    Re: leak testing

    Quote Originally Posted by frank View Post
    I follow the arguments, but, if you ensure that the bottle regulator maximum pressure will not exceed the maximum pressure of the gauge set you are using (common sense I know), then the possibility of an unforeseen accident should be eliminated.
    I have had the sight glass blow out on a set of gauges where the reg could not exceed the max working pressure of the gauges.

    Admittedly it was my own fault.

    Had the gauges hooked up and closed, connected reg and opened valve on bottle. Last person that used reg had left it fully open, momentary inrush of pressure through reg was enough to break glass and send it into my lip.

    I always check the reg first and make sure it is closed now.

  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: leak testing

    Quote Originally Posted by Temprite View Post
    I have had the sight glass blow out on a set of gauges where the reg could not exceed the max working pressure of the gauges.

    Admittedly it was my own fault.

    Had the gauges hooked up and closed, connected reg and opened valve on bottle. Last person that used reg had left it fully open, momentary inrush of pressure through reg was enough to break glass and send it into my lip.

    I always check the reg first and make sure it is closed now.
    You can't buy experience.

Similar Threads

  1. Leak Testing?
    By Thana in forum Trouble Shooting
    Replies: 36
    Last Post: 31-08-2010, 02:57 PM
  2. Leak Testing Daikin K Series VRV
    By jedi in forum Trouble Shooting
    Replies: 8
    Last Post: 21-08-2008, 07:16 PM
  3. Leak Testing
    By Samarjit Sen in forum Technical Speculations
    Replies: 26
    Last Post: 25-03-2008, 08:30 PM
  4. Trace Leak Testing?
    By Jus1 in forum Trouble Shooting
    Replies: 3
    Last Post: 24-03-2008, 05:06 PM
  5. leak testing with OFN
    By davej in forum Refrigerants
    Replies: 17
    Last Post: 02-11-2006, 09:12 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •