not pressure test a refrigeration system system using a nitrogen bottle even if has a requlator via a manifold set which has a sight glass, anticipated nitrogen pressure 6 - 20bar.



  2. #2
    Join Date
    Dec 2008
    Location
    USA
    Age
    41
    Posts
    58
    Rep Power
    16

    Re: leak testing

    I've heard to use Helium becuase the molecules are smaller which will make the Leak easier to be detected. Never heard that nitrogen was bad. Only that you should not pressure test over 350psi

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: leak testing

    Quote Originally Posted by pentond1 View Post
    I have been informed that you should not pressure test a refrigeration system system using a nitrogen bottle even if has a requlator via a manifold set which has a sight glass, anticipated nitrogen pressure 6 - 20bar.

    It is correct!
    Nitrogen is right gas for that purpose. To use manifold set with which has sight glass is also normal practice, if you are not exceeding pressure rating of that manifold set and if you are using pressure reducing valve, adjusted to max allowable pressure of that part of circuit you are testing and not exceeding pressure rating of weakest part in setup. That part could be easily your manifold gauges with sight-glass. Use safety goggles.
    Last edited by nike123; 12-01-2009 at 07:05 PM.

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: leak testing

    Quote Originally Posted by jcook1982 View Post
    I've heard to use Helium becuase the molecules are smaller which will make the Leak easier to be detected. Never heard that nitrogen was bad. Only that you should not pressure test over 350psi
    Max pressure depends on maximum allowable pressure of weakest part under testing.
    If you have heat pump on R410 you have higher working pressures than 350PSI.

  5. #5
    Join Date
    Nov 2008
    Location
    United Kingdom
    Age
    46
    Posts
    33
    Rep Power
    0

    Re: leak testing

    I would have look on system info, usually on back panel. It says maximum pressures. For R410a do 30 bar, R134a do 20, other 25. If here is pitch hole I do higher pressure... up to 5 bar more.
    If pressure test negative, I would recommend to have chat with customer and put UV and Sealant into system... usually helps.

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: leak testing

    Quote Originally Posted by Mozambezi View Post
    I would have look on system info, usually on back panel. It says maximum pressures. For R410a do 30 bar, R134a do 20, other 25. If here is pitch hole I do higher pressure... up to 5 bar more.
    If pressure test negative, I would recommend to have chat with customer and put UV and Sealant into system... usually helps.
    NO, if pressure test negative then fix the leak properly.

    Adding any form of sealant is likely to cause problems unless you know something better than usual products.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: leak testing

    there is a new pressure testing regulator that you can get that should be used now, no sight glass should be used with high pressure nitrogen anymore.
    The new manifold has a braided hose and it is heavy duty to withstand higher pressures without explosion on failure..
    this device weighs about 8kgs and is new common practise.

  8. #8
    Join Date
    Oct 2004
    Location
    uk
    Age
    56
    Posts
    194
    Rep Power
    20

    Re: leak testing

    come on guys, the question was about using a manifold with a sight glass to pressure test. it has always been recommended that you do not ever use a sight glass equipped manifold for pressure testing due to the unknown condition of the glass. it would be bad enough if the glass broke under normal system pressure, but if you get into the habit of using your normal manifold set to pressure test even the low side of the system then one day you will forget and "quickly" pressure test the high side. the same goes for using a faulty nitrogen regulator or gauges. we all know someone who has done it. but we probably also know someone who had a near miss as well.
    it may seem a bit nannyish but don't do it and don't advise anybody that it is ok to do it for a short time.

  9. #9
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: leak testing

    Well said Bill1983, succinct and to the point. Thanks.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  10. #10
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: leak testing

    Quote Originally Posted by brunstar View Post
    there is a new pressure testing regulator that you can get that should be used now, no sight glass should be used with high pressure nitrogen anymore.
    The new manifold has a braided hose and it is heavy duty to withstand higher pressures without explosion on failure..
    this device weighs about 8kgs and is new common practise.
    I don't see why you should not use gauge manifolds with sight glass with which you measuring your system pressures, for pressure test, who is same or slightly elevated as operating refrigerant pressure, if they are rated for higher pressure than test pressure.
    Of corse that I mean that pressure regulator should be used at nitrogen botle to reduce pressure from botle to test pressure.

  11. #11
    Join Date
    Oct 2004
    Location
    uk
    Age
    56
    Posts
    194
    Rep Power
    20

    Re: leak testing

    the problem isn't the pressure you intend to test at, its the pressure you might release into the manifold. most of us i would hope are skilled enough to be able to do this safely, but because of the potential risk shouldn't do it anyway.

  12. #12
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: leak testing

    We've had this discussion before.

    Personally, I consider the manifold set to be safe upto the maximum pressure shown on the dial, otherwise, the manufacturer would not release the product into the main market place, considering their responsibility if something went wrong.

    In this day and age of litigation driven thinking, every responsible manufacturer would build some safety factor into their product, even considering such things as wear and tear on the sight glass.

    I've yet to see some scientific evidence about sight glass failure to convince me otherwise.

    Scaremongering, that's what I say ............

  13. #13
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: leak testing

    Quote Originally Posted by bill1983 View Post
    the problem isn't the pressure you intend to test at, its the pressure you might release into the manifold. most of us i would hope are skilled enough to be able to do this safely, but because of the potential risk shouldn't do it anyway.
    Sorry at my hair splitting, but I don't see how you could release higher pressure in to manifold if you have reduced pressure at test pressure value before manifolds at pressure reducing valve.

  14. #14
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: leak testing

    Quote Originally Posted by frank View Post
    We've had this discussion before.

    Personally, I consider the manifold set to be safe upto the maximum pressure shown on the dial, otherwise, the manufacturer would not release the product into the main market place, considering their responsibility if something went wrong.

    In this day and age of litigation driven thinking, every responsible manufacturer would build some safety factor into their product, even considering such things as wear and tear on the sight glass.

    I've yet to see some scientific evidence about sight glass failure to convince me otherwise.

    Scaremongering, that's what I say ............
    Good said Frank. You have one Paulaner Hefe-Weizen from me.

  15. #15
    Join Date
    Oct 2004
    Location
    uk
    Age
    56
    Posts
    194
    Rep Power
    20

    Re: leak testing

    i agree with you both, but it doesn't change the fact that the manifold is not built to be safe at the maximum pressure that the nitrogen cylinder can supply, nor are the gauge lines. like i said we are probably safe enough to do it, but do you want to be there when it goes wrong? yes the problem is litigation, the rules are now made for the less intelligent but they do apply to all. the choice is yours.

  16. #16
    Join Date
    Oct 2004
    Location
    uk
    Age
    56
    Posts
    194
    Rep Power
    20

    Re: leak testing

    as regards the hair splitting nike, dont worry about it, its what the forum is for. it doen't matter what you have set the regulator for, it matters that it COULD release more pressure than the manifold,lines, sight glass can take.

  17. #17
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: leak testing

    Quote Originally Posted by bill1983 View Post
    i agree with you both, but it doesn't change the fact that the manifold is not built to be safe at the maximum pressure that the nitrogen cylinder can supply, nor are the gauge lines. like i said we are probably safe enough to do it, but do you want to be there when it goes wrong? yes the problem is litigation, the rules are now made for the less intelligent but they do apply to all. the choice is yours.
    I think that you are not reading carefully what I wrote my friend:

    how you could release higher pressure in to manifold if you have reduced pressure at test pressure value before manifolds at pressure reducing valve
    I dont see how! Could you elaborate?

  18. #18
    Join Date
    Oct 2004
    Location
    uk
    Age
    56
    Posts
    194
    Rep Power
    20

    Re: leak testing

    if i'm reading you right nike, then you are saying that if you set the nitrogen regulator to a safe pressure for example 100psig then you will not then release any more pressure into the manifold than that. therefore the operation is safe. is that correct?

  19. #19
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: leak testing

    Quote Originally Posted by bill1983 View Post
    if i'm reading you right nike, then you are saying that if you set the nitrogen regulator to a safe pressure for example 100psig then you will not then release any more pressure into the manifold than that. therefore the operation is safe. is that correct?
    Yep, that is correct!

    When I set pressure reducing valve, I first put cap at valve outlet and then adjust pressure to test pressure value, and after that, I remove cap and connect gauge manifold! So there is no way that pressure higher than set on pressure reducing valve could reach gauge manifold.

  20. #20
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    985
    Rep Power
    19

    Re: leak testing

    Paul


    "KEEP IT COOL"

  21. #21
    Join Date
    Oct 2004
    Location
    uk
    Age
    56
    Posts
    194
    Rep Power
    20

    Re: leak testing

    ok. in an extreme scenario which is what the rules are now made for regardless of how little sense they make to you, let us say that you have to leave the nitrogen bottle unattended. you shut down the bottle before you leave the plant. you then go to the other end of the system you are leak testing and begin to look for leaks. you are leak testing for maybe 15 minutes max, during which time you judge that it is safe to leave the nitrogen unattended because you have chained it to a pillar to prevent it from falling over. while you are away, somebody sees the nitrogen and being curious decides to have a closer look. he wonders what will happen if he turns the regulator knob. nothing happens of course because you sensibly isolated the cylinder valve just in case the regulator catestrophically fails. however this curious person just happens to be carrying a multitool and can open the cylinder valve. he does this and winds the regulator fully open. now if the manifold valves are open, he will burst the lines first and receive lacerations to the face and torso from the whipping action ofthe burst lines. however if the valves are not open where is the weak point of the manifold. oops remeber when you dropped it while you were putting it away. it didn't seem to damage it, but what if it caused the sight glass to crack . not enough so you could see it, but just enough to set up a weakness. with 35 bar behind it, and an idiot in front of it you can see what could happen. this is the person for whom health and safety rules were written. this is a unliokely scenario i know BUT the rules are written for just such an event. sad but very true. i can only presume that this is not yet the case in sunny Split?

  22. #22
    Join Date
    Oct 2004
    Location
    uk
    Age
    56
    Posts
    194
    Rep Power
    20

    Re: leak testing

    thanks swill? item 12 on the procedure list will make the test safer but only muppet proof if you take the line with you or lock it away.

  23. #23
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: leak testing

    I follow the arguments, but, if you ensure that the bottle regulator maximum pressure will not exceed the maximum pressure of the gauge set you are using (common sense I know), then the possibility of an unforeseen accident should be eliminated.

  24. #24
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: leak testing

    Quote Originally Posted by bill1983 View Post
    ok. in an extreme scenario which is what the rules are now made for regardless of how little sense they make to you, let us say that you have to leave the nitrogen bottle unattended. you shut down the bottle before you leave the plant. you then go to the other end of the system you are leak testing and begin to look for leaks. you are leak testing for maybe 15 minutes max, during which time you judge that it is safe to leave the nitrogen unattended because you have chained it to a pillar to prevent it from falling over. while you are away, somebody sees the nitrogen and being curious decides to have a closer look. he wonders what will happen if he turns the regulator knob. nothing happens of course because you sensibly isolated the cylinder valve just in case the regulator catestrophically fails. however this curious person just happens to be carrying a multitool and can open the cylinder valve. he does this and winds the regulator fully open. now if the manifold valves are open, he will burst the lines first and receive lacerations to the face and torso from the whipping action ofthe burst lines. however if the valves are not open where is the weak point of the manifold. oops remeber when you dropped it while you were putting it away. it didn't seem to damage it, but what if it caused the sight glass to crack . not enough so you could see it, but just enough to set up a weakness. with 35 bar behind it, and an idiot in front of it you can see what could happen. this is the person for whom health and safety rules were written. this is a unliokely scenario i know BUT the rules are written for just such an event. sad but very true. i can only presume that this is not yet the case in sunny Split?
    That scenario is like you say that someone in office could kill himself with pencil?
    And legislation is not holy cow that we "believers" should not reexamine some of rules put by some clerk who actually newer has been at field and now write rules for field peoples.
    Have you ever been in shipyard? If everyone included in shipbuilding strictly follows the rules about safety etc.. ship would never see the day of baptizing.

    Don't you thing that is also same chance to blow out for damaged pressure gauge as it is for sight glass, and that exploded pressure gauge could make same damage as sight-glass blowing.
    It is our common sense and education what keeps us safe, not some legislation.
    Last edited by nike123; 12-01-2009 at 11:23 PM.

  25. #25
    Join Date
    Jan 2009
    Location
    england
    Posts
    15
    Rep Power
    0

    Re: leak testing

    Thank you for your replies - if the manifold gauge set with sight glass should not be used what is the procedure when pressure testing with nitrogen with fitted sightglass on the compressor/refrigeration systems (407c/R22).

  26. #26
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: leak testing

    Quote Originally Posted by pentond1 View Post
    Thank you for your replies - if the manifold gauge set with sight glass should not be used what is the procedure when pressure testing with nitrogen with fitted sightglass on the compressor/refrigeration systems (407c/R22).
    Good point!
    Answer is probably " sight glass on compressor is not that much endangered as your gauge manifold set".

  27. #27
    Join Date
    Jan 2008
    Location
    Norfolk - England
    Posts
    95
    Rep Power
    17

    Re: leak testing

    That scenario is like you say that someone in office could kill himself with pencil?

    Thats pretty much the best one i've heard for a long while!!

    I agree.

    My line manager would probably do that as well!!

    The key to this is the right man for the right job!!

    & that man needs training & buckets of experience!!!

    & that man could be a female!!!!

  28. #28
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: leak testing

    Quote Originally Posted by Billy Ray View Post
    & that man needs training & buckets of experience!!!

    & that man could be a female!!!!
    I would be pleased to work with that female man!
    But females somehow don't like to carry around bottles of acetylene around and be in blast freezer rooms at -40°C more than 2 seconds.
    Could be that they are smarter than mans.

  29. #29
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: leak testing

    Quote Originally Posted by pentond1 View Post
    Thank you for your replies - if the manifold gauge set with sight glass should not be used what is the procedure when pressure testing with nitrogen with fitted sightglass on the compressor/refrigeration systems (407c/R22).
    Test pressure could be lower on those two gases compared with R410a so maybe not such a problem.

    Unless of course your worst case scenario takes over again
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  30. #30
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: leak testing

    Quote Originally Posted by frank View Post
    I follow the arguments, but, if you ensure that the bottle regulator maximum pressure will not exceed the maximum pressure of the gauge set you are using (common sense I know), then the possibility of an unforeseen accident should be eliminated.
    I have had the sight glass blow out on a set of gauges where the reg could not exceed the max working pressure of the gauges.

    Admittedly it was my own fault.

    Had the gauges hooked up and closed, connected reg and opened valve on bottle. Last person that used reg had left it fully open, momentary inrush of pressure through reg was enough to break glass and send it into my lip.

    I always check the reg first and make sure it is closed now.

  31. #31
    Join Date
    Oct 2004
    Location
    uk
    Age
    56
    Posts
    194
    Rep Power
    20

    Re: leak testing

    QED unfortunately

  32. #32
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: leak testing

    Quote Originally Posted by Temprite View Post
    I have had the sight glass blow out on a set of gauges where the reg could not exceed the max working pressure of the gauges.

    Admittedly it was my own fault.

    Had the gauges hooked up and closed, connected reg and opened valve on bottle. Last person that used reg had left it fully open, momentary inrush of pressure through reg was enough to break glass and send it into my lip.

    I always check the reg first and make sure it is closed now.
    You can't buy experience.

  33. #33
    Join Date
    Sep 2008
    Location
    england
    Posts
    429
    Rep Power
    20

    Re: leak testing

    Quote Originally Posted by nike123 View Post
    I would be pleased to work with that female man!
    But females somehow don't like to carry around bottles of acetylene around and be in blast freezer rooms at -40°C more than 2 seconds.
    Could be that they are smarter than mans.

    "I would be pleased to work with that female man! "
    ....anything you need to tell us nike? we`re all here for you now, just where did I put my wig.

    Glenn

  34. #34
    Join Date
    Nov 2008
    Location
    United Kingdom
    Age
    46
    Posts
    33
    Rep Power
    0

    Question Re: leak testing

    Quote Originally Posted by Brian_UK View Post
    NO, if pressure test negative then fix the leak properly.

    Adding any form of sealant is likely to cause problems unless you know something better than usual products.
    Brian U're 100 percent right. Here are no good sealants in HRP.

    Let's imagine A/C VRV with kg R-410a.
    U're contractor, got quota for recharging the system /short of gas/...
    After 2h on 43bar no leaks found and you checked all joints, or most of them... u doing VAC and in another 2h pressure comes up from 4 Torr to 6... Test kit is OK.
    Well. Technically OFN test positive, but ...
    What u would recommend me to do when I've got max 20h to complete a job? /please be constructive/


  35. #35
    Join Date
    Jan 2009
    Location
    Queensland
    Age
    64
    Posts
    113
    Rep Power
    16

    Re: leak testing

    Rules are for the guidance of the wise and the protection of fools.
    When I started in the trade in the late 70's we'd put a 5/8" MF to 1/4"MF reducer in the nitro bottle and hook it up to the system to be tested or purged with a 1/4" copper line.
    We'd crack the bottle valve carefully (if you can use that word in that context).
    Now I'm older and I hope wiser, I won't go near a nitro bottle without a proper nitro reg. I always close the reg and open my manifold valves before opening the bottle.
    I've never owned a set of gauges with a sight glass and don't really see the need.

  36. #36
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: leak testing

    Quote Originally Posted by glenn1340 View Post
    "I would be pleased to work with that female man! "
    ....anything you need to tell us nike? we`re all here for you now, just where did I put my wig.

    Glenn
    You know what part of female man I was thinking!

  37. #37
    Join Date
    Oct 2007
    Location
    Britain
    Posts
    223
    Rep Power
    17

    Re: leak testing

    Its reassuring to see the promotion of sexual equality in our industry.
    Good Work!!
    Regarding the pressure testing I agree with Nike and Frank.

  38. #38
    rachid269's Avatar
    rachid269 Guest

    Re: leak testing

    hi guys.

    i've taught that the strengh test has to be 30% more of the normal pressure that soport the wakeast device on the system.

    leak test > is 1 time of the normal pressure

    strengh test> is 1.3 of the weakeast device on the system.

    thank you guys,,,

  39. #39
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: leak testing

    I think most EU posters forget EN37-2008, pressure testing with an inert gas is compulsory..in fact since 2000.
    RAchid269, where you found 1.3?
    And 1.3 of what?
    I have 1.1 of ps (EN378-2008-2 - 6.3.3.)
    And even then, it all depends in what category your installation is falling.

    Mozambezi, if in the Eu, fact you only have 20 hours for the job doesn't matter. You have to comply with the EU- regulations, even if it takes 20 days.
    But I know, you and yuor clients will have limits but it's up to you to decide if you don't wanna follow the rules.

    Pentond, your compressor sump and the sightglass are on the Lp of the system, which can be pressurized at a lower pressure (En378-2008-2 - 6.2.1.1. - Table 2)
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  40. #40
    Join Date
    Feb 2007
    Location
    UK
    Age
    58
    Posts
    158
    Rep Power
    18

    Re: leak testing

    The company I work for does not allow any pressure testing with a charging manifold.
    All pressure testing MUST be carried out using a pressure relief valve.
    Hence we have steel pressure testing manifold with an assortment of 1/2" and 3/8" ports, to this a calibrated gauge and a vent valve is fitted - the rig is hydraulic tested at 200Bar. For normal testing a CVP valve is fitted into this manifold and set to start venting 2 bar above test pressure.
    For pressure testing CO2 systems (@77Bar +) the CVP is blanked off and a seperate pre-set relief valve fitted.
    All hoses used for pressure testing are 6 or 10mm braided SS or 6mm SS tube.
    Why take a chance with pressure testing?
    Nitrogen regulators can fail - normally due to the diaphram being reverse pressured when changing the nitrogen bottle without first valving the regulator off from the rest of the system and venting it, this CAN cause the regulator to pass, perhaps only by a small ammount, but enough to over pressure a system or charging manifold/hose. Always close the nitrogen bottle as soon as test pressure is reached.

    To the people who boast about using minimal equipment, I hope you are still here to boast of it when your equipment fails during a test. Why take the chance?
    The pressure test guidelines in BS-EN378 should be regarded as the MINIMUM standard required, not some inconvieniance that you should do everything to bypass. Too many people have already died pressure testing systems, don't add your name to the list.

    Regards
    Steve
    Last edited by Plank!; 20-01-2009 at 07:44 AM.

  41. #41
    Join Date
    Nov 2008
    Location
    United Kingdom
    Age
    46
    Posts
    33
    Rep Power
    0

    Re: leak testing

    Quote Originally Posted by Peter_1 View Post
    I think most EU posters forget EN37-2008, pressure testing with an inert gas is compulsory..in fact since 2000.
    RAchid269, where you found 1.3?
    And 1.3 of what?
    I have 1.1 of ps (EN378-2008-2 - 6.3.3.)
    And even then, it all depends in what category your installation is falling.

    Mozambezi, if in the Eu, fact you only have 20 hours for the job doesn't matter. You have to comply with the EU- regulations, even if it takes 20 days.
    But I know, you and yuor clients will have limits but it's up to you to decide if you don't wanna follow the rules.

    Pentond, your compressor sump and the sightglass are on the Lp of the system, which can be pressurized at a lower pressure (En378-2008-2 - 6.2.1.1. - Table 2)

    Pressure test use to be 1.3 PS in DIN /German standart/.

    U are saying .... as long as it takes... Here is a yesterdays example from real life.
    My company A quoted for 4h of OFN leak test. Company B quoted 3h for leak test. Job was compressor change. Company B won.

  42. #42
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: leak testing

    If you're in the UK, then you have to follow the UK rules and not DIN rules and even more specific the EN rules.

    EN378-2008 even states that national rules are no longer valid.
    So I doubt your statement about DIN rules and especially in the UK.

    If you have to change a compressor, I don't think 1 hour difference in pressure testing will not make a difference in winning the job. And if you do it it now 3 hours or 4 hours, it will not better strength or leak tested.

    Again, it's up to you to follow the rules or to neglect them.

    But saying this, in the new EN378-2008, we no longer find any(!! ) requirements about pressure testing and vacuum procedures. Those were detailed explained in the old EN378-2000.
    Someone noticed this already?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  43. #43
    jbiasutti's Avatar
    jbiasutti Guest

    Re: leak testing

    One of the problems with single stage pressure regulators is that the set pressure of the regulator depends on the pressure inside the nitrogen cylinder.

    As the pressure in the cylinder drops the outlet pressure of the regulator increases and the flow of gas from the regulator also increases.

    Thus it is possible to set the nitrogen pressure at a safe level and if there is a leak in the system that causes the bottle pressure to drop results in higher pressure.

    I have seen a system where a system was put on a nitrogen purge with a low flow of nitrogen. The system was left for some hours and then the outlet of the system closed. This resulted in much higher pressure in the system than anticipated.

  44. #44
    Join Date
    Jan 2009
    Location
    NZ
    Age
    48
    Posts
    35
    Rep Power
    0

    Re: leak testing

    I mostly install city multy systems in commercial buildings. On the 410a systems the test pressure is 600 psi and I use a high pressure gauge and flared copper connections. A gauge manifold with sight glass is not only a safety risk, but also tends to leak after a few tests.

  45. #45
    Join Date
    Jan 2009
    Location
    Queensland
    Age
    64
    Posts
    113
    Rep Power
    16

    Re: leak testing

    For serious pressure or vacuum testing, you can't go past copper and flares. Flexible gauge lines are just another possible point of failure.
    If you have an open compressor (pretty unlikely on R410a) and you have to pass a low vac test, I'd valve it off from the test. Shaft seals are meant for a positive pressure and often don't hold a high vacuum.

  46. #46
    Join Date
    Mar 2008
    Location
    England
    Age
    68
    Posts
    251
    Rep Power
    17

    Re: leak testing

    Quote Originally Posted by sumsor View Post
    I mostly install city multy systems in commercial buildings. On the 410a systems the test pressure is 600 psi and I use a high pressure gauge and flared copper connections. A gauge manifold with sight glass is not only a safety risk, but also tends to leak after a few tests.
    Is not a requirement when pressure testing (strength testing) to those high levels to evacuate the building? I seem to remember seeing something about this somewhere but can't remember at present.
    The point being that if a brazed joint failed at 600psi it could take someones head off.
    If in doubt read the instructions. If still in doubt follow them.

  47. #47
    Join Date
    Jan 2009
    Location
    UK
    Age
    58
    Posts
    161
    Rep Power
    16

    Re: leak testing

    Our insurers witness pressure tests and we have to evacuate the area where the system is installed and barrier it off and include signage to restrict access!

  48. #48
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: leak testing

    its like frank says, "you cant by experience" but whe pay dearly for it.

    Ice

  49. #49
    Join Date
    Nov 2008
    Location
    United Kingdom
    Age
    46
    Posts
    33
    Rep Power
    0

    Re: leak testing

    Well...

    Following Mitsu or Daikin Intallation manuals we need to keep pressure for 24h on comissioning...
    in 2-3h some engineers could find that pressure drops or raises and depends up to air/ sun temperature.
    True leak test is VAC test... Left pomp through the night and in the morning take VAC for 2-3h... if holds 4-6 Torr, then OK... If more.... use sealant, if more then 10, then put CO2 + Refrigerant or OFN + HE... or if system compicated, use distilated water...

    P.S.: DIN standard is in base of EN and is more demanding. Belive me /have Tuv nord certificate for pressure test./
    Last edited by Mozambezi; 13-02-2009 at 06:43 PM. Reason: Add

  50. #50
    Join Date
    Nov 2008
    Location
    United Kingdom
    Age
    46
    Posts
    33
    Rep Power
    0

    Re: leak testing

    P.P.S.: For companies with long service contract /5 or more years/ would recommend to keep equipment gas register and monitore leaks...
    I would say loss 10% of charge in a year is bottom line... 2% is optimistic for new Daikin VRV systems...

Page 1 of 2 12 LastLast

Similar Threads

  1. Leak Testing?
    By Thana in forum Trouble Shooting
    Replies: 36
    Last Post: 31-08-2010, 02:57 PM
  2. Leak Testing Daikin K Series VRV
    By jedi in forum Trouble Shooting
    Replies: 8
    Last Post: 21-08-2008, 07:16 PM
  3. Leak Testing
    By Samarjit Sen in forum Technical Speculations
    Replies: 26
    Last Post: 25-03-2008, 09:30 PM
  4. Trace Leak Testing?
    By Jus1 in forum Trouble Shooting
    Replies: 3
    Last Post: 24-03-2008, 06:06 PM
  5. leak testing with OFN
    By davej in forum Refrigerants
    Replies: 17
    Last Post: 02-11-2006, 10:12 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •