    hand exspansion valve settings



    the company I work for has contracted with some "experts" to help fine tune our ammonia system for energy efficency. they have told my supervisor (who has no education or experience in refrigeration) that all our hand exspansion valves should be set at 1 1/2 turns open. I have valves set at 1 1/4 turns to 2 1/2 turns depending on the coil. the frost patterns are even and the temperatures in the rooms are consistant. anyone out there have any thoughts on this subject?
    Last edited by chilldis; 11-01-2009 at 10:50 PM. Reason: bad typing skills



  2. #2
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: hand exspansion valve settings

    Quote Originally Posted by chilldis View Post
    the company I work for has contracted with some "experts" to help fine tune our ammonia system for energy efficency. they have told my supervisor (who has no education or experience in refrigeration) that all our hand exspansion valves should be set at 1 1/2 turns open. I have valves set at 1 1/4 turns to 2 1/2 turns depending on the coil. the frost patterns are even and the temperatures in the rooms are consistant. anyone out there have any thoughts on this subject?
    Hi Chilldis

    I would think the settings would be different for every coil. 1 1/2 turns might be a starting point, but only that.

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  3. #3
    Join Date
    Sep 2008
    Location
    United States
    Age
    59
    Posts
    57
    Rep Power
    16

    Re: hand exspansion valve settings

    thanks Andy, that validates what I have been saying to my supervisor since this came up

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: hand exspansion valve settings

    Using 1-1/2 turns open is a good starting point to help commission the system. If anything, you could start with the valves slightly open more on the coils at the highest elevation or those furthest away from the pumps. The coils closest to the pumps might be less open, since the pressure will be higher when you are closer to the pumps.

    The frost pattern method is a good way to adjust these after the system has stabilized because it is difficult to adjust for zero superheat on the evaporators.

    When someone starts spouting off general adjustments for all things you might want to question them closer. It's easy to also sell energy saving projects by stating general statements, like get the suction pressure up and the discharge pressure down. Both are fairly easy to do, but might not work depending on the actual system operation also.
    If all else fails, ask for help.


  5. #5
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: hand exspansion valve settings

    There are so many energy efficiency "experts" around. They can claim anything as energy saving measure.
    I found simple way to adjust bottom feed overfed coils. Majority of these coils have BPRs(back pressure regulators) for defrosting. During cooling mode these BPRs show liquid pressure after expansion valves. Usually, this pressure should be 5-10psig higher than suction pressure. So expansion valves can be adjusted accordingly.

  6. #6
    Join Date
    Sep 2008
    Location
    United States
    Age
    59
    Posts
    57
    Rep Power
    16

    Re: hand exspansion valve settings

    thanks for the feedback, I really do appreciate it.

  7. #7
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: hand exspansion valve settings

    Clients pay mega bucks for these desk jockey experts. I had several clients come back with their suggestions, and reply by saying turn everything off and really save some money. Client then drops into the reality groove.
    magoo

  8. #8
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: hand exspansion valve settings

    That's very true magoo. A lot of these characters have not actually worked on a system or even designed one, but they insist on telling people how they should work.
    If all else fails, ask for help.


  9. #9
    Join Date
    Jan 2006
    Location
    Valrico, Florida
    Posts
    509
    Rep Power
    19

    Re: hand exspansion valve settings

    Like what most everyone has said, 1 1/2 turns is a good place to start, you will still have to visually check the unit to see how it is performing.

  10. #10
    Join Date
    Dec 2008
    Location
    USA
    Age
    64
    Posts
    6
    Rep Power
    0

    Re: hand exspansion valve settings

    You want to make sure the entire evaportator is frosted and 1-1/2 turns is a good starting point. To dial it in you should measure the air temp across the coil with a device that will measure tenths of a degree. Adjust the HEV in 1/4 - 1/2 turn increments (then wait 1/2 - 1 hour) to get the maximum air temp difference across the coil. Once you stop getting increases, back down to the last increase in temp and open 1/4 turn past that setting.
    As operating conditions change (summer vs winter) the expansion valve adjustment will also.

  11. #11
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: hand exspansion valve settings

    Quote Originally Posted by jromine View Post
    You want to make sure the entire evaportator is frosted and 1-1/2 turns is a good starting point. To dial it in you should measure the air temp across the coil with a device that will measure tenths of a degree. Adjust the HEV in 1/4 - 1/2 turn increments (then wait 1/2 - 1 hour) to get the maximum air temp difference across the coil. Once you stop getting increases, back down to the last increase in temp and open 1/4 turn past that setting.
    As operating conditions change (summer vs winter) the expansion valve adjustment will also.
    It is a good idea to check the date of the post before replying.
    Your good advise may be a little late.
    Cheers Grizzly

  12. #12
    Join Date
    Sep 2008
    Location
    United States
    Age
    59
    Posts
    57
    Rep Power
    16

    Re: hand exspansion valve settings

    advice, even a little late, is still a good thing. thanks for the feedback.

  13. #13
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: hand exspansion valve settings

    Quote Originally Posted by jromine View Post
    You want to make sure the entire evaportator is frosted and 1-1/2 turns is a good starting point. To dial it in you should measure the air temp across the coil with a device that will measure tenths of a degree. Adjust the HEV in 1/4 - 1/2 turn increments (then wait 1/2 - 1 hour) to get the maximum air temp difference across the coil. Once you stop getting increases, back down to the last increase in temp and open 1/4 turn past that setting.
    As operating conditions change (summer vs winter) the expansion valve adjustment will also.
    I don't think that it is practical. If you have 100 coils, it takes time to adjust them twice per year. What is the difference between summer and winter coil operation?

  14. #14
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: hand exspansion valve settings

    Quote Originally Posted by chilldis View Post
    advice, even a little late, is still a good thing. thanks for the feedback.
    Agreed. I'm new to RE & find this kind of practical information very valuable.

    Thanks to the kind advisers on RE.

  15. #15
    Join Date
    Dec 2008
    Location
    USA
    Age
    64
    Posts
    6
    Rep Power
    0

    Re: hand exspansion valve settings

    Segei,
    The difference to be concerned with is the operating conditions of the system. Typically the system operates at significantly different pressures between winter and summer.
    I agree, it may not be practical to adjust all if you have a large number of coils (and limited staff), it may be best to find the happy medium. On the other hand, you may be able to record the settings after one annual cycle and just make the adjustments seasonally. The main point was just giving guidenace on how to find the "right" setting...just my opinion.

  16. #16
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: hand exspansion valve settings

    Quote Originally Posted by jromine
    Typically the system operates at significantly different pressures between winter and summer.
    Why?

    The evaporating pressures should exist within a defined range depending on how much you let your suction pressure float (or minor adjustments to BPR's - which I don't care for).

    So if the evaporating pressures stay within their prescribed range then the only factor that change the hand expansion valve capacity (other than adjusting it) is the liquid feed pressure to the hand expansion valve.

    If you use a pumped liquid system (mechanical pump or gas powered) or a control pressure system the liquid pressure is relatively stable all year long.

    Hence no need to adjust the hand expansion valves once they are set during commissioning.
    If all else fails, ask for help.


  17. #17
    Join Date
    Sep 2008
    Location
    United States
    Age
    59
    Posts
    57
    Rep Power
    16

    Re: hand exspansion valve settings

    very true Iceman. in my experience once a HEV is set ( or reset to keep the paperpushers happy) it should do the job no matter the season. I do vary my suction pressure by a few pounds from season to season. this whole thread started when I asked what other techs do to set a HEV, I think I have got the answers I was looking for, thanks to all.

  18. #18
    Join Date
    Oct 2008
    Location
    Colombia
    Posts
    80
    Rep Power
    16

    Fine tune of ammonia system for energy efficiency

    I w´d apprecciate that anyone out there can talk about why and how [procedure] to do this kind of system adjustment. [Fine tune of ammonia system for energy efficiency.].

    Thanks.

    J.I.M.

  19. #19
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Fine tune of ammonia system for energy efficiency

    Quote Originally Posted by josei View Post
    I w´d apprecciate that anyone out there can talk about why and how [procedure] to do this kind of system adjustment. [Fine tune of ammonia system for energy efficiency.].

    Thanks.

    J.I.M.
    Adjustment of HEV isn't energy savings. This is regular commissioning.
    Energy savings require 2 steps.
    1. Determine optimum set points.
    2. Implement these set points.
    Very often we don't know the optimum set points and sometimes we don't know how to implement them.

  20. #20
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: hand exspansion valve settings

    The adjustment of hand expansion valves is a one-time requirement. The valves should be set so that a sufficient supply of liquid is provided to the evaporator so that it can achieve it's catalog rated performance. This is not efficiency related.

    Think of efficiency as a ratio. A common ratio is COP. Here in the US we use kW (power)/Ton of Refrigeration (for compressors). Other ratios can be defined as needed to explain operating data of any specific component (one where electricity is used in relation to something else, i.e., air flow, liquid flow, etc.).
    If all else fails, ask for help.


  21. #21
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: hand exspansion valve settings

    Quote Originally Posted by US Iceman View Post
    The adjustment of hand expansion valves is a one-time requirement. The valves should be set so that a sufficient supply of liquid is provided to the evaporator so that it can achieve it's catalog rated performance. This is not efficiency related.

    Think of efficiency as a ratio. A common ratio is COP. Here in the US we use kW (power)/Ton of Refrigeration (for compressors). Other ratios can be defined as needed to explain operating data of any specific component (one where electricity is used in relation to something else, i.e., air flow, liquid flow, etc.).
    We have to take all these ratios and estimate system efficiency. Certain combination of variables will give us optimum system efficiency.

  22. #22
    Join Date
    Mar 2009
    Location
    U.S.A.
    Posts
    320
    Rep Power
    20

    Re: hand exspansion valve settings

    If the evaporators were built for recirc duty and the unit has a guage connection near the liquid header: Close the HEXV COmpletely. Read pressure. Open the HEXV unitl the gauge gains pressure representing the delta-p of MFRS Spac.

  23. #23
    Join Date
    Mar 2009
    Location
    U.S.A.
    Posts
    320
    Rep Power
    20

    Re: hand exspansion valve settings

    Note that will not work with both Gauge and HEXV close to each other and well above the evaporator....

    The seasonal gain topic exists only for devices like air handlers which encounter more than 3-times the load at 35 C as at 25 C outdoor temperatures. Other than flooding return pipes: Theres no essential or continuing efficieny to be gained by tuning HEXV's on recirc units. On Liquid Makeup there is some gain in terms of control regularity and moving parts on controlled devices (slide valves, unloading solenoids)...So it could be of some effect on vessels for medium temp duty; the process , minus 40 loads don't know how hot it is outdoors.

  24. #24
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: hand exspansion valve settings

    Go back to the basics and check what the pumps, for example are pumping to satisfy the refrig load, against pump curves, one or many evaps., what ever. Double check the compressor performance, you can only get the max from compressor.,with a system balance, the fine art of trimming HEV's come from evap outfeed temps., the compressor dicatates the efficiency factor.

  25. #25
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: hand exspansion valve settings

    There is an old saying in NZ about consultants, that rings very true.
    Consultants "are the ones that come out of the hills after the battle is over, and kill all the wounded ".
    magoo

  26. #26
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: hand exspansion valve settings

    Quote Originally Posted by Magoo View Post
    There is an old saying in NZ about consultants, that rings very true.
    Consultants "are the ones that come out of the hills after the battle is over, and kill all the wounded ".
    magoo
    Very true...

    The version I have heard is: A consultant is someone that comes from out of town!

    They only get called after everything else has not worked.
    If all else fails, ask for help.


Similar Threads

  1. Oversize Relief Valve
    By Dacosta in forum NH3
    Replies: 1
    Last Post: 05-09-2008, 11:35 AM
  2. Service Procedures For TK Scroll
    By absolute-zero in forum Transport
    Replies: 0
    Last Post: 03-02-2008, 07:42 PM
  3. Compressor valve test
    By RackMechanic in forum Air Conditioning
    Replies: 11
    Last Post: 03-02-2008, 05:57 PM
  4. Benji
    By benji in forum Trouble Shooting
    Replies: 29
    Last Post: 30-01-2008, 01:25 PM
  5. Replies: 5
    Last Post: 16-10-2002, 12:38 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •