    Re: Controlled Pressure Receiver Operation

    Hi Segei.

    I'm not quite sure what you are mentioning. Can you elaborate please? Thanks.
    If all else fails, ask for help.


  2. #2
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Controlled Pressure Receiver Operation

    I mentioned about low limits on compression ratio. Are these limits apply to screw or recip. compressors? Why?

    Thanks
    Sergei

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Controlled Pressure Receiver Operation

    Each compressor has different issues. For most recip.'s and screws the minimum compression ratio is 2:1. So, if the suction pressure is high like on a CPR system, the minimum discharge pressure may be close to summer design conditions.

    Screws you have to worry about oil pressure if they do not have a full time oil pump.

    On recip.'s if the compression ratio is too low the explanation I have heard is; the loads on the wrist pin and valve springs can cause accelerated wear.
    If all else fails, ask for help.


  4. #4
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Controlled Pressure Receiver Operation

    For screw compressors without oil pump, pressure difference between discharge pressure and suction pressure should be above the minimum limit. Some Frick compressors have 55psig.

  5. #5
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Controlled Pressure Receiver Operation

    Yes, which would mean the minimum discharge pressure would be at least 65 psig + 55 psig = 120 psig (using the CPR pressure provided by kooltek). This also means the compression ratio is approx. 1.7 at this condition.

    Each application and compressor type may be slightly different. All I'm saying is to check the minimum requirements for operation.
    If all else fails, ask for help.


  6. #6
    Join Date
    Jul 2006
    Location
    USA
    Age
    74
    Posts
    865
    Rep Power
    26

    Re: Controlled Pressure Receiver Operation

    Quote Originally Posted by US Iceman View Post
    On recip.'s if the compression ratio is too low the explanation I have heard is; the loads on the wrist pin and valve springs can cause accelerated wear.
    Can you elaborate or speculate on that a bit?

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  3. Benji
    By benji in forum Trouble Shooting
    Replies: 29
    Last Post: 30-01-2008, 01:25 PM
  4. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •