Results 1 to 8 of 8
  1. #1
    ding dong's Avatar
    ding dong Guest

    carrier 30GK 085



    I have a problem with a carrier chiler model 30GK 085
    this chiler can work with two set points i need to now how can i control it.
    i now i have to conect or disconect two connections.



  2. #2
    Join Date
    Jun 2006
    Location
    South Coast
    Posts
    278
    Rep Power
    23

    Re: carrier 30GK 085

    How are you controlling the chiller, local or remote control.
    If you check the wiring to the following terminals this will help to tell you how this chiller is controlled remotely..
    30 -31 remote alarm
    32 -33 remote start stop
    34 -35 remote water loop pump contacts or flow switch.
    63 -64 remote cooling or heating
    65 -66 remote cooling setpoint

    Hope this helps

  3. #3
    Join Date
    Nov 2007
    Location
    Peoples Republic of Geordie Land
    Posts
    47
    Rep Power
    0

    Re: carrier 30GK 085

    Does any of you know how to set the temperature down low than pre set +3.3*C. I have a customer with a 30GK 085 which would like to run it at -3*C. They have added glycol within the liquid mix.

    I have contacted Carrier last week but are still awaiting there response. Do i need to change components to the unit for it to run sub zero?

  4. #4
    Join Date
    Jun 2006
    Location
    South Coast
    Posts
    278
    Rep Power
    23

    Re: carrier 30GK 085

    Quote Originally Posted by CoolKids View Post
    Does any of you know how to set the temperature down low than pre set +3.3*C. I have a customer with a 30GK 085 which would like to run it at -3*C. They have added glycol within the liquid mix.

    I have contacted Carrier last week but are still awaiting there response. Do i need to change components to the unit for it to run sub zero?
    According to the IOM for this unit to operate at -3C you will require some factory options either option 5 or 6 you will need to wait for Carrier to return your call to confirm which one you will need as for the glycol you have added you do realise you will reduce the capacity of the chiller, how much depends on the amount of glycol. Who did you call at Carrier ?

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: carrier 30GK 085

    Do you have a controls manual?

    http://eto.carrier.com/litterature/cm/13411.pdf
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Jun 2006
    Location
    South Coast
    Posts
    278
    Rep Power
    23

    Re: carrier 30GK 085

    Forgot to add that Carrier Service would be needed as well to reconfigure the Service Configuration Software in the chiller control board.

  7. #7
    Join Date
    Nov 2007
    Location
    Peoples Republic of Geordie Land
    Posts
    47
    Rep Power
    0

    Re: carrier 30GK 085

    Evening

    Thanks for all the help.

    We have the IOM and are aware the cooling capacity will be reduced depending on the glycol/temperature set. I spoke to Chris@ Carrier tech this morning and he cannot find any options that will alter the set points for the unit to run colder equired setpoint -3*c. He was going to speak to one of the Carrier engineers to see how to carryout the procedure. I'm still awaiting the call.

  8. #8
    Join Date
    Jun 2006
    Location
    South Coast
    Posts
    278
    Rep Power
    23

    Re: carrier 30GK 085

    Option 5 (Medium Brine) allows leaving temperature from +5C to -6C at minimum requires reselected Electronic Valves and varnished compresser terminal plates.
    Option 6 (Low Temp Brine) allows leaving temperature from -6C to -10C all of the above plus modified cooler and increased cooler insulation.
    Also if the chiller is to be run at ambients below 0C then Option 28 is needed which is Condenser Varifans (variable speed fan motors) 1 per circuit.
    As you can see its a bit more than just adjusting setpoints.

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. 30GK carrier chiller wiring diagram
    By ash_sabi2006 in forum Electrical
    Replies: 6
    Last Post: 20-05-2010, 04:26 PM
  3. Carrier Chillers
    By Ed Burris in forum Technical Discussions
    Replies: 6
    Last Post: 27-03-2010, 02:00 AM
  4. Help identifying carrier HiWall dom. split
    By paul_h in forum Air Conditioning
    Replies: 4
    Last Post: 12-12-2008, 09:12 AM
  5. carrier remote
    By superswill in forum Trouble Shooting
    Replies: 2
    Last Post: 26-04-2006, 09:17 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •